Can SCXI 1102 measurement of current and voltage signals simultaneously?

This may be a simple question, but I have a pair of moisture sensors that output 3 x 0-10 Vac @ 10 my max of signals that will be connected to a test loop that will have also a pair of sensors of flow as 2 x 4-20 my output signals, and I need to know if I can connect all four sensors on the same card of SCXI 1102 with endings of 1300 block , or if I need separate maps for the voltage and current signals. I am also looking at extra material for the other sensors, so I can have a different card if it will do the job better.

Thanks in advance!

BBalmforth Hey!

If I understand your description of the system you want to measure tension through the moisture sensors and known for flow sensors simultaneously.

Absolutely, this can be done with the 1102.  In the pilot DAQmx can we individually select the channels to read the voltage by the moisture sensors, and then choose the appropriate channels to read the current of the flow transducers.

Let us know if there is something else you need said.

Happy holidays!

Tags: NI Hardware

Similar Questions

  • Measurement of current and voltage USB-4065

    I have an application where I need to measure the direct current and the voltage. The current and voltage will be stable if the measures do not need to be simultaneous. I would use a USB-4065 to the two measures. I've seen the kb indicating the voltage inputs must be disconnected when the measurement current. The current inputs must be separated for a measure of tension?

    Hi Collin,

    I think that you are referencing this knowledge base.  After a few tests, and worked with the R & D group, it seems that the effects of input connections are perceived during the passage of two ways.  When the current entries are connected, a less accurate voltage reading occurs.  As such, please disconnect the current inputs for a measure of tension (as well as disconnect with tension when taking a measurement of current entries, who you know).

  • Measurement of current and voltage on Agilent B1505A

    Hi all

    I'm learning to program the Agilent b1505A using LabView.  I want to just start with a simple measure of a voltage supply and reading/measure of the voltage and current.

    I was able to analyze the data and apply tension without and the problem.  However, I can't understand how to check the voltage and the current.  I can get it only to record one or the other.

    I don't know how to know everyone is with Flex Agilent controls.  When we look through the manual, I see that there is a CMM order that sets the mode of operation of EMS measure.  I put it in mode 4, which measures both, but it still does not work.

    Anyone who is familiar with the use of LabView to parameter program Agilent analyzers?

    I got my code and the manual of the order of Flex of Agilent.

    Thank you.

    I think I found my problem!

    It is in the FMT command that specifies the format of data output.

    Thank you.

  • Measure the current and voltage using DMM sharing a port

    I want to measure pressure several times on a pcb, where I connect the ports of digital multimeters to the card using simple cards. Switching between the different voltages is done using simple. If the black port of DMM (the second from the top photo) is connected to the Earth to give the measure correct volt.

    And then I want to measure current through different lines. The problem is here. Given that two measurement types share a port, how do I get the correct voltage and current measurement? The second port of top would be grounded, so I can't use the method of measuring the voltage across the line through a resistance with a known value, since then the second port must not be connected to the ground. How can I use the current state of the DMM measurement? How measure current? Are there examples of this? Tried looking through manuals, but could not find the good starting points.

    so I can't use the method of measuring the voltage across the line through a resistance with a known value, since then the second port must not be connected to the ground.

    On all of my games to test I have to mux my land of the signal along with the salvation of my signals.

    All my mux test sets are set up for the topology 2-wire because there is no other way to do it without the weak side of switch also.

  • NEITHER 9207 reading current and voltage at the same time channels

    I have a cDAQ-9178 chassis USB-three cards NI 9217 RTD, three cards 9263 0 - 10V and one the output OR 9207 16 channels analog card. What I m trying with this kind of things, is to read all the analog input channels (information of transducer, temperature, pressure, etc.) and adjust my controls to process with the analog output channels.

    My problem at the moment is the following:

    When I create tasks with DAQmx VI:s, how to create a task that reads current and voltage on the 9207 channels at the same time?

    When I created a task for RTD-channels (16), a task for the outputs analog 0 - 10V (12), a task for the analog input 4-20mA (8) and a single task analog 0 - 10V input (8) I get an error-50103. I think it s because the tasks of current entry and voltagge are trying to use the same CAD at the same time and LabVIEW informs that "The specified resource is reserved. Tasks are to leave so that the analog output task starts first, then I merged all clusters of the error and the rest of the task are started by an order to current input-> input-> RTD input voltage. I get this error after the current enter task started and enter voltage task begins.

    Because I m new on the LabVIEW and stuck in that time, I wanted to try the forum to find answers. I tried to find if someone else was having the same kind of problem, but with a quick search, there was none. I m in a bit of hurry, so I apologize if West a subject with a happy for that and I missed too much according to me.

    Really, the best way to do it is just adding 8 channels of voltage at a task, then 8-channel current, somewhat like this:

    Then spread over different channels when you read later:

    It should run without error.  It always is multiplexed to sampling, but it will be much faster to create two separate tasks.  There will be between 2ms (mode high speed) and 52ms (mode high resolution) between each playback channels, but it will still be much faster than the permutation of the tasks.

  • Measurement of the current rail voltage > 10V

    Who am I to measure the current and voltage on a 15V supply rail.  (Here's a copy of my circuit attatched) I use an acquisition of data USB-6225 and Lab View,

    I have my camera to test connected to a power source. I connected two differential channels to the acquisition of data, one for the current and the other for the voltage.

    I understand that data acquisition is unable to manage more than 10V so I use a voltage halfway through the voltage divider. When I run the action, the indicated current is incorrect. It shows the 10A when it should be about 500 my.

    When I reduce the tension on the power supply 10V, it everything works fine, so I think that its got something to do with the limit of 10V.

    Please can you advise how I can connect that places correctly?

    Do it this way.

  • Help design a trigger for an analog voltage signal

    Hello guys,.

    I have a real problem one design trigger for an application, what I do is to power a motor and measure consumption current and voltage during each operation. What I would do is to begin to acquire the signal once the voltage rises to a certain value and finish when it falls to a certain value. The equipment I use is a cDAQ 9178 with a NI9205 and 9221 modules.

    Any help / samples / detailed explanation will be really appreciated. I have no idea on how to work with the outbreak of the vi in Labview.

    Concerning

    SergeArmz

    Finally after a lot of research, tests and many developments, this is a VI that I developed and who is able to do what I was looking for. Thanks to the guys who helped me out to understand how solve my problem.

    For all those who may have the same problem I had, I enclose the VI.

    And of course if you can improve on what I did will be great, I think it's the purpose of this forum

    See you soon!

    SergeArmz

  • Need help with measurement excitation current OR 9219 Module

    Hello

    I have problems to find the answer to my question.  My question is...  How do you analyze the excitation of a 9219 module current?  It seems that the excitation current which is specified (0.0005 (A) is not what is provided at the exit.  With a load of KOhm 10.5 a 0.00025 current is output.  As the resistance changes as the current and measured excitation voltage seems to change.  I just need to know the resistance... So, if I can monitor the voltage and current I can calculate the resistace.  BTW, why don't the current excitement remains fixed in the first place?

    Thank you

    Nate

    Hi Nate-

    In almost all modes of the 9219, the current and the voltage automatically adjusts to the load it experiences.  The resistance is then measured according to the amount of current and voltage sunk by the load.  This is explained in 9219 User Guide and specifications.  The guide also States the the 9219 input impedance according to which mode it is.

    I hope this helps.  Good luck with your application!

  • I/o current or voltage check with the switching matrix

    Hi all

    I want to use a switching matrix to test current and voltage of a control cabinet. For this, I have a voltage of the injector, injector current, a voltage measurement and measurement of currents from one side of the matrix (side line) and a 20 lines by I / O test. Is there a way to check (with a hardware or software solution) that we are ready for a test voltage or current in automatic mode.
    The ideal would be to have a physical key indicating that we are testing the right card, but if the operator uses the wrong card, I would check it is not injected + 24V-on entry to an entry card 0-20mA current.

    I wish you turns me on!

    Best regards

    Vincent

    Vincent,

    Some approaches for you to consider:

    1 Add a resistor or a few resistors to each card.  Measure the resistance before applying all power to the i/o lines.  The code of the resistance (s) to identify the class of Council (current or voltage) and rank (if applicable).  Simple jumper on the unused pins of the connector can also be used.

    2 measure the input impedance (or at least the resistive component) before turning the power on.  An input voltage device probably has a high input impedance while the current input device has a low input impedance. It could detect and reject some devices with resistance to entry incorrect installed.

    3. use a camera to determine which device is connected.  (This should satisfy your request to be informed!)

    4. you can replace the operator with a robot, but the robot would still need to use something like 1, 2 or 3 to identify the boards.

    5. use edge configurations physically incompatible connectors/card so that the cannobe Board connected to the tester bad.

    Lynn

  • Electrical engineering. Delay or phase of divergence of a voltage signal acquired by RedPitaya.

    Hello!

    I work with Labview and RedPitaya in order to measure the voltage and current to calculate the instantaneous power lift consumes when it works and then see how many are P active and reactive Q.

    I need to measure the voltage between line and neutral and multiply it and current, the problem is that the neutral is not accessible, so I have to measure the voltage from line to line and turn it into the phase voltage line.

    In order to realize that I have to make two changes.

    (1) I have /sqrt3. I have already done without problem

    (2) I have to define a phase difference of 30º, or delay of a period that is equivalent (1,6666667 ms) for the voltage signal.

    I tried to do this using a block to wait a certain time structure, but it does not work correctly when the voltage needs a loop, because the Subvi does not work at the same speed, during the reading of current and voltage after a delay I see with the option to highlight. And all the clock, wait or delay the blocks I've seen are supposed to work in a loop, not connected to a signal that reads / acquisition of an instrument.

    Is it possible to affect this difference in phase or equivalent delay without a loop that only affect the voltage signal?

    Thanks in advance.

    Did you just ask to all samples, then throwing those that you don't need? For example, let's say that you are sampling at 10 kHz, if each sample corresponds to a period 100us, 16 equals 1.6ms samples and so on. So you multiply 0 line 1 (0 indexed table) sample, for example 15 or 16 of the line 2 (the one that it works best for ya, or an average of 2) and use it as your result. In this way, you don't need any delay whatsoever and do not have to worry about synchronization, since all data is coming at the same time

  • Can a module SCXI 1102 with a block of 1303 b cause some channels of reading of the voltage signals and other signals of current reading at the same time?

    Hello

    I'm trying to use two sensors of moisture Omega HX85BA and experience two CFI mass flowmeters in current loop. Humidity sensors have three outputs 0 - 10V, while flow meters have two outputs 4-20 Ma. Can I have all four sensors to wire to the same block of connection SCXI-1303 and read all the signals in the same VI? the block is connected to an SCXI 1102 b card and a 6052E DAQ of NI PCI card.

    Thanks in advance!

    Hello BBalmforth,

    Yes it can. Although you will need external resistances (I recommend resistors precision for better accuracy) for current signals. The SCXI 1102 b is indirectly measuring the current by measuring the voltage drop across the resistance. The table below describes the current diagram and how it will seek in LabVIEW and DAQ assistant.

    Wiring diagram

    LabVIEW

    DAQ Assistant

    Kind regards

    Izzy O.

    Technical sales engineer

    National Instruments

    NI.com/support

  • measures of thermistor using modules SCXI-1102 and SCXI-1303

    Hello

    I have a 1303 SCXI front-end module connected to an SCXI-1102 module

    I read the article detailing how to remove bias and pullup resistors to activate measures of RTD/thermistor on the 1303. What did not mention article was the case plug the excitation source, and what is the best source of operating voltage (normal etc., high precision)

    I was wondering where I can find this information, also, I could do several types of measure on the same 1303? I have an analog voltage to a flow meter, and I would like to put it on the same module as the Thermistors

    Thank you!

    Kevin

    Kevin,

    The pulling up of resistors to connect to + 5 V internally.  If the values are not suitable for your application, you can use those.  It does give you much flexibility but.  The 1303 does not give you any other access to any source of current or voltage through screw terminals.

    Pull upward and pull down resistors are networks of resistors Series 9-pin SIP. So you can edit them in blocks of 8 channels for joint measures.

    Lynn

  • Where can I get a brief history of versions of Firefox, including the current and beta versions?

    I just upgraded to 3.6 to 5.01 and received a message saying that this version is obsolete, and should I upgrade to 6.0. OK, well I would like to know just where, in the history of Firefox, it will take me. This is not the first time I have wondered about the Firefox version history and tried to find the information. Looks like you have all hide information or are ashamed of something (the number of versions, maybe?) and make it difficult to find this information. I don't understand the logic of making this information so difficult to find, if it is available to all.
    (BTW, I'm a software sales engineer retirement for Tivoli/IBM products.)

    Kind regards
    Lynn Larsen

    Is not hidden; not a secret. Relatively easy to find.

    Enter "versions of firefox" (including the quotes) in Google, you can get: https://encrypted.google.com/search?sclient=psy & hl = in & lr = & tbs = qdr % 3Ay & source = hp & q = % 22firefox + releases % 22 & btnG = Search

    • In the "Advanced search" options, I have "Date" set for the year passed

    Second point, releases-MozillaWiki, gives you future versions, current and past.

    You'll see version news on all the 6 weeks, with a few numbers of minor version, if any, as you had with Firefox 3.6.x and earlier versions.

    If this answer solved your problem, please click 'Solved It' next to this response when connected to the forum.

  • Can I charge my iPad using a voltage converter and an outlet of 50 Hertz in Europe?

    IF I want to reload my iPad in a foreign country with 230 v AC and 50 hertz can do with a (at 115 v) voltage converter and still using 50 Hz instead of 60 Hz? Who will work ok without damage to the iPad?

    If you use the charger supplied with your iPad, it will switch automatically. You may need an adapter outlet such as those at Travel Kit for the Apple world.

  • Motor current and the current valve using CAN interface.

    Hello

    I want to order current engine and valve for some time. The currents of control valves and engine are different for different times, they also have different repetation for test times.

    My problem is how can exploit all the valve and engine at the same time.

    I use NOR-X-net, I have attached a capture, control valves and motors signals are the same message PSD1 - x 605.

    The valve are engine operation is also attached to the file xlx.

    Thank you.

    Rahul.

    Hello

    Please suggest me that how can I run motor and valves separately, both of the soul, I have attaced a program in which I am running engine and set of valves, but I want to run them with time to different repetation and check the valve and engine based on time, current diffrently.

    Thanks in advance.

Maybe you are looking for

  • Satellite L50 - B has very low-speed Wi - Fi

    Hello, I have a problem with my new B - L50 (bought yesterday for my son). The internet connection is very slow while my other laptop works very well. And if I go away from more than 5 metres from the Wi - Fi hotspot, no more connection! Can someone

  • Automatic rotation

    My auto screen just stopped turning. I checked the setting and it's turned on... What can I do? A reboot didn't help... I don't know what else I can try.

  • problem to open and cancel a Subvi by invoking the node

    Hello I have a Subvi, which is runing in a while loop and it's calculation that finished in a variable time. So I decided to add the abort function to invoke the node. This works perfectly when the Subvi is running by its own but gives an error. 1000

  • Photos martignetti 6520 past the test print then prints blank pages

    Smart photo 6520 connected to Microsoft Surface running as Windows 10 prints blank pages. Have reloaded driver - assists print test, but all applications print blank pages.

  • E4200 can turn it on, but cannot connect

    So, naturally, I've had this router for over a year now so the warranty is out and it is to stop working last night. I'm pretty decent in the world of router, since I'm studying for my CCNA, so I tried just about anything imaginable. I woke up this m