Link to the variable of the scan engine

I have the attached labview, the settings on a variable diagram and shared block.  In my project I have a cRio who is using the analytical engine and signals some time RTD.  in my computer, I have a shared variable that I have an alias to the scan on the cRio engine variable.  I thought that this would then make the variable shared on myComputer would report to the same as the engine to scan on the cRio variable; However, this is not the case.  In the front, you can see I get 0 for the myComputer shared variable while getting the correct value of the variable of cRio scanning engine.

Binds a variable to a variable of scan engine means that it will keep the same value?  I have to do something more?  I want to do it this way because I have a VI that find all the variables in the file SystemParameter.lvlib and did things with them.

Hey GreenRiver

If I understand correctly, you bind the network variable to the ProcessInRTD indicator. If you put this code in a while loop with a stop button, what happens? You can have a race condition here, where he reads the network variable and puts this indicator and then reads the temperature of the unit and who refers to the indicator of RTD.

A suggestion I have is just wire the output of IO functionality in the network within a variable period of time loop. Then, on your host VI, read the network variable.

Tags: NI Software

Similar Questions

  • Why the new cRIO-9076 does not support the scanning engine?

    I spec'd a new chassis cRIO-9076 spiffy but learned that, despite its impressive capabilities, it does not support the analytical engine.

    I'm curious as to why this is.  I hope that this is not an indication of support OR away from the scan engine and perhaps NSV technology as well.

    OK, uninstalled and reinstalled OR RIO 4.0 and now all is well, guess it was just one of those inexplicable installation problems.

  • CRIO 9075 pilot to 9870 (use of the scan engine)

    Hello

    I want to use a 9870 (rs232, 4-port serial interface) on a CRIO 9075.  I also want my labview project to run on the analytical engine. (running on Labview 2010 SP1)

    I used this Setup several times using a CRIO-9073 very easily.

    But now I can't find the correct driver for the CRIO-9075 game to make this work.

    Can someone help me?

    The NI 9075 cRIO requires a minimum of LabVIEW 2011 to be supported if you use the real time module. I'm afraid to say you're stuck until you can get a newer version of LabVIEW. I think that's the reason why you are able to up your game to work on the 9073 but not the 9075.

  • How day modules when using the scan engine and ethercat without losing the names and channels

    I have moved my modules and would like to update the device custom, but it will erase all my current settings (including channels calculated, etc.). I thought I saw a post on how to do this, but I'm not.  Any clues out there?

    Hello

    Unfortunately, I don't know of any way to do it.  I think your device either custom or environmental VeriStand (be it in your aliases, channels calculated, etc.), you will need to rename each variable/channel at some point along the string.

    Kind regards

  • Version 6 of Cisco and the scan engines

    Looking for information on the number of instances of 'rulesx' and "sigx" can be run on different platforms? For example, I can set up rules0, regles1, regles2 and even for sig0, sig1 and sig2, but how can I do?

    Generally, you are limited to 4 configurations of virtual sensor... vs0 and up to 3 additional named virtual devices, such as vs1, 'this_sensor' and 'that_sensor' (see exception in the next paragraph). The number of defined components (sigX, rulesX, adX) is not capped, but a maximum of 4 will be active at any time... corresponding to the virtual sensors. It is worth noting that you can reuse components, for example sig0 can be used both vs0 and vs2 while sig1 is vs1. Ditto for rulesX and adX.

    There is a limitation on the sensors 'insufficient memory', currently the 4215 and NM-CIDS, a unique virtual sensor active. These low-end sensors do not have the capacity of memory to keep several Active configurations in memory and still meet performance standards.

  • You try to run the scan mode and mode interface fpga at the same time is causing errors

    I'm reading a 9236 9237 and a 9215 with the scanning engine and read from two 9211 modules with the fpga. It's because I need to acquire to 200 Hz with the 9236 9237 9215 but maximum rate of the scan engine is limited by the slower module in the system, which in this case is the max of 15 hz the 9211.

    So to use both interfaces (scan engine and fpga), I followed the percisely given in this article for instructions.

    1. the project has created and added the peripheral crio using the interface of the scan engine.

    2. Add the target fpga and drag and drop the 9211 inside modules

    3. has created the fpga in interface file with and compiled with no error.

    4. interfaced with the file fpga at almost exactly the way the sample project of "getting started with 9211' by using the engine of analysis in the interface with the other modules.

    5. after the errors to discover that I created a VI that tests for just the portion 9211 code (called "thermocouple FPGA method Test.vi")

    The data returned by the interface fpga was nothing else than zeros on all channels, even if thermocouples were hooked on some of them. (all zeros as entries in the convert temperature vi gives-410, 6160 degrees F, if you happen to have the material to try this.)

    I get the following error from the open fpga vi reference:

    code error-61141
    "Thermocouple method Test.vi FPGA.
    Activities FPGA:

    Open FPGA interface reference.
    Reserved outside LabVIEW FPGA: turns The RIO Scan Interface. You must set the mode Interface FPGA chassis in order to unlock the FPGA. »

    It's extremely frustrating, because as I explained, I've been very attentive not only follow the instructions for concurrent fpga and analysis but also to model my VI by the example of VI, even if only for the moment, just to try to work things out.

    Any help would be appreciated as I need to fix this for the further development and I am somehow in a lack of time. I opened a support ticket (reference #7256226), but the app engineer had no time to answer.

    My system:

    cRIO-9014 controller RT with crio-9104 bottom of basket.

    LabVIEW 2009

    Latest drivers and peripheral software pc and rio (RIO scan 3.2 engine support june2009)

    rex1030 wrote:

    I'm reading a 9236 9237 and a 9215 with the scanning engine and read from two 9211 modules with the fpga. It's because I need to acquire to 200 Hz with the 9236 9237 9215 but maximum rate of the scan engine is limited by the slower module in the system, which in this case is the max of 15 hz the 9211.

    This should not be the case.  9211 data will not update with each sweep, but you should be able to run the scan faster than 15 Hz without problem.  Do you have specific issues with this?

    So to use both interfaces (scan engine and fpga), I followed the percisely given in this article for instructions.

    1. the project has created and added the peripheral crio using the interface of the scan engine.

    2. Add the target fpga and drag and drop the 9211 inside modules

    3. has created the fpga in interface file with and compiled with no error.

    4. interfaced with the file fpga at almost exactly the way the sample project of "getting started with 9211' by using the engine of analysis in the interface with the other modules.

    5. after the errors to discover that I created a VI that tests for just the portion 9211 code (called "thermocouple FPGA method Test.vi")

    You can try making sure that the chassis is set to mode Interface FPGA and the setting is deployed.  I wrote that article that you referenced says will select the deploy option later and not explicitly speak to deploy the chassis later.  Run a VI with a reference open FPGA vi not automatically deploy chassis settings if you need to do it explicitly.  Try the following steps.

    1. right click on the frame element and select Properties.  Make sure that the Interface FPGA option button is selected. \

    2. right click on the frame element and select deploy.

    3. repeat your VI.

    The data returned by the interface fpga was nothing else than zeros on all channels, even if thermocouples were hooked on some of them. (all zeros as entries in the convert temperature vi gives-410, 6160 degrees F, if you happen to have the material to try this.)

    I get the following error from the open fpga vi reference:

    code error-61141


    "Thermocouple method Test.vi FPGA.
    Activities FPGA:

    Open FPGA interface reference.
    Reserved for LabVIEW FPGA outside: The RIO Scan Interface is running. You must set the mode Interface FPGA chassis in order to unlock the FPGA. »

    The likely cause of this error is that the setting of the FPGA Interface on the chassis has not been deployed.  If the chassis is still Mode Scan fixed personality bitfile will be loaded on startup and the FPGA will be locked.

    It's extremely frustrating, because as I explained, I've been very attentive not only follow the instructions for concurrent fpga and analysis but also to model my VI by the example of VI, even if only for the moment, just to try to work things out.

    I'm sorry that you have had difficulties.  Assuming that I'm wrong about the source of your problem, it seems we have to update less than Ko to include the deployment step.

    Any help would be appreciated as I need to fix this for the further development and I am somehow in a lack of time. I opened a support ticket (reference #7256226), but the app engineer had no time to answer.

    My system:

    cRIO-9014 controller RT with crio-9104 bottom of basket.

    LabVIEW 2009

    Latest drivers and peripheral software pc and rio (RIO scan 3.2 engine support june2009)

  • Scan engine mode on RT does not not with EtherCAT NI 9144 chassis

    Hello

    I have problem with communication of the cRIO-9074 RT with NO 9144 via EtherCAT.
    I add the expansion with a NI 9203 module chassis to my system running on the cRIO-9074.
    I use it in engine scan mode. My PC application communicates with RT by network data stream. When I run only asks to RT, the RT is the reading of variables EtherCAT I/O chassis with no problems, but when I run the PC host application, RT probably go into configuration mode and interrupts communication with chassis EtherCAT - I can see that the LAN LED on expansion chassis stops flashing. "" Then, with still running application I click in the LabVIEW Project Explorer, the item target and select utilities ' Mode Scan Engine "pass back"Switch to active"Configuration, then it starts to communicate. I tried to do the same thing programmatically work with the Scan Engine VI Mode Set but it doesn´t so Runt-time it does not work as well.

    The behavior described above happened when I added the chassis extension in the project and only the module place entries in this chassis are affected, the rest modules 8 places directly in the cRIO-9074 work withou any problem.

    System:

    Professional Win7
    LabVIEW 2013 SP1
    OR-Industrial Communications for EtherCAT 2.7
    OR CompactRIO 13.1

    Hello

    problem solved. The reason was function RT Set Date and TIme.vi what casues on NOR-9144 error and blocked EtherCAT communication. I found that this function is no longer supported in LabVIEW. After the removal of this feature of application of RT, everything works fine.

    BR, Jan

  • Scan engine OR does not work

    Hello, I'm trying to deploy a program on the a compactRIO real-time controller. I decided to use the scan mode for now. However, when I try to start my VI I get the following error:

    One or more items in this deployment that the NI Scan Engine and the corresponding I/O driver (s) must be installed.  Go to MAX to install.

    If you continue to experience this conflict, see the topic "Deploying and running screw on year RT target" in LabVIEW help for more information on the deployment target conflict resolution.

    I time LabVIEW Real-time on my machine so I don't know what is the reason for this and I can't find it under MAX where to install the scan engine (again, I guess that it is already installed).

    I'm using LabVIEW 8.6.1 and the modules I use on my cRIO-9073 are 9477 module and the module AI 9205. Any help would be appreciated.

    Hi Pawel,

    You must install the NI-RIO driver on you cRIO (but first on your PC). After that, go to the MAX and select your cRIO. There is a point of software. Click on it and install the driver on your cRIO OR Rio. The latest version is 3.1.1.

    You will find here.

    Mike

  • cRIO - Scan engine's hybrid mode does not

    Hello

    I have a cRIO project in which almost all my modules must operate in mode of scanning (high density, low sampling etc. requirements), however I 9870 module that requires the FPGA interface, so I will try to get cRIO to work in hybrid mode. I followed the instructions in the article on this subject without success. At the present time, everything works perfectly if I leave the chassis in the interface in scan mode, but when I go to the FPGA interface (deploy the change, compile my FPGA vi, download the bitfile and restart the RT vi) none of my data values are updated, and it's not just that they are stable, the timestamps on them are all zeros. The RT is Scan Engine State VI says the scan engine is in Active mode, but still it behaves as if it is not. Any suggestions?

    Thanks for the help,

    Jon

    Hello Jon,

    Can you explain your configuration a little more in detail?

    When you say download the bitfile tell you download the bitfile blinking to run at startup?  The FPGA VI is set to run at startup?

    Your code RT has an 'open FPGA VI reference' calling in?  If not, can you try that one?

    You are able to communicate with the 9870 in hybrid mode?

    Thank you

    Sebastian

  • Scan engine access on CRIO protection?

    I'm running a production Tester high volume using the CRIO in a car factory, and my application uses the analytical engine.  I fell right on s analysis vi engine in the measures of e/s palette that allows you to target a CRIO and alter the scan engine.  Although very convenient, it seems that it is a very dangerous thing to leave unprotected or some kind of user access rights.

    Can password - protect the scan engine settings changes to avoid this kind of change?  Locking of the CRIO accomplishes this?

    Thank you

    Rob

    Hi Rob,

    I found a better way to protect the cRIO. In your project, right-click on your controller for cRIO, and go to properties. In the properties on the left side menu, you will see a list of Catergories. If you click on the user access, you can allow and deny access to certain IP addresses. Now, only the IP addresses in the list of the grant will be able to connect to the cRIO (and if you can not connect, you can not deploy any code). I tried this and I accidentally the cRIO locked out. If you never lock yourself out, you need to modify the nor - rt.ini, located on the RT controller. Because you can change the access to this file as well, you want to password protect the Max cRIO thus so that this file cannot be changed.

    Thank you

  • Trend Micro PC-cillin Internet Sec 14 for Dell - Scan Engine version

    Hi all:

    Can you people posting your current version of your engine for me?  My auto system updated to v. 8.550.1001 around December 07 and all was well with the program.  I check my version of template w / Trend Micro to check website I have the current template file and I always do.

    For some strange reason, my scan engine did not update to what's trending says is the 'current' version of 8.70.  I established a procedure for manually updating the scanning engine for this v.14Dell of the web site of trend, but it has dated 12/19/06.  Mentions XPsp2/XP/Vista, but I'm not comfortable with this old info.

    Anyone have the current version of the analysis of the engine 8,700 running on your computer?  If so, how did you get it?  The automatic update, or did you download the file from the engine and do it manually?

    I had a lot of luck with this version of Trend Micro, uninstalled the firewall to deal with other issues.  I am running Vista Home Premium, SP1 (sp1 really makes things more zippier noticed a pretty big difference).

    Any help is greatly appreciated

    Thank you very much

    Ted

    Message edited by Ted_C on 04/19/2008 05:49

  • IPS scan engine

    Referring to the type of scan engine specifically signature 3030. Signature 3030 uses the scan engine. The unique value of the default value is 15. What is the component "hour" of the scanning engine? There must be a time component, otherwise you'd have GIS 3030 tire all the time (15 events per hour... triggers an alarm).

    There is a 5 second timeout.

  • When I click on a link that I searched in a search engine a new faucet is opened. How can I change it so that it remains in the same tab, in that I tried

    When I click on the link in a search engine. allows you to use Google for instance and say that I find the camden wyoming fire company. When I click on the link to the website a new tab opens with the web site. . How can I change it so that it uses the same tap in that I tried

    Hello to bratman0, by default google results should already open in the same tab, if they don't please ensure that you have not set to open a new window browser for them within the parameters of google: https://support.google.com/websearch/answer/425

  • I don't see the link to the engineering of Netgear XWNB5201 units for my Mac?

    I don't see the link to the engineering of Netgear XWNB5201 units for my Mac?

    I thought that this establishment should be simple, plug-and-play as such.

    The security on the access point button is not very good. I think that this will be returned for a refund

    Netgear equipment is now packed ready to mail to perceive as I spent quite long try to put equipment which is completely lost time.

    I am disappointed with the Netgear site for support when you follow the instructions in the manual and connect, I see is complaints and comments and no solutions. The site is in my opinion, very poorly built and managed.

    As solution I just ordered Devolo units that have been strongly recommended and will be with me in a few hours, and my Netgear headache will be resolved.

  • cRIO 9068 + Scan Engine Support error - even if it is installed on the cRIO, after the deployment of error says his lack

    All,

    I have a cRIO-9068 I try to use the scan mode for. I have intalled all the latest drivers and software as explained. However, when I put my chassis to scan mode, then select deployment all, I get this error on my chassis and all my modules:

    "The current module settings require a NI Scan Engine support on the controller. You can use Measurement & Automation Explorer (MAX) to install a software package recommended NOR-Rio with NI Scan Engine support on the controller. If you installed LabVIEW FPGA, you can use this module with LabVIEW FPGA by adding an element of FPGA target under the chassis and drag and drop the module on the FPGA target element. »

    Everyone knows this or know why labVIEW does not recognize that the software is installed on my cRIO or is it not installed correctly?

    AGJ,

    Thanks for the image. I saw a green arrown beside all my pictures of chip and it seemed that meant that the software wasn't really being installed. I formatted my cRIO and did a custom install. My problem was that I had the two labview 2013 and 2014 installed and the cRIO put conflicting versions of software. After doing a custom installation and choose only the versions of 2014, my picture now looks like yours!

Maybe you are looking for

  • Satellite L650-14F - system does not have WiFi

    Hi all I've seen a few topics about this, but I still can't solve my problems. I have brand new Toshiba Satellite L650 14th but I can't seem to use my WiFi. The problem is that the system does not recognize, even in the Device Manager there is nothin

  • T61 screen

    Dear friends, is it normal for me to see that the color white for example looks like it has grain inside and seems to be a bit like gray-blue? I only mean if you observe it? It's very strange, and given that I don't have opportunity to compare with o

  • Sticker custom control

    Hello I need help. I'm changing this control in order to put a '1' on it. I need to merge the 1 and the graphics race so when the user can click on the '1' button and the button works.  The button does not work now, when you try to click on the '1 '.

  • Pavilion p6267c maximum memory

    Hi Expert, Anyone know what is the maximum memory I can add to my Pavilion p6267c?  The original specification is 8 GB of memory, and I'm hoping to add more.  Is this possible? TIA Steve

  • 5505 all-in-one printer not print some pdf images.

    5505 all-in-one printer not print some pdf images. the paper passes through the printer, but no image or text is printed on the paper. This seems to happen when the document is an 'image' and the text is not "searchable". Windows XP. no error message