MODBUS RTU multiple request & response (OR VISA)

Hello

I would like to ask how many request and response on MODBUS RTU using VISA? I tried 2 camera digital surveillance, I did a Labview program to connect this device alternately using stacked sequence Structure, but it can communicate with 1 device and the answer, I think that there is an error, the number of bytes does not match what I ask (0 A 04 0000 0002 B 70-0)

It's my screenshot

any suggestion? or maybe use other way to many request and response use NI VISA?

Thank you ~.

It was pretty hard to see this video.

Of course, as part of the 2nd, lower comparison was coming to True, which means the false cases where things was spent could not run.  (Seems like the reverse logic to me.)

Well, you check the first two bytes to see if they were not equal to 010 a.  They were good because it is the response to the command you send who left 010 a.

In the first picture, it worked because you send the command from 0A 04 and compare to see that's not equal to 0404, which of course is not.  What is the point of this?  It makes sense to mixed.  You want to confirm it is the correct slave address and the correct command (so that they would be equal) to run the code of decoding.

The other comparison is also useless because you try to check if the first two bytes are equal to 0 a, (any image you're in) which they will never because a string of bytes 2 can never be equal to a 1 byte string.

Through execution of high point, you should have been able to understand what was or wasn't running and why.

In addition, you only need a VISA close because you open just a resource of VISA.

Really, you'd be better off using the Modbus Library.

This is a much cleaner version of your code using the Modbus Library.

Tags: NI Software

Similar Questions

  • Watlow F4D Serial Communication problem error Code-1073807339 VISA Read in Watlow F4.lvlib:Utility MODBUS RTU receive message

    Hello

    I am trying to contact a Watlow F4D controller on a room using RS232. I use a cable converter USB-series and NI Watlow F4D Serial Driver.

    The code of error-1073807339 occurs in:

    Read in F4.lvlib:Utility MODBUS RTU Watlow VISA receive message-> Watlow F4.lvlib:Utility Register.vi reading

    I don't know what caused the problem. I am able to see the cable converter USB-Serial OR max. Please see the pictures for more details

    Thank you

    Felix


  • MODBUS RTU via TCP/IP

    Dear all

    I'm looking for a Modbus RTU on example TCP/IP VI. Does anyone have experience with this Protocol?

    Please kindly give me some advice!

    Thanks and greetings

    Luong.Tran

    Hello

    Start herefor more information and the LV ModBus lib.

    Kees

  • Protocol Modbus RTU data types

    Hello

    I use series ADAM with the data type Modbus RTU protocol.which should I use to read and write operation?


  • need help on modbus RTU: do not know the meaning of the other output registers

    Hi all

    I use LV 8.5, a programmer time & 1st novice LV to post msg in discussion, so please let me know if I missed something important.

    In any case, I'm 2 power meter data acquisition (1st is CPM-50 model, 2nd is MWH - 10, the two brand ADTEK). the Protocol of these devices are modbus RTU. I have two targets to:

    1 acquire data using RS - 485 (portable <-->meters of power)

    2. acquire data using ethernet (laptop <-->converter series/ethernet <-->meters of power)

    now I'm in the 1st part, I use the local brand USB-RS485 converter & I think that there is no problem in the port itself (past the loopback test). I create a program using LV samples Mo using w / these port settings: 9600, 8, N-1 as databit baud, parity, stop bit respectively (the same data format of the device: see page 17/42 of the manual). I use the query.vi series of MB that I customized to eliminate the error timeout 6101 (see attached photo).

    Problem: I can read the right data into the output register , but is located in the 5th element of the 1 d array. In the peak of the attached example, I'm currently reading the baudrate of the device (see manual pg 26/42: address 0102 h = 258 d). so I read the 9600 w/c is correct. I also had the correct readings of other addresses of parameter which is also located in the 5th element of the 1 d array. Note: I never tried to read data from power because the meters are not yet installed in the cabinets of power (maybe installed nextweek leave)

    Question:

    1. What is the significance of the first four output records in my table 1 d of output?

    2. why I got 5 output registers eventhough I'm asking only 1 quantity?

    3 read the correct data in the 5th element normal?

    I want to just be deleted in the data I read before jumping in part 2 (connection via ethernet). If I forgot some valuable information, let me know. Thanks in advance!

    Kind regards

    Ivel


  • MODBUS RTU - problem reading Holding - myPCLab Novus records

    Hello

    I've tried for a few days to read the logs at Novus myPCLab (it uses the Modbus RTU Protocol). I used the DSC module both Modbus Library without success (it seems to connect properly but cannot read).

    I need to read the given current.

    Does anyone have an idea on what am I hurt?

    Here's my vi and modbus address.

    Through the DSC

    I used the address PLC to 'HR Inicial' and 1 'St number.

    Through the library

    I used the PLC address in "start address".

    You have created a connection that is configured to use a "unit ID" 0.  Slave never devices typically use a device number 0 which is considered to be a broadcast address.

    Check the address of the slave of your device.  So make sure that you use this number.

    I guess that you communicate with a device that behaves like a slave.  If so, you must create a Modbus master in your code.  With the new modbus communication protocol Subvi, you created a slave.  A slave cannot talk to another slave.

    Similarly, in your second picture when you use the older Modbus Library, you not connected any constant to the top of the SubVI WriteRead that defines the parameters of series of devices such as RTU and address of the slave, so she takes by default to 0.  Once again, a broadcast address.

  • Problem of Lookout 6.0.2 modbus rtu?

    One of our clients has Lookout 6.0.2 communicates with several Packs of Scada CMI on wireless modems using the Modbus RTU Protocol. All of a sudden Friday night he got comm fail alarm pages on site all but one. The Modbus statistics window revealed that Lookout had stopped voting for all sites, except a single site that remained in communications. The only activity is a single site.

    He saw it queries this way for 2 hours, never to regain the normal polling cycle.

    I had him quit and relaunch Lookout and mark returned to normal and has been like this since late Friday night.

    This system has been in use for several years with very close 100% good communications sice we have deployed so far.

    It was obviously a Lookout failure, since the only approach was to quit and relaunch Lookout.

    Is there a timer for this kind of mistake?

    Is this a failure of the cbx Modbus object? (We use the plain vanilla Modbus driver)

    Roger Foote

    Foote control systems


  • Issue of JMS request/response model

    Hi all

    I'm a JMS request/response using q temporary queue model, as I understand it.

    I want to know is if it is possible to use a single queue of the application and the response without 2 subscribers on the queue of diversion of each and other messages.

    For example:
    -client A sends a message to the queue of Q.requestReply with text ("query")
    B reads the message off the coast of the Q.requestReply queue
    B captures MessageId
    B sets the CorrelationId MessageId = replyMessage
    B sends replyMessage to queue Q.requestReply with the text ("the answer")
    -A reads the response message and prints them out 'the response '.

    Is this possible without B pick up the message that he has responded to A?
    I'm trying this through java, and if A is down, B continue to read the message you post in response to A q.

    Hope it makes sense
    Concerning
    Ruan

    without filters, any Subscriber could get any message. with filters, you can choose who receives this message. I don't know what is your exact usage scenario, but since your original post, I think maybe you have a pool of workers who listen on a queue, remove a message, do the work, then the response on the same queue. you could implement this scenario by using a property of message custom as "isReply".

    -all 'workers' listen queue with a filter "isReply is false.
    -client A makes a request in the queue, then listen to the queue with the filter "correlationId = & isReply == true.
    -When a worker receives a request, it does the job, then hands the answer on the queue, by setting isReply to true and the correlationId for the messageId property request

  • is it possible to use the ROWNUM in the request/response

    Hi, is it possible to use the ROWNUM in the request / response.

    for example, in the "Advanced SQL filter '. Thank you!

    Hello

    Using RCOUNT (1) and try...

  • Modbus reading on request

    Is there a way to read only a modbus on request? I want to be able to click a button 'Get Data of the controller.

    Also related, I just want it write on command. I currently have a trigger/relay for writing data, but I can't tell if modbus is always send the "write" command (using the previous value of the line) or not.

    I'm reading through the modbus test data. It seems that additional orders would limit the sampling frequency, leading to lost data. If I read that data registers, the data have no recurrence. With other commands, I get up to 10 blocks of the same value.

    Thank you.

    You take the input module in a relay with option of data block.  Only when you raise the output of the command, you will be allowing the flow of the module.

    This average thagt unless you trigger the relay, the module will not process and ask for value

  • Modbus write multiple registers incorrect version

    I use NI Modbus.llb, found on the site OR somewhere...

    Now, I found the broken wires by calling vi because MB series Master query write multiple registers (poly) .vi has an output at least (probably written content, read later... check...)

    Where can I find the good .vi MB series Master query write multiple registers (poly)?

    Thank you

    It may also be that previous guys changed the Modbus function OR...

  • Download CS6 Master Collection using request / response code - is legitimate?

    I bought a copy of Adobe CS6 Master Collection download and wonder now if it is legitimate. It's instructions go like that.

    1. Download from mediafire.com, what is called "Adobe CS6 license PREACTIVATION.rar"
    2. Unzip and run "Adobe CS6 license PREACTIVATION.exe"
    3. Connect on Adobe.com and sign in with the user [email protected] ID and password included in the purchase
    4. Go to the product download CS6
    5. Download the two files for CS6
    6. Run the smaller of the two files to the collection facility
    7. When asked for a serial number enter "1325-xxxx-xxxx-xxxx-xxxx-3266" (of course the s 'x' were the numbers)
    8. A dialog box appears during installation with a links saying "click later and install CS6. Select it
    9. Complete the installation
    10. Start Photoshop
    11. A dialog box saying "Having problems connecting to the Internet" appears. Click the 'Generate the Code request' activation offline
    12. Take the generated application code and send it to an address of mail in Turkey.
    13. The address of e-mail in Turkey will respond with the response code that I could then get into Photoshop

    This is not legitimate or have I been scammed?

    I asked the Turkish user a few questions.

    1. Can it be installed on two computers which I think is common for such Adobe products? Answer: No.
    2. Assuming that the answer was Yes, should I use this method of response for each installation code? Answer: Yes
    3. Can CS6 be moved to a new computer in the future? Answer: Should use the method of response code
    4. After activation successful using the response code, Belarc Advisor scored a different serial number. Can I use this number and work around the stuff of response code? Answer: No.

    Thank you, Brian

    Nothing of what you describe seems legitimate to me... but I'm just another user like you (although I buy Adobe's Adobe products).

  • OSB: How to send multiple requests to a proxy service.

    Hello

    I got a new requirement, I e, my power of Attorney must accept multiple applications of the source system and treat them sequentially. How to proceed in the proxy?

    Thanks in advance.

    As I am new to conditional branches,

    http://docs.Oracle.com/CD/E23943_01/admin.1111/e15867/proxy_messageflow.htm---article 21: 5

    http://docs.Oracle.com/CD/E17904_01/doc.1111/e15867/modelingmessageflow.htm#i1061669

    can u pls tell me how to do a loop for each incoming request?

    Use for each action
    http://abhinavgupta3.blogspot.in/2013/01/for-each-loop-in-OSB.html

    It could be useful!

    Kind regards
    Afonso Gupta

  • Delay request response routing rules

    Hello
    I am uttering a service that can be called by any number of applications of the applicant.

    I build it as an EBS by using the deferred query response MEP.

    I'm currently building the response message routing rule.

    In the 11.1.1.5 dev guide, Section 10.8.2.3 tells me to create routing rules as follows:

    & lt; Quote >
    In the service, this information is transferred from demand EBM to the EBM response. This information is used in the EBS response by placing a routing rule in the filter as:

    < name of EBO > ResponseEBM\corecom:EBMHeader\Sender\
    WSAddress / wsa: ReplyTo / wsa:ServiceName = < asking the name of Service >
    Target endpoint for the assessment of this rule should be set to the requesting service.

    For each service applicant of EBS to request that is waiting for a response EBS to send back a response, specify a rule of routing as shown above.
    & lt; / Quote >

    It tells me to hard code the name of the service to the requesting service. I don't know this at design time. I don't have a list of services that will call my EBS.

    I want to use the replyTo address that is sent in the EBM query, transfer in the EBM response and make the EBS to send the message to the message what ever is sent there.

    Does anyone have instructions on how to do it?

    So far what I have is:
    ABCS applicant fills < EBMHeader > < Sender > < WSAddress > < ReplyTo > < address > with the uri for the call return
    Calls to ABC EBS as usual
    EBS called ABC software packages as usual
    ABCS copy sender > < WSAddress > < ReplyTo > < address > < EBMHeader > < in the EBM to < EBMHeader > < target > < EndPointURI > query
    ABCS call EBS answer
    Response of EBS has a second mediator who a is connected to a false reference:
    < reference name = "ProcessTransactionRequestEbizProvABCSImpl_002".
    UI:wsdlLocation="oramds:/apps/AIAMetaData/AIAComponents/EnterpriseBusinessServiceLibrary/core/sys/IC/TransactionRequest/v1/TransactionRequestEBS.wsdl" >
    < interface.wsdl interface = "http://ic.ac.uk/AIAMetaData/AIAComponents/EnterpriseBusinessServiceLibrary/Core/SYS/IC/TransactionRequest/V1/TransactionRequestEBS#wsdl.interface (TransactionRequestEBSResponse)" / >
    < binding.ws
    port = "" "
    Location="oramds:/apps/AIAMetaData/AIAComponents/EnterpriseBusinessServiceLibrary/core/sys/IC/TransactionRequest/v1/TransactionRequestEBS.wsdl".
    / >
    Ombudsman as a result of the EBS sets the property value endpointuri < EBMHeader > < target > < EndPointURI >

    It will not work for me because I am currently getting an error.
    Does anyone know how this should be done?

    Thank you
    Robert

    What I suggested was to use ASYNC two-way MEP. Ombudsman and BPEL support this.

  • Using request/response patterns to the WLI process

    I'm building a wli process and I have a schema that describes the request and response burden that I want to use. When I select the schema items to use in the request of the customer and the customer return nodes should I choose a complex type or an element in the schema?

    I can define my payloads as complextypes in the schema and use it directly or I can create complextypes elements to represent the complextypes, then select the items in the schema instead of the complextypes. Is this really a design problem or is there another reason for this somehow?


    Which one to choose for my applications node? (payloadRequestObject or payloadGlobalElement) Why?

    Example:

    < xsd: complexType name = "payloadRequestObject" >
    < xsd: SEQUENCE >
    < xsd: element name = "payloadelement" type = "string" minOccurs = "1" maxOccurs = "1" > < / xsd: element >
    < / xsd: SEQUENCE >
    < / xsd: complexType >

    < element name = "payloadGlobalElement" type = "tns:payloadRequestObject" > < / item >

    There's a reason why the elements are marked with green icons and types are marked with grey icons when choosing what you have to go in and out process WLI. Unfortunately, I can't find the reason documented anywhere :-). To answer your question, I've always had success with elements, and I have never had success with guys, so use items. I hope this helps.

Maybe you are looking for

  • Why firefox redirects my homepage site to wrong address

    Hi, I have firefox redirect this http://cureyourimmunesystemnow.com/ to the following address: http://cureyourimmunsystemnow.com/wp I thought that he was a cpanel or problem of WP and have spent ages trying to solve. Finally, I wiped all my work (all

  • photo library is not available when synchronize with the iPod touch

    When syncing my iPod Touch with iTunes & Photo, I get a message saying could not synchronize the photos because the photo library is not available, please try again later. Can anyone advise me on why this message is received and if there is a patch o

  • Probems with decoder video tuning MC

    My F10 has worked well in the United Kingdom. Now, in the Middle, eating can not give to the TV in the Middle East. Message "Video decoder not installed restart MC" a catch 22 situation. What can I do

  • ReadyNASOS 6.4.0 - T127 (Beta 3) on Readynas Pro 6

    Guys, I just installed last 6.4.0 beta branch. I've noticed that disk numbers are not displayed on chassis display upwards. Only squares are shown but not number inside them. I think it is a bug. Good bye

  • What is now updated?

    does anyone know which did not appear in the update today?