NEITHER 9211 / CRIO 9013 thermocouples measure?

Hi, I'm a beginner with thermocouple, but I try to read the values of the two thermocouples (type S and K) on my module 9211.

I thought that module analog 9211 send me the voltage and use a VI to convert it to a temperature.

But I'm wrong module give me the temperature on the A0 A1 channels!

So I try to use the example (C:\Program NIUninstaller Instruments\LabVIEW 2009\examples\CompactRIO\Module Specific\NI 9211) labview VI but I can't use it because I do not have the license th FPGA have so I don't have access to the track and the cjc chanel!

How can set the NI 9211 to give me the right temperature with the thermocouple model? or how can I convert the sending real time the odule byx in the right a (type S or K)?

Thanks for your help

Auto answer:

Simple (too simple maybe ) to configure thermocouple I need to press on the property of the module (not on the channel, I tried just this one)

and you can configure the type / unit and for the result!

Hates me...

Tags: NI Hardware

Similar Questions

  • NEITHER 9401 + cRIO 9082 speed measurement

    Hello!

    I want to measure a signal rotation with the NI9401 and the cRIO 9082. For the test, I use a signal generator and it is connected to the Mod5/DIO0. In the FPGA, I want to measure the rising edges. (see photo) With them, I'd be able to calculate the number of laps. But my code does not work: counties meter up constantly even I have no signal generator connected. What is the problem?

    Thank you in advance.

    Best regards

    Franz

    Hi Franz.

    I found no examples in LabVIEW version 2013, but in 2012, you can find them. In general, you can simply download the version as an assessment and get examples. Since I found the examples in a VM youc an discovered the examples attached to this post.

    Not to mention that most of the examples are restructuring in the new versions of LabVIEW but general subjects are still there.

    Best regards

    Christoph

  • NEITHER 9211 not showing correct readings

    Hi, I use neither 9211 4-way TC +-80mv temperature measurement with thermocouple type k and c - Rio but I get random values.

    anyboday can help!

    Hello

    You seem to be the value of TC0 missign and there is no point in your loop that I see. Bring values back to your host and then convert back to temperature through the NI9211 convert temperature VI. There is one for raw and one for calibrated, they are both in the 9211 support Files.llb \Exmaples\CompactRIO\ModuleSpecific\NI9211\NI

    Mike

  • With the help of several NI USB-TC01 Thermocouple measuring devices

    I am currently set up with 1 NI USB-TC01 (http://sine.ni.com/nips/cds/view/p/lang/en/nid/208177), and everything works fine.  My question is, can Labview control multiple TC01s simultaneously or I have to buy the NI USB-9211 has (http://sine.ni.com/nips/cds/view/p/lang/en/nid/201881#) to manage multiple thermocouple measures at the same time?

    Thank you

    Ben

    Ben,

    I didn't know we even had this device but I think that all of the information you want are in the link below.

    http://digital.NI.com/public.nsf/allkb/7A9DAE5554C9D503862576FC005A3908

    If you use the built in program, it is four devices, if you are using LabVIEW, you are limited to 127 devices.  I don't know if several windows built-in software should be used if you use a LabVIEW.

  • NI9213 Thermocouple measurement noise AC

    I use a cRio with various thermocouple C-Modules NI9213. For my application, I need thermocouples not be safe and be very close (same body) sources and AC cables. When I read the thermocouple values that are close to the AC cables, I see noise sinusoidal structure in different frequencies (according to my sampling frequency). I use high-resolution scanning engine (mode high speed gave a louder signal). I would appreciate any help on this matter. Should I ground my cRio in a particular way? My last resort will be to sample at a higher frequency and the average of the values (assuming 60 Hz noise, I want to sample at least 120 Hz).

    Thank you!

    Thank you very much for your answers.

    I had to settle for ' high resolution ' on the NI9213s and its rejection of 60db 60 Hz with some 'best practices' noise when the wiring of the AC power lines and thermocouples. However, the noise is not completely filtered. Looking around for other data acquisition devices (no OR in particular) I found modules thermocouple with at least 120db 60 Hz noise rejection. I personally use another provider of data acquisition with a thermocouple module that filters the noise of 60 Hz as a charm. I wonder why limited filtering on the NI9213.

  • USB NI 9211 measurement range has

    Hi all

    I would like to know if there is someone who can confirm the measuring range of temperature of the case NOR USB 9211 a

    thermocouples of using the en J and K?

    Kind regards

    Hello

    9211 a USB device works on the normal defined temperature ranges the NIST (J, K, R, S, T, N, E, B and types of thermocouples)

    Please open the link below

    Thermocouple NIST database

    Kind regards

    Mart G

  • I need to a portable data acquisition that can measure up to 15 thermocouples which is usb

    Hello, a friend of mine who has no experience with labview wonder on what daq can he buy in order to have a portable thermocouple, measuring system.  It must be usb so he can take it with him and his laptop computer and can connect up to 15 thermocouples.  I've seen some usb based systems which are specifically for thermocuple measure but have only 4 entries.  It is all daq usb that I could use for this application and that I also have to cancel any unwanted noise via programming?

    Take a look at Measurement Computing which is a part of National Instruments.  The USB-TC has 8 channels, so 2 of those who would do the job.

  • Reading of thermocouple

    All, I am new to this, make an old system of will vary from data upgraded.  I've been through basic training 1.

    I have a problem.

    I use one OR momo-9178 with NI9211 and NI9205.  The NI9205 is a simulated flow signal removes a conditioner of frequency.  I use the DAQ Assistant to acquire signals.  I am currently plotting flow vs temp just to get an understanding of the XY plots.  My problem is this... when I write temp and flow values to a file TDMS I noticed that my thermocouple measurements are as follows (see below).  Don't know what I'm doing wrong, can anyone help, see attachment.

    78.52764246
    78.52764246
    78.52764246
    78.45823079
    78.45823079
    78.45823079
    78.45823079
    78.5143133
    78.5143133
    78.5143133
    78.44951917
    78.44951917
    78.44951917
    78.44951917
    78.45512712
    78.45512712
    78.45512712

    Hi rfireton,

    Is the concern that there are 3-4 copies of the same data?

    The reason is that the 9211 is considered a module included in the slow sample (14 s/s in this case).  A feature of these modules is that they allow you to define a sampling frequency more quickly what is technically possible on the module, but just repeats the data if necessary.  This feature was a necessity for these modules included in the sample slow to operate in the same task in the form of modules faster as the 9205.

    Indeed, the former cDAQ chassis (9172), he was required to put all the modules of analog inputs in the same spot.  9178 chassis more recent that you use it is no longer necessary (but it is still possible).  9178 a 3 engine synchronization of input analog, so you can actually run a separate task for your 9211 at a rate of support if you want to avoid receiving duplicate data.

    Best regards

  • control thermocouples

    Hey, I have a strange problem and I hope someone can help. I have been using a program for about 6 months now that basically keeps a cold temperature next to a heat sink and maintains a warm temperature on the other side.  Then I 25 hung in the meantime thermocouples to measure temperatures I can do the analysis of the material in the environment.  My problem is that all of a sudden the readings of the thermocouples were out of control and unpredictable.  I add me automation program so it could run several tests at the same time and in the process developed by this problem.  The weird part is that the problem is also past in the old version of the program now too, and that has worked perfectly for the last 6 months.  I have 25 hung thermocouples and temperatures will all look all right, but then 3-5 of them will be quite wrong at random.  What is interesting about this problem, it is that when I change the thermocouple which become the use of heaters to maintain the set temperature, the values that were wrong again on the right and some other thermocouples start giving invalid data.  The installation program uses a NI 9213 and 3 NI 9211 inputs for thermocouples.  It also uses one OR 9401 to control heaters through a box pulse width modulation power we have.  Someone at - he never experience something like this or have any ideas?  Thanks for any help

    Hey Nathan,.

    Thanks for the ideas.  I ended up spending to playback of multiple samples as you suggested and this error has not popped up once again, so hopefully that fixed this issue.  I think I solved the problem of both weird thermocouple readings! I think that I had a ground loop problem which I fixed it by the grounding all thermocouples to a metal table.  For all those who on their getting odd unexplained readings, certainly experiment with ground everything correctly.

  • How to use the probe PT 1000 with NI 9211

    Hi all

    How to use a PT 1000 with NI 9211 temperature sensor?

    I am currently using Signal Express, just try to measure the temperature, but so far with no success

    THX in advance,

    Lasse

    A NI 9211 is a thermocouple device I.  A PT 1000 is an RTD.  While it might be possible to signal conditioning to get this to work, you're better off:

    Purchase of a thermocouple to replace the PT 1000

    Or buy a NI 9217 (RTD module) to replace the NI 9211

  • Reading of Thermocouple Type K with myRIO

    I have a myRIO (room only) and I need to read for an internal PID K type thermocouple measures.  I am able to do this directly in the room?  Or I need an adapter?

    Be as specific as possible.

    Thank you.

    The above listed connector is the connector for the card myRIO only.

    In addition, the thermocouple type k has a + and - sign. If the + needs to go to one of the analog inputs and - needs to go ALWAYS, analog ground. See page 5 of the below myRIO 1950 manual for the pinout of the connector.

    http://www.NI.com/PDF/manuals/376099a.PDF

  • NI9217 + CompactRio to measure two sons RTD resistance thermometer

    I have 4 two sons PT1000 RTD. How can I use NI9217 with the cRio-9024 to measure the temperature?

    I followed the link below, but I do not know where to put the module in mode 3-wire. Right now I'm getting + -1200 C, which must be wrong. And RTD0-3 are now available, but I need to use all of the 12 stations to measure RTD 4. I would appreciate any idea and help. Thank you in advance. I have attached two screenshots, which displays the property page for NI9217, and only 4 devices can be used in each NI9217.

    http://digital.NI.com/public.nsf/allkb/09E99F60C481D613862572C300637341

    Well, the unit has a range of 0-400 Ohms (she waits a RTD 100ohm) so throw a PT1000 in the system certainly will give him a max value output throughout the day temperature.

  • Impossible to get more than 1 channel to read with DAQmx cDAQ-9172 under Windows 7

    I have the cell load, voltage, and input thermocouple connected to a cDAQ-9172. My sensors entries have been scaled and verified in MAX, and all of them work.  DASYLab 13, the driver is "dcDASY.dll" and the hardware configuration is "NI MAX.

    When I add a task NEITHER-DAQmx Analog Input (that is, a set of scales) it appears correctly. If I add a second channel of the task and select it, I get this message:
    'Channel of task name saved with the module is not available. DASYLab resets the module parameters for usable first channel name task. »
    The name of the task remains the same for each new channel I have Add. If I change the name of the task by using the tab to the drop down menu, it says:
    "You have configured several ways out for the module. If you modify the task, you lose the settings. You want to change the task? »
    Both display the same data channels, and I can't work simultaneously several channels. It seems I missed something obvious, but I can't.

    The parameters are:

    Measurement and Automation Explorer 4.6.1
    NOR-DAQmx 9.0

    Material:-cDAQ-9172
    Slot 1 - NOR 9215 (0-10 Vdc analog voltage)
    Slot 2 - NEITHER 9211 (thermocouple)
    slot 3 - NI 9481 (relay)
    slot 4 - NI 9237 (entry deck w / excitement)
    housing 5 - OR 9402 (DIO)
    slot 6 - NI 9263 (0-10 Vdc output analog)

    Thank you

    You can't perform different tasks (continuous) HERE on a single chassis. The first tasks that starts will be 'the resource booking '.

    Combine the AIs of the various modules in a single task (see photo): start by creating the task of thermocouple. Then add AIs 9237 (e.g. Kraft) and 9215 (volts) using the button with the blue, symbol. Set the mode of synchronization of the task of "continue". Save the task, start DASYLab (second photo).

    Change a task (adding channels, etc.) to the MAX while DASYLab works always, will result in unexpected behavior. To synchronize the configuration of MAX with DASYLab, you will need to close/restart DASYLab or use the 'sync' of the function (see photo 3 "syncmax.jpg"). You can set this function as a shortcut by right-clicking on one of the eight green or grey circle things.

    You should think about an update of the MAX/DAqmx drivers. 9.x is a little outdated.

    Updated at least DAQmx 9.9, better 14.x or 15. 0 (stay far 15 1.x).

  • You try to run the scan mode and mode interface fpga at the same time is causing errors

    I'm reading a 9236 9237 and a 9215 with the scanning engine and read from two 9211 modules with the fpga. It's because I need to acquire to 200 Hz with the 9236 9237 9215 but maximum rate of the scan engine is limited by the slower module in the system, which in this case is the max of 15 hz the 9211.

    So to use both interfaces (scan engine and fpga), I followed the percisely given in this article for instructions.

    1. the project has created and added the peripheral crio using the interface of the scan engine.

    2. Add the target fpga and drag and drop the 9211 inside modules

    3. has created the fpga in interface file with and compiled with no error.

    4. interfaced with the file fpga at almost exactly the way the sample project of "getting started with 9211' by using the engine of analysis in the interface with the other modules.

    5. after the errors to discover that I created a VI that tests for just the portion 9211 code (called "thermocouple FPGA method Test.vi")

    The data returned by the interface fpga was nothing else than zeros on all channels, even if thermocouples were hooked on some of them. (all zeros as entries in the convert temperature vi gives-410, 6160 degrees F, if you happen to have the material to try this.)

    I get the following error from the open fpga vi reference:

    code error-61141
    "Thermocouple method Test.vi FPGA.
    Activities FPGA:

    Open FPGA interface reference.
    Reserved outside LabVIEW FPGA: turns The RIO Scan Interface. You must set the mode Interface FPGA chassis in order to unlock the FPGA. »

    It's extremely frustrating, because as I explained, I've been very attentive not only follow the instructions for concurrent fpga and analysis but also to model my VI by the example of VI, even if only for the moment, just to try to work things out.

    Any help would be appreciated as I need to fix this for the further development and I am somehow in a lack of time. I opened a support ticket (reference #7256226), but the app engineer had no time to answer.

    My system:

    cRIO-9014 controller RT with crio-9104 bottom of basket.

    LabVIEW 2009

    Latest drivers and peripheral software pc and rio (RIO scan 3.2 engine support june2009)

    rex1030 wrote:

    I'm reading a 9236 9237 and a 9215 with the scanning engine and read from two 9211 modules with the fpga. It's because I need to acquire to 200 Hz with the 9236 9237 9215 but maximum rate of the scan engine is limited by the slower module in the system, which in this case is the max of 15 hz the 9211.

    This should not be the case.  9211 data will not update with each sweep, but you should be able to run the scan faster than 15 Hz without problem.  Do you have specific issues with this?

    So to use both interfaces (scan engine and fpga), I followed the percisely given in this article for instructions.

    1. the project has created and added the peripheral crio using the interface of the scan engine.

    2. Add the target fpga and drag and drop the 9211 inside modules

    3. has created the fpga in interface file with and compiled with no error.

    4. interfaced with the file fpga at almost exactly the way the sample project of "getting started with 9211' by using the engine of analysis in the interface with the other modules.

    5. after the errors to discover that I created a VI that tests for just the portion 9211 code (called "thermocouple FPGA method Test.vi")

    You can try making sure that the chassis is set to mode Interface FPGA and the setting is deployed.  I wrote that article that you referenced says will select the deploy option later and not explicitly speak to deploy the chassis later.  Run a VI with a reference open FPGA vi not automatically deploy chassis settings if you need to do it explicitly.  Try the following steps.

    1. right click on the frame element and select Properties.  Make sure that the Interface FPGA option button is selected. \

    2. right click on the frame element and select deploy.

    3. repeat your VI.

    The data returned by the interface fpga was nothing else than zeros on all channels, even if thermocouples were hooked on some of them. (all zeros as entries in the convert temperature vi gives-410, 6160 degrees F, if you happen to have the material to try this.)

    I get the following error from the open fpga vi reference:

    code error-61141


    "Thermocouple method Test.vi FPGA.
    Activities FPGA:

    Open FPGA interface reference.
    Reserved for LabVIEW FPGA outside: The RIO Scan Interface is running. You must set the mode Interface FPGA chassis in order to unlock the FPGA. »

    The likely cause of this error is that the setting of the FPGA Interface on the chassis has not been deployed.  If the chassis is still Mode Scan fixed personality bitfile will be loaded on startup and the FPGA will be locked.

    It's extremely frustrating, because as I explained, I've been very attentive not only follow the instructions for concurrent fpga and analysis but also to model my VI by the example of VI, even if only for the moment, just to try to work things out.

    I'm sorry that you have had difficulties.  Assuming that I'm wrong about the source of your problem, it seems we have to update less than Ko to include the deployment step.

    Any help would be appreciated as I need to fix this for the further development and I am somehow in a lack of time. I opened a support ticket (reference #7256226), but the app engineer had no time to answer.

    My system:

    cRIO-9014 controller RT with crio-9104 bottom of basket.

    LabVIEW 2009

    Latest drivers and peripheral software pc and rio (RIO scan 3.2 engine support june2009)

  • Question of Shunt of LabVIEW

    Greetings,

    I'm working on a pump shrimp. I have problems of measurement of voltage across a shunt when tension, it reaches a certain point (~ 13 Volts or more).

    Reading, as seen in the excel worksheet, takes a dive until the voltage on another channel is measured under 13V (it is in fact through a voltage divider 1/5).

    Material:

    NEITHER cDAQ-9184

    NEITHER 9211

    NEITHER 9402

    NEITHER 9207

    R shunt = 0.0005 ohms

    I have attached the excel file of data where the measure of incorrect amperage appears in red. He did this on another pump as well.

    When the input voltage is greater than 13.0 Volts (on the 1st channel of the NI 9211), the shunt voltage difference (on the 2nd channel of the NI 9211) would jump down in value.

    It ruins my collection data will more 13.0 volts.

    I'm looking for advice on how to solve the problem. I'm not sure if this is a hardware problem or a software that needs to be changed.

    The volts are read by a voltage divider, but they have been accurate to date.

    Thanks in advance,

    -Tom

    It is the voltage to the DAQ entry that counts with this.

    For differential inputs, it is not the differential voltage that matters.  Each entry in the differential input must be less than 10.2V to the town (on the ground).

Maybe you are looking for

  • How can I get the game to Windows Vista, Microsoft Tinker back...?

    I had downloaded the Publisher Microsoft Tinker and don't like it and so I uninstalled it and I lost the game. I need to know how to retrieve. Can someone help me out here? I tried to get answers from other sites of computer on their forums, but noth

  • HP pavilion p6 - in 2356: white screen on the modernization of new NVIDIA graphics card

    I have a hp pc model no p6 product - 2356 in no #ACJ H3W39AA with windows 8.1 update installed on the computer. There already is an entry level graphics card NVIDIA geforce 620 installed in the computer as part of the specifications. However, I wante

  • change to dual display lamp

    I have a dv9825nr and the display only stay on for about a minute before going empty, an external a spare part works fine. It is a dual lamp screen and I have a simple fire spare screen.  can you replace a double lamp with a screen of single lamp as

  • Door hard drive

    I do not see button or whatever it is to open the door of the disk drive.  need to know how to open it, please.

  • Microsoft Word 2007. I have Windows Vista Home Premium

    Whenever I open Word 2007 I'm unable to use it. At the top of the Page of the Document, it says non-commercial use of Microsoft Word (not responding). I have to click in the Microsoft Info box that is displayed, the icon that says "Find solution and