Procedure closure and standard power for system UCS
Hi all
We have two Cisco UCS chassis with three blades B200M1 in each chassis. The two chassis are connected to two 6120 fabric of interconnections.
ESX 4.1 runs on each blade.
Please let me know if there is a standard and detailed procedure at the stop and power up the system.
Any information would be a great help.
Thank you
Arun
Arun,
Devices in the following order:
1. stop the blades
2 Disable Smart Call home (if enabled)
3 chassis (unplug the power supply)
4. cut the secondary current to FI
5 cut the power to the primary FI.
Before any maintenance please save your config UCSM two 'All' and 'Full '.
Reverse the order to supply the system upward.
Kind regards
Robert
Tags: Cisco DataCenter
Similar Questions
-
Difference between Enterprise Edition and Standard Edition for Oracle RAC
Hello
In our current configuration we have CARS on standard edition and customer is now considering to go to Enterprise Edition, but not yet to decide because of the cost.
Is there a difference between the Infrastructure of grid 11gR 3 Enterprise edition and Standard Edition?
They told me first install Enterprise Edition and then will move to Standard Edition if they can not get the EA license, so in this case do I have to re - install standard edition network infrastructure?
Kind regards
Chirag994551 wrote:
HelloIn our current configuration we have CARS on standard edition and customer is now considering to go to Enterprise Edition, but not yet to decide because of the cost.
Is there a difference between the Infrastructure of grid 11gR 3 Enterprise edition and Standard Edition?
They told me first install Enterprise Edition and then will move to Standard Edition if they can not get the EA license, so in this case do I have to re - install standard edition network infrastructure?
Hello
There is no "grid Infrastructure 11gR 3 Enterprise edition and Standard Edition", is the only Infrastructure of grid 11 GR 2.
On the Oracle Clusterware licenses (grid Infrastructure).
At least one of the servers in the cluster is allowed for the Oracle database (SE1, SE or EE)
A cluster is defined to include all machines that share the same Oracle Cluster Registry (OCR) and the drive to vote.
http://docs.Oracle.com/CD/E11882_01/license.112/e10594/editions.htm#CJAHFHBJOn the licensing database.
http://www.Oracle.com/us/products/database/Enterprise-Edition/comparisons/index.htmlNote: Oracle Real Application Clusters (Oracle RAC), is an option to Oracle Database 11 g Enterprise Edition and included with Oracle Database 11 g Standard Edition (on clusters with a maximum of 4 Sockets).
If you move to EA Oracle, you must purchase a separate license to use the RAC optionRegarding the Installation:
Nothing changes on your current installation of Grid Infrastructure 11.2
Just install a new fresh install to choose EF of the Oracle (the current clusterware) database during installation. Configure services database from this new HOME of ORACLE. Change anything on the database of all the previous backup and used functionality remains unchanged. With the help of this new House Oracle new features are enabled to be used by your databases.On the Downgrade:
Step by step procedure to perform the conversion from Enterprise Edition to edition Standard [ID 465189.1] -
I tried to call a script in a loop of a procedure of Jython, using startcmd.bat and sub-process; the command succeeds when I omit the "-AGENT_CODE = MySA_Agent1 ' parameter (highlighted and emboldened)
But omitting the '-AGENT_CODE = MySA_Agent1 "the scenario starts with the default value (no Agent) and subsequently fails to find the w: drive. Wen, I understand the '-AGENT_CODE = MySA_Agent1 ' the command fails with return code 2.
Also, it seems that the OdiWaitForChildSession will not work with this approach, because the sessions so are not recognized as child sessions at all.
Another simpler process is to have a step for each folder that I want to ask and just use OdiTools and StartScen; but it's a huge process because it could have potentially many interrogation records.
Please Guide:
from __future__ import with_statement
from com.ziclix.python.sql import zxJDBC
import of subprocesses
#GetSources.py
def getdata (c, stmt):
Try:
c.Execute (stmt)
except zxJDBC.Error, e:
raise Exception (e, stmt)
Another thing:
return c.fetchall)
driver, url, user, passwd = ("< % = odiRef.getInfo ("SRC_JAVA_DRIVER") % > ',")
'< % = odiRef.getInfo ("SRC_JAVA_URL") % >',
'< % = odiRef.getInfo ("SRC_USER_NAME") % >',
'< % = odiRef.getInfo ("SRC_PASS") % >'
)
Try:
subprocess.check_call ([' cmd',
'/c',
"dir" command
« t: »
])
except subprocess. CalledProcessError, e:
raise the Exception (e, ' Mapping The for the t: drive has not completed in the previous step. aborting... ")
Another thing:
folddic = {}
with zxJDBC.connect (url, user, passwd, pilot) as conn:
with conn.cursor () heart:
stmt = "SELECT SOURCE_SYSTEM, ABS (DIC - ROWNUM) FROM (SELECT SOURCE_SYSTEM, COUNT (1) DIC FROM DIR_USER.). (RÉPERTOIRES WHERE ACTIF = \ 'Y\' GROUP BY SOURCE_SYSTEM) ".
for the NTC in getdata (cur, stmt):
folddic [Str(CNT[1]) [:-2]] = cnt [0]
because me in folddic.iterkeys ():
Try:
subprocess.check_call ([' cmd',
'/c',
"startcmd.bat,"
"OdiStartScen,"
'- SCEN_NAME IS POLL_T_DRIVE_AND_SUBDIRS',
'-SCEN_VERSION = - 1',
'-SESSION_NAME = Polling_' + str (folddic.get (i)).
'-AGENT_CODE = MySA_Agent1',
'- SYNC_MODE = 2',
'-Interfaces.VarSubDirectory =' + str (folddic.get (i)).
'- Interfaces.VarPollInterval = 5'.
'- Interfaces.VarTimeout = 4'.
'- Interfaces.VarWait_N_Minutes = 30000 ".
])
except Exception, e:
raise the Exception (e)
Another thing:
Print "Called".
Hello
After much deliberation with the approach Prrocedure to do that are installed with the package, has been described in https://blogs.oracle.com/dataintegration/entry/using_variables_in_odi_creatin.
It takes away that the question of the child scenario waiting problem sessions will be managed ODI.
It was a good learning experience anyway.
Thank you for contributing A J Chantal Mangano
and JeromeFr for your taste.
-
Dell order and integration Suite for System Center Configuration manager 4.0
Hello
I just installed the Dell order and SCCM integration suite.
When you try to import a driver cab file to create a driver package, I get an error saying that the software could not recover present distribution points in the server.
I tried to install the suite actually on a distribution point, but got the same thing.
Any ideas?
Thank you
Close the Configuration Manager console. Then re-open it by right-clicking the icon and select run as administrator.
-
XP installation problem
while trying to install windows xp on my computer (processor i3), she shows looking for previous versions of windows and then crashes the system. So please give me a solutionHi deva_reddy,
Looks like you are trying to do a repair of windows xp installation.
You use a windows installation cd?
Refer to the link below for the procedure to install windows XP using different methods.
http://support.Microsoft.com/kb/978307
Hope the helpfu.
-
My parents bought a laptop from a friend, and recently my father ran an antivirus program that came with multiple files in a folder that has been created by this friend. When you try to delete the folder a box appears that says "it is a Windows system folder and is required for Windows work.» It cannot be deleted. "But all the folders inside are empty and of no use to us. Help?
The standard answer to questions that begin with «I bought a used computer...» "is you can do a clean install of Windows, because you know not what could be hiding somewhere in the computer. In this case, it seems as if he is infected with something.
Legally, the seller was required to give you a way to do this reinstall, but in the vast majority of the private sales of used computers, this requirement is simply ignored.
If it's a laptop to 'mark' (e.g., Dell, HP, IBM/Lenovo) there may be a hidden partition on the hard drive that can be used to restore the computer to its "fresh from the factory" State. Of course, this will remove all applications that the previous owner had installed after he or she has bought new, but you should still seriously to consider making such a restore, if the mechanism is available.
What is the name and the version of the antivirus application that has detected the wrong files?
What are the names of the files?
What is the name of the folder that cannot be deleted?
Are you logged on as a user with the rights "computer administrator" when you try to delete it?Assuming that you can not or will not do a clean install of Windows, I suggest the following (do not run scans at the same time, each analysis may take some time, depending on the number of files on the computer):
Connect as a user with the privileges "computer administrator" and do a full scan with each of the following:
http://www.eset.com/us/online-scanner
http://www.Microsoft.com/security/scanner/en-us/default.aspx (requires download)
http://www.PCtipp.ch/downloads/Sicherheit/35905/multi_av_scanning_tool.html (page is in German, but the downloaded scanner is in English)Also download, install, update and run a scan complete with each of the following:
-
I HAD TO REINSTALL WINDOWS VISTA (SERVICE PACK 2) DUE TO A TROJAN HORSE THAT ATTACKED MY SYSTEM. I USED THE SUPPLIED RECOVERY DISCS SET WITH MY COMPUTER BECAUSE THE SOFTWARE HAS BEEN PRE-LOADED AND I HAVE NOT RECEIVED SOFTWARE FACTORY. WHEN I WAS SETTING UP USER ACCOUNTS, I CREATED THE ACCOUNT TO ADMINISTRATOR (WITH PASSWORD) AND A STANDARD USER ACCOUNT. WHEN I CHANGE THE SETTINGS IN MY COMPUTER IN EACH ACCOUNT, IT DOES NOT APPEAR THERE EITHER ACCOUNT. I DO CHANGES IN PARAMETERS OF EACH ACCOUNT INDIVIDUALLY. CAN I SET UP SO THAT WHEN I CHANGE THE SETTINGS, IT WILL DO THAT IN THE TWO ACCOUNTS? THANK YOU FOR YOUR HELP.
original title; HOW TO CONFIGURE WINDOWS TO ALLOW THE SETTINGS AND SOFTWARE DOWNLOADS APPEAR IN ADMIN SYSTEM AND STANDARD USER?Most PC manufacturers who don't give you the disks give you a partition on your hard drive that contains the images of the disks so that you can burn yourself. You should check out.
When you say "change settings in both accounts' exactly what are the parameters what do you mean? It is normal that many Windows settings to be on a per user basis. For example. the desktop background is a 'definition' which is completely independent for each user. You cannot set up a wallpaper for a user and hope that it displays desktop of another user.
-
Hi all
Recently, I replaced a non redundant power supply on my Dell Poweredge R410. During troubleshooting, I also temporarily removed the battery from the system at any given time.
The server is back up and running, but when booting, I get:
"The 4 fan speed can change in installation configuration feature and the option card systems
Press F1 to continue, F2 to run the configuration utility.
I think that some BIOS setting reset to remove the battery? I also see a lot of forum posts mentioning the cause of this error is the integrated SATA is connected to anything.
My hard drives are connected to a PERC via the PCI slot, and the machine has an optical drive. I don't see the existence of the optical drive in omreport.
Here are a few outlets omreport about SATA settings.
Integrated SATA controller: ATA
SATA port 0: Auto
SATA port 1: Off
SATA port 2: stop
SATA port 3: Off
SATA port 4: OffAny advice on how to go about this debugging more?
Thank you!
Dave
Yes, it is possible that the optical drive is defective. Check the logs of equipment. Also enter the system BIOS setup using the F2 key and search for devices listed as unknown.
-
Is possible let activate domain multi UCS VM - FEX and sign up for the same vCenter
Hi Experts,
We have 7 domain UCS. But only a vCenter. Now, we want to enable VM - FEX on each UCS area and sign up for the same vCenter. Is - it work? I have found no description limit configuration on this relationship.
Or we create 7 vCenter for each UCS area? (But I think it's not sense.)
Best regards
Meng-Yuan Hsieh (Nick)Hi Moua!
I open a TAC case on that, and after that many discussions with Cisco, connecting several areas a single vCenter UCS is supported. However, it turns out that Cisco failed to document this and how to make it work. You will find that the procedures were written in old documentation for VN-LINK and others for VM - FEX. This documentation shows that it is necessary to create new certificates, and it must match the key to expansion. This is NOT true nor with the new versions of UCSM and vCenter. Cisco, said they will update their documentation.
Here are the steps that we took to connect two UCS areas for the same vCenter using default self-signed certificates. I hope this helps... Please mark this message as the right answer when you get a chance. Thank you!!
vCenter Version: 5.5
UCSM Version: 2.2(5a)
- On the VM in UCS Manager tab, click VMware.
- Set up a key of the unique extension for every area of UCS.
- Click on "Configure VMware integration" on each area of UCS and export expansion of local storage.
- Install each UCS domain extensions in vCenter.
- After you install the extensions, back to UCSM and click Next where you left off in configure integration with VMware
- Run the wizard and after that it's over, areas of the UCS should now be connected to the vCenter.
-
Upgrade GPU for Studio XPS 435MT and indine power load max
Hi, I have a Studio XPS 435MT with a 360W power supply and an ati radeon HD4800 series GPUs (likely a 4850). I want to improve the gpu with a gpu from Gainward GeForce GTX 750 2 GB (one slot), GDDR5. It uses just 55W and there is no external power supply plug, the HD4800, but in the GTX card appears: minimum 300W or more system power supply (with a minimum of 12V current rating of 20A). And I do not know if this 20 a could be a problem, because my Delta DPS-360FB-1 diet doesn't seem to reach the rated current.
What do you suggest me?
Thank you
combined maximum 12V 12VA and 12VB output for this unit is 300W which is 25, but you can't have your cake and eat it too.
If you draw 20 amps on the 12v rail you used 240W leaving 60W for everything else that needs 12V.
And if you use 300W on the 12v rail that leaves 60W max for the 5v / 3.3V through less 10W to + 5VSB.
GTX 750 will be in this case either well, or it does not at all due to the lack of power on one or more tracks.
HD4850 certainly consumes MORE energy than a GTX750 so that only one point of view, it should be good.
-
I have adapters and converter of power for international travel. I was told by someone who often visits that the converter is not necessary for apple products. I don't want to ruin my phone or watch - can I use my power converter?
If you use the Apple adapter supplied, you will simply need an adapter to use in other countries. The adapter can be used with voltages between 100-240 v AC 50-60 Hz
-
Satellite 1410-604: I lost the screen saver and power management system
I have a Satellite 1410-604. I lost my screensaver and cannot access the Toshiba power management system: I click and nothing happens. I saw a suggestion to run the system restore. When I go to system restore it says it is running, but is there something more specific that I can do?
Thank you!
I put t know what you did with your operating system, but more often if the system restore option enabled, then it shouldn't be a problem to restore the operating system to the beginning
Simply, start the system restore and choose the starting point that was automatically created.I also found this useful FAQ:
http://support.toshiba-tro.de/KB0/TSB6B01MB000BR01.htmWhat about installation? Have you created an image?
-
I plan to upgrade my OS to El Capitan. What are the processor speed and memory required for the operating system works well?
I use a processor 2.3 GHz Intel Core i5 with DDR3 4 GB 1333 MHz memory.
My last similar attempt on another machine resulted in a very slow computer.
Thanks, Ron
Apple says the following:
General requirements
- OS X 10.6.8 or later version
- 2 GB memory
- 8.8 GB of available storage
For best performance, I would say not less 4 GB and preferably 8 GB or more.
Your i5 is well able to support properly.
http://www.Apple.com/OSX/how-to-upgrade/#Hardware Configuration
-
Forgot administrators and the power on password for my hp pavilion g6 with windows7. Halt # 80147381 thank you.
Hello
Try: 35825907
-
I bought my new laptop exactly a month before Windows 7 was released and standard for all new laptops. Can I upgrade to Windows 7 for free, or at least some discount?
Thanks in advance,
DonatContact the manufacturer or ask in this forum instead: http://social.answers.microsoft.com/Forums/en-US/w7install/threads ~ Robear Dyer (PA Bear) ~ MS MVP (that is to say, mail, security, Windows & Update Services) since 2002 ~ WARNING: MS MVPs represent or work for Microsoft
Maybe you are looking for
-
Conversion of Word for download at the Web site
I have a MacBook Pro and I have a number of files in Pages I need to download from a Web site in Word. I don't have software haveWord. How can I do this? Thank you.
-
Hi all. (My laptop is configured with 3) USB 3.0 ports and 1) USB 2.0 port. 2 ports are located @ front left side, and the other 2 are @ right rear of connecting the power supply... How to distinguish between USB 2.0 and 3.0?
-
Control that supports copy - paste from Excel?
Hello! Is there a control that supports the cell simple copy - paste from Excel? I make a program and a large amount of data I can imagine my user copy - paste from Excel spreadsheets. The tables do not work and the Table controls do not work... I f
-
Someone or something is somehow sending emails to spam from my email account with obscene language.
-
Blue Screen installation updates (KB2419640) & (KB2478935) for Windows Vista
I get the blue screen when I install the above, and this update was 12/01/2011 and continues to reappear after I restore the system to January 9. So I turned off auto updates but isn't this bad since I DON'T want to prevent remote control? What can