Scaling DAQ Assistant

I'm looking for help with the DAQ assistant,

I have a signal 0-20 my. I want my card 8 to 100 and 16 my to-100. I entered y =-x + 300 25. I put I. Max = 300 (x = 0 my) and AI. Min = - 200 (x = 20 my). I get the following error:

Error-200077 occurred to the DAQ Assistant
Possible reasons:
Requested value is not supported for this property value. The value of the property may be invalid because it is in conflict with another property.
Property: AI. Min
Asked to value: - 200.0
Valid values begin with: 299.500000
End with valid values: 300.500000

When I get 300, I get the following error:

Error-200082 occurred to the DAQ Assistant
Possible reasons:
Minimum is greater than or equal to the maximum. Make sure that the maximum value is greater than the minimum value. If you are using a custom scale, check that the maximum on the scale is greater than the minimum scale.
Property: AI. Min
Value: 300.0
Property: AI. Max
Value: 300.0

What I am doing wrong?

Thank you, but I just found this one. I use the range mapped instead of the linear range. Not sure why it makes a difference, but it works!

Tags: NI Software

Similar Questions

  • DAQ Assistant does not export the values on the scale

    Hello all-

    Potentially stupid question but here goes: I'm using the DAQ Assistant to read in 4 analog input voltages, continuous sampling acquires data at 10 Hz 1 point, using LabView 12 on a machine with an acquisition of data USB-6341 simulated device (because my office is more comfortable than the lab!). I want to change the first two signals of voltage to temperature and humidity, respectively. I used the «create a new...» "in the 'Custom Scaling' drop-down in the"Voltage configuration"tab for each of these channels, named gave the slope and the intercept at the origin for the respective linear scales and click OK."

    When I test the code - and yet once again, I'm not on a machine with a 'real' DAQ system, I use a simulated device, and it seems that NEITHER MAX generates a sine wave of long period with little noise on top for this - I do not get the results on the scale of my 'signal', I get the raw tension. (If you run my code, I will join, the Relative humidity must be between 0 and 100 and temperature-40 to 60, is not 0 to 5, for example.)

    So, what happens? Is there some flag or setting that I missed? The scaling only works on voltage data 'real' of a 'real' instrument DAQ, instead of a simulation (which is why I mentioned twice!)? I have to do something in NI MAX as well as Labview?

    Thanks for any help you can give.

    John Easton

    Simulations devices will not respond to custom scale.  They are just supposed to allow you to configure your device without errors when you do not have the unit on-site.

    "NOR-DAQmx simulated devices create a noisy sine wave to all the entered analog." Simulated data other set-up is not available at this time. »

    http://www.NI.com/white-paper/3698/en

    They generate a sine with an amplitude equal to half of your specified input range.  If you want to work with simulated data that would be more realistic for your application, you could write a VI to generate the data and have a business structure to manage both "simulations" and "real", then you could switch back depending on whether you have access to the material.

    I just checked this with a PCI-6254 I install and simulated a PCI-6254.

  • Calendar and the problems of data collection with the DAQ Assistant

    Hello NOR Developer area,

    I am a Novice of LabVIEW and have seen how helpful you all can be, and if I come to ask for your help.

    I'm having some trouble with a VI I built that specifies an input voltage, a SCB - 100 connected to a PCI-6031E and converts this tension in a temperature displayed on a waveform table. The goal is to give a constant reading of the temperature and display it in a chart for as long that the VI is running (and to reset the chart the next time the tracks of VI).

    The problems I've encountered currently are:

    -After a few minutes of the VI running, I get an error message 200279: tried to read samples that are no longer available. The requested sample was already available, but has since been replaced. (to the DAQ Assistant express VI).

    -I don't know how to change my chart so that the minimum value X is both during which the VI was launched and have the maximum X value increases with each iteration of the loop. Currently, I have the VI get the time system and contributing to the property node X scale. This worked for the graph of the voltage, but not for the temperature chart

    I appreciate those of you who took the time to read my post.

    Thank you all for your help.

    Sincerely,

    Ethan A. Klein

    SB candidate in Chemistry & Physics

    Massachusetts Institute of Technology

    Class of 2015

    PS I enclose my VI to give you a better understanding of my current situation.

    E A Klein wrote:

    Thanks for writing.

    What property node is talking?
    I do not understand that many different data types. How can I go on the treatment of all the data?

    (Did you mean I should wire 'blue' data for mathematical functions rather than using the node property tension?)

    Sincerely,

    In fact, one of the nodes property.  I mean specifically the tension property node.  But in reviewing, I noticed the other nodes in property for the chart.  Just set auto-scaling to the X scale and that should take care of two of the nodes property (right click on the graph, X scale-> AutoScale X Scale).  I also recommend placing your mathematical functions in a Subvi to make things easier to read.  Attached, that's what I think you're after.

    I hope that these small tweaks will speed things up enough to avoid your error.  If this isn't the case, then we should begin to look at the design of producer/consumer model or take readings at the same time.  It might also be worth looking away the DAQ Assistant and DAQmx real screws.  But one step at a time.

  • DAQ Assistant is not in LabView

    Hi all

    I use NEITHER cDAQ-9174 and NI 9203.  I have already installed the driver for the NI 9174 cDAQ, which is NEITHER-DAQmx 9.8.0.  I can see the device when I opened NI MAX. However, when I open LabView 2015, I can't find DAQ Assistant in the function Palette. I noticed on the chassis, 'ACTIVE' light is not on while two other "POWER" and "READY" light is on.  I look in the forums OR but I can not find the solution.

    Any suggestion, please help!

    Thank you!

    DAQmx 9.8 is not compatible with LabVIEW 2015.  You must use at least DAQmx 15.0.  See here for more details: NOR-DAQmx and LabVIEW compatibility

  • 201003-error occurred in the DAQ Assistant

    Hello. I use "cDAQ-9178" and "NI 9215" and "NEITHER 9402" are added on. "

    However, when I run Labview code, "Error-201003" occurs.

    {

    Device not available. Possible causes:

    Device is no longer present in the system / device is not powered.

    Device is turned on, but was temporarily without electricity / device is damaged

    }

    (Error appears as the 1st and 2nd figures below).

    (Plans of logic is the figure below).

    Thank you.

    I could be something with the pilot

    Check this box:

    Error 201003 to the MAX test panel or all by running the DAQ Assistant

    http://digital.NI.com/public.nsf/allkb/5413F392D88326148625746B006745C5

    In this forum, they speak the same error:

    Spontaneous error code 201003 for acquisition of data PCI configuration

    http://forums.NI.com/T5/SignalExpress/spontaneous-error-code-201003-for-PCI-DAQ-Setup/TD-p/830707

  • Control relay with Boolean switch using DAQ assistant 9481 - problems

    Sorry for what may be a stupid question but I'm stuck in quicksand.

    I use a relay module 9481 and have two external relays connected lines 0 and 1.

    When I create a digital output 0 line by line, I can run the test inside the express and activate the relay and turn off without problem.

    The generated block DAQ expressed expects a Boolean input of 1 d. (See attached photo).

    I want to connect a Boolean switch relay line disk 0. You can connect live not because the switch is Boolean and the input is Boolean 1 d - I'm a conversation in the pict.

    All plumbing lines display results, the relay never active.

    Any bunch would be greatly appreciated! Thank you

    Mr._Mechanical,

    Welcome to the Forums of switch OR this forum is generally intended for products OR-SWITCH [such as the NI PXI-25xx & NI SCXI-11xx], I think I know the answer to your question.

    I think the reason why it's a failure is the conversion you make generates a table of 16 Boolean [as the 'boolean to (0,1)' function creates a data I16 type] with your data more false data points 15.

    When you try to control the relay, he sees 16 datapoints are you Commander to a single port [channel] and so error out.

    My suggestion would be to use normal DAQmx digital output screw [with, he set up as ' Digital > single channel > single sample > Boolean (1 line) "] rather than the DAQ assistant.

    If you use the daq assistant, simply by using the function 'Building the table' will transform your simple Boolean data point in a Boolean array containing a single element.

    While the DAQ assistant is very easy to use, I recommend that you use the DAQ assistant, because this reduces the features and increases the execution time.

  • Simulate signals wired to the DAQ assistant for USB-6009 device

    Hello

    I'm trying to send a signal to the DAQ Assistant Express VI.  I watched the movie "Generating a Signal" on the Web site of NOR (www.ni.com/academic/students/learnlabview/generate.htm) and I have my Signal simulate connected directly on the DAQ Assistant, as shown in this film.  In my case, the DAQ Assistant sends the signal to a device USB-6009.

    However, I received this message:

    Error-200077 occurred to the DAQ Assistant
    Possible reasons:

    Requested value is not supported for this property value. The value of the property may be invalid because it is in conflict with another property.

    Property: SampTimingType
    asked the value: Sample clock
    You select: On-demand

    If I select 'On Demand' in my DAQ assistant and run the vi everything works beautifully.  However, I need my DAQ assistant to be configured to generate a waveform AC continuous, not output a single alternating current rippling.

    What happens here?  I did not have this problem before on other devices of NOR. I am using LABView 2010.

    Please answer.

    Thank you.

    double post

  • Under VI 'DAQ Assistant': Sub VI is not executable

    Salvation OR engineer,

    My task is to acquire and record data of input voltage analog with PCI-MIO-16-1 and BNC-2110 connector. I can get the signal via MAX, but as soon as I drop down the function palette DAQ assistant in FASHION Lab blocks diagram, my run button becomes broken. I got the error message like "Sub VI"DAQ Assistant": Sub VI is not executable. How can I overcome this?

    Thank you

    Yvette.

    Hi Paul,.

    Unfortunately, SignalExpress is a different license than LabVIEW. However, you don't need a SignalExpress to acquire and record data. LabVIEW has every ability to SignalExpress and many more.

    Kind regards

  • Multiple entries to the DAQ Assistant

    Hello

    I'm doing my DAQ Assistant, in several (formed of an array) Boolean inputs where there is 1 digital output. (see attached software folder)

    Physically, I want a valve to open and close at a certain pace, where the user can install/control this pattern until the program starts.

    I think that the best way to do it is to have multiple Boolean values that the user can press or unpress.

    Before that, I started, I tried with only Boolean 1 where it worked perfectly.

    As seen on the attachment (error), it is possible to an easy problem to solve, but I just can't figure it out, I'm stuck at my already made solution.

    I use USB6008.

    I hope that there is a gentle soul who can help out me.

    Best regards

    Kenneth G. Vejen

    Hi Kenneth.

    When the output to the generation mode is set to "sample 1", which means that whenever you call the DAQ Assistant will generate 1 sample. In order to generate 5 samples, you must therefore call 5 times.

    I have attached a modified version of your VI, which shows a way to archive it. However, be aware that the samples will be generated fast and not at 100 ms note your loop runs. It depends on your application, if it is as you want samples to be issued.

  • Calibration of thermocouples in the DAQ Assistant, using data from spreadsheet?

    Hi all

    For my first application LabVIEW, I'm looking to automate the calibration of thermocouples by measuring their response at different temperatures in a dry well Sizer. I get temperatures of thermocouples six by SCXI 1303/1102/1600 and have six channels put in place in one of my subVIs in the DAQ assistant.

    I compare these values to temperature calibrator that I am acquiring by VISA series in an other Subvi. All these values are written in a .csv file.

    Can I import these data into the DAQ Assistant to use for calibration? Is there a simpler way to associate with the channel calibration data? Currently, I could manually copy - paste the cells on the worksheet in the calibration sheet, but that seems just silly.

    If there is everything that I could provide to help solve the problem, let me know!

    Thank you!

    Hi Zoysiamo,

    It is possible to automate the calibration screws DAQmx at a lower level, in particular the DAQmx channel property node. Using you can specify advance nationwide and the values on the scale for your channel. I recommend you take a look at this example of the community. The property node configuration will be similar to, as illustrated below:

  • DAQ Assistant stopped working

    Hi all

    I have labview 8.6 installed on my laptop. currently of the problems with the DAQ assistant. When it initializes the host of assistant OR no longer works and an unknown error message is given. Don't know where to get corrupted files etc my daq is a usb-6008 and my laptop is running windows vista. I think that the issue is to do with a driver in the folder of Max but I don't have enough experience with her. I currently install OR-DAQmx 9.0.2 in the hope it will solve the problem. any help on this would be greatly appreciated.

    Kind regards

    Jason

    Hello jpraffer,

    Install the DAQmx helped 9.0.2 or you're always to see the current issue.

    Kind regards

    Philippe

  • Missing DAQ Assistant

    Hi guys,.

    I have LabVIEW 2015 and 14.0 DAQmx.

    Yet, the daq assistant is absent the express--> palette entry.

    Any help?

    Message 5 of this thread will give you the answer.  More precisely

    DAQmx and LabVIEW version compatibility

  • Error of the DAQ Assistant

    I've just updated LV 2009 SP1 LV 2010. I use a LV 32-bit on a 64-bit computer.

    When I open the DAQ Assistant, I get a pop up window that says "LabVIEW: an exception occurred in the external code that is called by a function of the call library node."  This could have corrupted memory of LabVIEW.  Save all work to a new location and restart LabVIEW.  VI "Advanced Timing.vi:1" was arrested in node "" a call to "get of DAQmxAssitant_DAQmx IO Info.vi of control.

    If I hit OK, DAQ Assistant is locked up, if I use the Task Manager to close the LabVIEW vi breaks down.

    I already reinstalled 9.5.1 DAQ device drive. without success.

    There is no such version. The most recent is 9.2.2.

  • DAQ Assistant acquires the data into segments

    I'm writing a code that reads and records the voltage, temperature and pressure on a cdaq-9174 using or 9221 and cards or 9173.  The problem is that when the daq assistant is set to N samples outputs the data blocks in the graphics.  I wish it were a continuous stream so I can see what is actually happening.  I tried to change continuously, but it gets an error or is has data about 16000 points in 10 seconds, which is a lot more that I prefer.  The code I am using is borrowed from another person and then the installation exactly it works on this computer, but not mine.  Does anyone have any suggestions on how to solve this problem.  I enclose the code as well as the sub live he uses.

    Thanks for all the help.  I didn't know at first that the NI 9237 card has a minimum sampling rate of ~ 1600 Hz.  I am now able to taste to 2000 Hz then use decimating continues to write in my file at 200 Hz.

  • Second DAQ assistant in the power control system does not

    Hi all

    I need your help on this issue. I'm currently programming a VI for one command power supply for pool boiling experiments. The organizational structure of the VI program is attached.

    I use two assistants DAQ for steady-state acquisition and temperature unstable state data respectively. The first assistant DAQ (samples to read 5, 5 Hz rate) for the acquisition of works unstable state data well (see the attached image file first DAQ Assistant for acquisition of temperature unstable state). The second assistant DAQ (samples to read 12 k, 200 rate) for stationary data acquisition does not work (please see attachment image Second Assistant DAQ of steady-state temperature acquisition), showing only a series of data files size of 1 KB with no data on the inside. And indicators for steady-state data also revealed nothing.

    After a similar Q & A search in the forum, I tried to distribute different channels for 1 and DAQ assistant 2. However, the situation was almost the same.

    The material I used are chassis SCXI 1000 and SCXI 1303 Council to acquire thermal couple temperature data. Food was AMREL SPS200-50-K025. LabVIEW software is the 2014 version.

    I had just started to learn LabVIEW for only a month, and I know that the VI is a little messy. Hope you guys can also give me some advice on how to improve this VI.

    Have you looked at the error on the second daq assistant? You will see that a reserved resource error because you cannot use two different assistants. You do not mention the real DAQ hardware but there a clock unique convert. You can use only one assistant with a unique sampling frequency.