Application built with an OPC Server

Hello everyone
I build the application on the development using wich S7 computer - connected to the OPC Server 1200
and I want to build the application to run the VI on another PC without installing labview, however when I finished to build the application with the installer and install the application on another PC it cannot connect to shared variables so I installed an opc Server ON this machine and add the server to the software mutual FUND that contains tags and variables
but it is not also connect to the opc Server
So how do you run the application on another PC with an opc Server!
How the VI to use a specific opc server on this PC with no labview?

Hello

What do you call the OPC Server? You are creating a mutual FUND of LabVIEW client and linking to the shared variable? If this is the case while you use the LabVIEW DSC module and it works very well in the development environment.

However, every time that you deploy (creation of executable or installer) a VI using DSC module, you must have a license to run on each computer that runs the executable file. http://sine.NI.com/NIPs/CDs/view/p/lang/en/NID/210561

the alternative would be to use the socket api in LabVIEW to call the server.the attached VI OR OPC illustrates how.

I hope this helps!

Tags: NI Software

Similar Questions

  • Problem with Photos Soft - error message the application built with PhotoLibraryPrivate version 215.65.00 but works with version 209.52.00

    Hello, hope someone can help with my MacBook Pro sluggish.

    I'm in OS X Yosemite 10.10.3 version and tried to upgrade to El Capitan 10.10.5 on a Macbook Pro 13inc mid-2012.  He said it has already downloaded twice, but when I open the software it is still sitting at 10.10.3 without modification, download seems to take a lot of time - been sitting for about 6 hours.

    Now I trying to open the photos app but get the following error coming - the application built with PhotoLibraryPrivate version 215.65.00 but works with version 209.52.00.

    Any advice on what are the options for my new photos app! Have you tried different time machine backups and the computer does not like it either

    Upgrade to El Captain OS X 10.11.2 which includes Photo 1.3

    I have no idea of what you see on "El Capitan 10.10.5" as far as I know is not exiat

    LN

  • cRIO communication as a PLC with NOR-OPC-Server

    Hello

    I have the task to implement communication between multiple cRIO and NOR-OPC-server. The OPC OR server should act as a data manager for a complex interface.

    I tried the NO-OPC Server and I managed to communicate with the server OPC-NOR as OPC-Client in Windows using a server IO and shared Variables. But the task is to do it on a cRIO. I tried to open a data from a cRIO socket connection to the NOR-OPC-server using a specific URL by using "DataSocket select URL.vi." But as long I do not activate the simulation in the OPC Server - OR-I get errors on the data socket connection opening. If I activate the simulation, which is not the solution, I can write data without error, but the quick OR-OPC-Server Client sees no change for the data label.

    I have the feeling that I am not a good way to get this working. Is there anyone with experience with this? Is data taken one possible at all? It is possible at all? I have to put in place a cRIO-OPC-driver?

    Thank you.

    Hello

    I found the solution in this article:

    http://www.NI.com/white-paper/7451/de#H36

    Thx for your help.

  • Apple begins to reject applications built with DPS?

    So, I built some cool interactive apps NAV, side shows and even one with more than 500 items.  Apple has rejected all of them. Now, I know I'm not the best designer out there and I did the test we may friends and clients, and all everyone thought it looked good and is easy to navigate and use.

    Here is the response from Apple.

    We have found the following issues with the user interface of your application:

    -A was only a PDF

    -Do not integrate the features of iOS. For example, the user must be able to interact with the content of your application, such as sort, list, bookmark, customize, etc..

    N ' not include features of iOS. For example, it would be appropriate to use the native iOS and iOS features other than just views web, Push Notifications or sharing.

    These examples to identify the types of problems found in your application, but don't represent these questions. Should carefully evaluate your application to respond to these types of problems.

    How can I solve this?

    This happens sometimes with simple editing applications. The dismissal of the appeal and you report of specific locations in your publication when you add interactivity. If it is a publication of article 500 + they may not have noticed the.

    In particular, point out the places where you use multi-state objects and scrolling images. In addition, make sure you mention your publication in book form and it does not send to book category in iTunes.

    Neil

  • Good way to check that an application built with SDK v10.3.1 works for 10.2.1

    Hello

    My application uses the SDK v10.3.1. A user asked me if it can be compiled to support v10.2.1 as well.

    Is there a formal procedure to verify this?

    Thank you

    You need to test yourself with a device running 10.2.1 or a simulator. Change your file bar - descriptor.xml to assign the minimum OS 10.2.1 there is also a blue text on the same screen of bar - descriptor.xml file saying API level or something, be sure to set for 10.2.1. If your project is a headless application, left-click on your project without head, choose Properties or preferences or configure (don't remember), there will be somewhere to change the level of the API for headless to 10.2.1. Clean and rebuild your project (s).

    All your QML file must import bb.cascades 1.2 instead of 1.3, otherwise it displays a black screen at startup where nothing happens.

  • How to install the OPC Server with the Application Setup

    Hi all,

    I make the datalogging progam in the PLC via modbus communication using the OPC server.

    1. I got configer the opc via the Project Explorer client some time it works perfectly, but when I run it by the next day, he cannot communicate with an OPC server but the OPC server is to communicate with the PLC. When I right click on the properties of the customer e/s in the exploer project opc and make any change and still run the application it works where is the problem.

    2. the second problem is by building the installer that will be installered to my PC targate OPC server. Bacuse I had installed the application on the computer target just for testing but OPC Server havn't installed even if there is no option for adding the OPC while bulding server.

    Serdar, SALVATION

    Thanks for the reply I saw your example, your idea is ok, but if I have more then 100 and with different types of data tag then where is the problem to manage all these tags.

    Now, what I had done I took the express to create vi or configer server I/O and give the name of the process even as file name as opcdemomo and same server name reference in the Project Explorer and restart and scream in low tow and three times it works I havn't get any problem.but which is not the right method. 

  • Error when you try to run an application that worked when built with 8.6

    I have a simple program that I wrote in the 8.6 version that I've never had a problem generation and execution of applications built with it to 8.6.  Two weeks ago, I got 2009 by mail because we had very recently purchased 8.6 and I get errors when you try to run an application built with the same code using 2009.  The error relates to the Mean.vi.  He claims that he can't find it.  The error I get is as follows:

    Error loading VI 'NI_AALBase.lvlib:Mean.vi '.  LabVIEW support 3 error code: could not load façade.  I don't have access to the front panel of this vi, so I wonder if there is a problem with the runtime and not my code.  Please answer as soon as possible because it will quickly start to the impact of my calendar.  Thank you.

    Hello!

    The same problem ?

    I talked with my local OR technical support team. The application now works without any problem.

    Rule of thumb: when creating a Setup program do not forget that the option "Run Time Engine xxxx" in the category "Other installers" is selected despite the fact that the runtime is already installed.

    Best regards.

  • problem with a 2012 opc Server

    I use LabVIEW 2010. I installed OPC Server 2012. Configure DCOM. Create tags OPC Server

    Create the project and create opc client

    But I don't see the tags in the variables:

    Can someone help me, I don't see why tags?

    What is under the OPC2 folder?

    Also, I checked my 2012 OPC Server readme (start > all programs > National Instruments > 2012 an OPC Server > Readme) and he said:

    "You can use the OPC servers OR with the following software applications:

    • LabVIEW 2011 SP1 full or Professional Development System
    • LabVIEW DSC Module 2011 SP1"

    This may mean that it is not compatible with your version of LabVIEW.

  • All 32-bit applications crash with error 0xc000005 after windows Server 2008 R2 backup

    Hello world...

    I am in a big mess... and really need help!

    I did last night a Backup windows... but one of my users were connected to the server works with applications...

    and this morning No 32 no bits applications... same installer...
    the 64-bit application works very well...

    Others or generating an error 0xc000005 and stop...
    failing Ole32.dll module...

    And I'm sure that the backup is reliable, even if the backup of windows said it was successful...

    I tried to restore only the apps files... but it seems more complicated than that...

    If anyone has an idea...

    Hi, Emeric,.

    Thanks for posting the question on Microsoft Community.

    According to the description, it seems that 32-bit applications crash with an 0xc000005 error code in Windows Server 2008.

    As the question more appropriate forums Technet, write the topic in this forum for better support.

    http://social.technet.Microsoft.com/forums/en-us/WindowsBackup/threads

    Using the windows-related issues feel free to post on Microsoft Community.

  • Event ID 10016 - the application-specific permission settings do not local Activation permission for the COM with the CLSID server application

    Lately, I'm getting this system error a lot now that I've upgraded to Windows 8 Pro is an event DistributedCom 10016 ID. Here is the text of the error:

    The application-specific permission settings do not local Activation permission for the COM with the CLSID server application

    {D63B10C5-BB46-4990-A94F-E40B9D520160}

    and APPID

    {9CA88EE3-ACB7-47C8-AFC4-AB702511C276}

    the user NT AUTHORITY\SYSTEM SID (S-1-5-18) from the address LocalHost (using LRPC) running in the container of the application unavailable SID (not available). This security permission can be modified using the Component Services administrative tool.

    Anyone has an idea why I get this error?
    Walt

    Same thing here. Grayed. Windows 8.1 seems to fill the observer of events with many more errors than previous versions.

    Edit: OK, discovered why it is grayed out. There are 2 reg key, you must set permissions before going to the Configuration of DCOM in component services. The CLSID key and the APPID key.

    From another forum, although it applies to a different application, same principle:

    1. open Regedit.
    2. go in HKEY_Classes_Root\CLSID\ * CLSID *.
    Note: * CLSID * stand for the ID that appears in your event viewer error. In your case, it is {C2F03A33-21F5-47FA-B4BB-156362A2F239}.
    3. right-click on it and select authorization.
    4. click on Advance and change owner to administrator. Also click on the box that will appear below the threshold of owner.
    5. apply a full control.
    6. close the tab, then go to HKEY_LocalMachine\Software\Classes\AppID\ * APPID *.
    Note: * AppID * is the ID that appears in your event viewer. In your case, it is {316CDED5-E4AE-4B15-9113-7055D84DCC97}.
    7 right-click on it and select authorization.
    8. click on Advance and change the owner to administrators.
    9. click on the box that will appear below the line owner.
    10. click on apply and grant full control to the administrators.
    11. close all tabs and navigate to the administration tool.
    12. open component services.
    13. click on the computer, click my computer, and then click DCOM.
    14 find the corresponding service that appears on the display of the error.
    15. right-click on it, and then click Properties.
    16. click the Security tab, and then click Add a user. Add the SYSTEM and then apply.
    17. check enable local.

    Then use the relevant keys here and the DCOM Config utility should give you access greyed onareas:

    CLSID:

    {D63B10C5-BB46-4990-A94F-E40B9D520160}

    and APPID

    {9CA88EE3-ACB7-47C8-AFC4-AB702511C276}

  • HFM 11.1.2.2 HsvDatasource for application ABC with a process ID of 5424 on server HfmServer could not start!

    Hi all

    We improve our 11.1.1.3 to 11.1.2.2 HFM application using hfm copy utility.

    We also have run utility upgrade schema hfm and then save it with shared services.

    but we can see the error in hfm as system messages

    HsvDatasource for application ABC with a process ID of 5424 on server Hhfserver could not start!

    Server: HIBTV-HYP1T with ID 0 has been removed from the list.

    Unspecified error

    It seems that HsvDatasource hfm application does not start even in the Task Manager

    have idea about it

    Kind regards

    Dattatray Mate

    Hello

    That's how oracle has solved this problem.

    We had rules of /HFM of calc scripts in calculation for this HFM application manager.

    If oracle has asked us to remove references by running as a result of the SQL on the schema from table binaryfiles HFM hfm

    delete ABC_binaryfiles where label like '% CalcRules % ';

    After execution of this statement, we could open our HFM application successfully without any problem!

    Kind regards

    -Matt Dattatray

  • VIX file in the user interface designer receives the data from the Web service application that communicates with the SQL server database

    I created the Web service VI ("Mt-insolacije.vi"), which has two terminals of the input string (FROM / TO) for the dates of arrival and exit of two data terminals (table 1 d) from database (MS SQL server). This VI communicates with the database with functions of the database with a DSN and SQL query appropriate palette. There are two tables with two data (time and Insolation) columns in the database.

    This VI works when you run in Labview 2010, but when I used it as VI in UI Builder it returns no data.

    Could you please help me find a solution. Is it possible to communicate with the SQL server database in this way or there is another way?

    There are two files attachmet: Image of .vix file in Interface builder and .vi file ("Mt-insolacije.vi")

    Please help me ASAP!

    Thank you

    Ivan

    I found the solution problem is in the DSN. I've been using the user instead of DSN system DSN.

    It's important to create the system DSN if you want your VI of web service to communicate with the database.

    PS Please put feature bundle format timestamp and XY graph in the web user interface designer. It's complicated to trace data with datetime on X axis without them.

  • EXE, built with the application Builder works on a PC but not on another PC

    Hello.

    I have the following problem:

    An old man. EXE-conversion of a VI (built with LabVIEW 8.2.1) works correctly on a PC with LabVIEW 2013. (This isn't the PC that was originally used to generate the original VI.)

    However, when I move this EXE to another PC (with the last engine LabVIEW to run (LVRTE2013std) installed) it does work correctly. It runs, but it's weird. Because of these specific "Symptoms", I am sure it has something to do with the custom scales used in the original VI. Anyway, I can't be sure of that because the EXE does not have the automatic error handling enabled.

    Finally, build a new EXE of the old VI would be quite difficult at this point for several reasons, so I would really like to get this old EXE to run correctly.

    Thank you in advance!


  • License Manager for applications built in LabVIEW

    What I have is a licensing system to add to applications built in LabVIEW that works more or less like a volume, or as FlexLM license server, where a customer is allowed to so many instances/seats of a program.  Most of what I found looking around my own has been for licenses Add-ons for LabVIEW, which is not what I'm looking for (it's what makes third-party attribution license and activation tool box, for example).  I want it to work like saying the CAD program to work - we have X licenses to run SolidWorks, so when someone starts the program, it fist check with the license server to see if a license is available.  If so, the application opens, and then withdraw the license when the app is left.

    I found Protection PLUS 5 of SoftwareKey SDK.  It looks pretty good.  I like that they have a licensed server product that manages the whole "set up a license server" for me.  I think that some (or a lot) of work, this could be useful.

    The problem I have with the product is that it's a terrible LabVIEW library.  It is not to add to the palette of features anywhere.  Not one of the screws included have a description.  They don't follow things to standard LabVIEW style, like the error code from the lower left and the lower right (actually go in and out of the top middle).  They have an online site that lists what each command and how it works, but it's a pain to work looking back from a webpage to LabVIEW.  The only example they included is a little obtuse.

    So I guess I have two questions.  The first is, has anyone used 5 over Protection, and what did you think of him?  The second is, is there an another add-on which recommend you people?

    Oh, just remembered, but I don't know if it has this feature - http://sine.ni.com/nips/cds/view/p/lang/en/nid/211731

  • OPC Server run only a few Variables - DSC

    Hello

    System: Win7, LabView2010 SP1, DSC

    I have a (Bachmann M1) SPS connected to the PC via an OPC server. I have a draft LabView 100 Variables. These Variables a figure on a HyperTrend a saved in an ASCII file. It works very well, most of the time

    But after a restart of the SPS it gives reading tower, about 25% of the Variables. In the control of the OPC tool, I can see that the OPC server is running and all Variables are very well. I also see in the NOR-DSM. Here, I can see that the value of the Variables is "NAN". After a restart of the process library, it works fine until the next reboot of the SPS.

    I have this combination of Hard - and Software component (SPS - OPC - PC) which works well on 10 other Test applications. Also after a reboot of the SPS. I also run the same software. I only change the address of the OPC Server and must import the reactive power. But the rest is the same.

    If anbody else have the same problem and maybe a solution for this problem?

    THX Martin

    Hi Martin,

    The LabVIEW Datalogging and Supervisory Control (DSC) Module offers servers OPC Client IO can communicate with any server that implements the OPC Foundation OPC server interface, which is a standard based on Microsoft COM.

    You should check the DCOM configuration for a local OPC server before connect you to a server OPC Client IO on the OPC server. National Instruments recommends configuring the server OPC runs with an identity of the interactive user.

Maybe you are looking for

  • Re: How to disable the sleep on Satellite C660 mode?

    How to disable hibernation / standby on a Toshiba C660-1JH? Tried to charge the battery on an ipod via a USB cable, left hip and noticed after a few minutes laptop screen became dark and "standby mode". So of course, my ipod stopped charging.Any idea

  • System preferences network settings

    I can't open my network preferences. I get the following error: Dutch: Het voorkeurenpaneel 'Netwerk' kan niet worden loading English: Failed to load control panel preferences 'network '. Screenshot: http://puu.sh/mtGN1.png Any idea what would cause

  • WindowsUpdate_800B0100

    Have recently installed Windows 7 Home Premium upgrade from Vista.  Windows Update problems with976325, 974571,975364 and 974431.  See also problems such as inability to download files, open the pdf files. A running system update rreadiness tool.  Go

  • Anyone know if it is possible to display a default signature line in the e-mail out to all users logging on to a domain?

    We use Exchange server 2007 and XP on desktop computers

  • Adobe flash player problems in vista

    After a freeze caused by adobe flash player it seems no sign of a recent update to windows vista 32 bit.  The appearance of my homepage lacks many things offshore, for example. no bookmark icon. My page shows even less than what I started with. My sy