Error-200278 occurred at DAQmx Read

Hello

Following an updated example developed by an engineer to support NOR super useful. I did a routine very simple acquisition of a certain level of synchronization between tasks (attached) to use in a PXI system between modules of strain gauges (4330), voltage module (6341) and a frame of independent SCXI1000. The routine seems to work very well up to a certain point, when a very strange problem appears (-200278). It's always the voltage task that generates the error.

Any suggestions?

The task of voltage is set to acquire finished samples.  You want "Continuous samples" I think.

Tags: NI Software

Similar Questions

  • Error-50103 occurred at DAQmx start Task.vi:11

    Hello

    I use a nor-6008 to perform a thermal sector and I get the error "error-50103 occurred at DAQmx Start Task.vi:11 '. I have read other forums of discussion and it seems combe because I use the wizard DAQmx who don't properly resolve the resource when finsihed. I've dug further and saw that it is linked to an on-board clock synchronization problems. However, I can understand how to solve this problem.

    I thought that I create a loop that continuously monitors inputs and sometimes to interrogate the memory so I'm not kidding to the top of the clock. It's much harder to do than sounds. Can someone take a look at my code and give me some advice/suggestions to clean the DAQmx assistants.

    Thanks in advance

    Cole

    I finished by dividing my resource between the two input channels using a single assistant DAQ and dividing down the data rate and the number of samples. Works fine now.

    Big pain in the ass well.

  • Error-50103 occurred at DAQmx control

    We strive to take into two signals in LabVIEW through our acquisition of data, and then pass them through two channels of detection of distinct peaks, however, when we try to run the program, we get the following message is displayed:

    Error-50103 occurred at DAQmx control Task.vi:14

    Possible reasons:

    The specified resource is reserved. The operation could not be performed as indicated.

    Task name: _unnamedTask<9>

    I have attached the circuit we use below, any help woud be appreciated.

    Problem solved, use:

    http://digital.NI.com/public.nsf/allkb/485201B647950BF886257537006CEB89#case4

  • Error 200088 using the DAQmx reading VI in a case structure

    Main problem: I'm writing a VI that will read data from a data acquisition and write to a text file when I hit a button "registration". To do this, I use the VI of reading DAQmx in a while loop, which is located in a case statement (I hit the 'Save' button for the case of true), which is in another while loop. My DAQmx create Virtual channels screws are outside of the loop, so a wire goes through three structures to connect these screws to the VI DAQmx Read.

    After clicking on 'Save', my VI works until I hit the "Stop" button, how I get error 200088: ' specified is not valid or does not exist. " If anyone can help me get rid of this error, that would be greatly appreciated!

    I enclose my VI and an image of the error.

    Secondary problem: currently, I use two different DAQmx read live: one mentioned above, which lays down: after clicking 'Save' and the other who reads data continuously to display on maps. I want to combine these two, but I don't know if this is possible given the case statement.

    Thank you!

    Hi Alexwright,

    I made some quick changes to demonstrate the producer consumer loop that would be effective in your case. You want to loop of producer in the first while loop so that you use and the same closing DAQmx task. Moving a forwardthis will require some trial and effective change for your application. Please also make sure you use our debugging tools: http://www.ni.com/gettingstarted/labviewbasics/debug.htm.

    I hope this helps.

  • error-50103 occurred at DAQmx control Task.vi:6

    I'm new to LabVIEW. I'm using LabView 8.6 and one NEITHER cDAQ-9172. For practice, I'm doing a program that takes the temperature and pressure readings and graphs.

    I don't have the modules or sensors yet, so I started by simulating a RTD temperature measurement NI9217 and a NI9237 module for the measurement of pressure.

    I created 2 while loops that run in parallel. One with an assistant of data acquisition for the temperature and the other with an assistant of data acquisition for the pressure.

    Highlight run out, when I run the program, the signal is both while loops. The temperature seems to work ok and the data graphic. The pressure, however, only goes in once, and I get the error message: "error-50103 occurred at Task.vi:6 DAQmx control Possible reason (s): the specified resource is reserved." The operation could not be performed as indicated. »

    In addition, the stop button does work on my front. I have to use the button stop in the toolbar.

    Anyone has any advice on what I can do to fix this problem or any suggestions on the best ways to address the issue?

    Thank you.

    Search the forums for error 50103.  That will tell you everything you need to know about this error code.

    For more information on your questions, post your VI so we can see what might be wrong.

  • Error-200022 occurred at DAQmx start Task.vi

    Hello

    I have peripheral cDAQ and 3 modules that nor-9234 connected.

    My program (see attachment) works correctly with only 2 modules, but does not work with 3 modules.

    With 3 modules I have this error: "error-200022 occurred at Task.vi DAQmx Start.»   "Possible reasons: resource requested by this task has already been reserved by another task."

    To solve this problem, please help me

    Thank you

    Now I understant the error. This is correct (see below)

  • Error 1074000000 has occurred in a place not identified and error 1073807339 occurred at VISA read

    I worked with it for a few weeks. I am a student doing research for a professor and I'm new to LabVIEW (about a month).

    We calculate impedance in an object with a pulsar. The pulsar will pass through an area of resistance before and after the charge for the calculation of v1 and v2. This will help us to find the current which will help us to find the impedance of the load. In this case, the charge will be a potato. The pulsar will send piulses so we want the program to record the waveform on the trigger.  We have v2 and v1 of two channels. We must record the results of v1 and v2, more than an hour. In addition, if v1, v2, and timestamp are in the same excel file then our lives would be easier. A waveform by file.

    -TL; DR Two channels to be recorded with a timestamp

    The oscilloscope is the WaveRunner LeCroy_64xi.

    We use LabVIEW 2014 SP1.

    I connect to an oscilloscope via an ethernet connection. The connection should not be the problem, but I connected the oscilloscope using NOR-MAX. The oscilloscope is an ACIP device with a remote system, passport and alias. The instructions step by step are http://forums.ni.com/ni/attachments/ni/140/43120/1/VICP-NI-MAX.doc.

    After you connect the oscilloscope, we took a sample program from the driver and changed that to do what we want. We got a few results. FetchWaveform strives to get the shape of wave, but after four or so waveforms, it gives two errors. We tried to add delays, loops and run the program once at a time. I'm willing to start one of these well. This worked well enough at some point, but I think it was because we had a few labVIEW programs open and he was capture the waveform at every second. I think it was because the LABVIEW program has been slowed by the natural delay. It was exactly what we were looking for, but mistakes don't happen often. After the computer restarts and the program, the waveforms are extremely fast registered and errors occur. It is not consistent and we do not know how to register only when the waveform is triggered. Trouble downloading my code here.

    Moving this, we tried ReadWaveform. For some reason, we cannot get readWaveform to work. It does not display the waveform and gives the second error or timeout error. We understand why he will not really connect with the oscilloscope. I do not change one of the examples that use readWaveform for this problem.

    I'll be here tomorrow, but I'm almost done for today. If there is anything I missed, I'm sorry and I'll it download tomorrow. I'm out of ideas. To message me please and thank you very much for your effort.

    Hi Tnorm007,

    I appreciate the level of detail you have included; It seems that there are a lot of things here.  However, it still seems to be inconsistencies and ambiguities in the errors that you receive.  You are able to get a consistent result by running the code you provided?

    For example, if you run the code once, it works as you want?

    If you press run is once again, it works the way you want?  (I assume that you configure the writing on a measure VI file to add the data to the current file?)

    Does it fail after a number of iterations, or it does not depend on the speed at which it runs, back to back?  Which two errors are thrown into this case?

    Also, just a general tip, if you want to receive signals continuously, you want only portions of reading/writing the code of the loop (and initialize/close the task only once), rather than put all the code in a large loop or by pressing the button several times run

    Best,

    David Randolph

    Engineering applications

    National Instruments

    www.NI.com/support

  • Error 1073807253 occurred at VISA read transitional SR830.vi visa: (Hex 0xBFFF006B) a framing error occurred during the transfer.

    Hello

    I wrote a program with labview transitional make measurement of c - v using a stanford amplifier research SR830 detent. The program seems to be runing fine, but sometimes it is givvibg an error:

    #

    You said when you look at the reading string-mode, it sends a \r which is a carriage return (decimal 13, hexadecimal 0d) instead of a \n which is a linefeed (decimal 10, hexadecimal 0a).

    But you did not set your intialize void VI to thread a hex set up 0d in the character of the VISA entry.  You have activated with a real ending, but nothing is wired at the entrance of character which means that it is still using the default value of hex 0A.

    That is why you are still getting the stop in the middle of reading character and timeouts if you ask too many bytes, it takes a lot of time to get X number of bytes, and he's never read the stop character you designate.

    In addition, you must have the VISA close the loop.

  • Error-50103 occurred at DAQmx Start Task

    Hello!

    I use the attached VI to control a stepper motor which works perfectly under LV2010 but begins to throw error (image below) when used under LV2012. If anyone has any idea please help... -Thank you!

    Note I have DAQ assistant is configured correctly.

    Hi KowdTek,

    Thank you for the update.  I assumed you didn't intend the output to be continuous (smooth).

    Screw Express generally are not designed for this type of use because they open and close a session whenever you call one.  This should result in a glitch in the output as you have seen.  To be honest, I'm quite surprised you did not see this before not smooth behavior with your application on Windows XP, and I don't have a good explanation of why it worked.  I can, however, recommend a more robust approach to generate this smooth output you are looking for.

    If the goal is to only move once by INIT (for example once you start moving, do not stop until you are finished, how the VI returns to INIT state), you must convert your VI Express DAQmx code (right-click"NOR-DAQmx generate code).  And try a similar implementation in your case EXEC & LUN.  This should produce the desired behavior.

    Kind regards

  • Error 200485 error has occurred to DAQmx create Task.vi:2

    I continue to have this error:

    The specified task cannot be loaded because it is not in the area of data.

    Check the data area to the MAX. You are looking for similar characters, such as the capital letter 'o' and the number zero.

     


    I would like to know what is the problem with the program.  I have attached the VI.

    Basically I'm controlling a physical light connected to the NI Elvis II by comparing input from 0-7 DIO and DIO 8-15.

    So if DIO 0 is enabled, 8 DIO must also be to turn on the LED.

    But for the moment, the program may not run. Need assistance to locate the error! ><>

    Try the function AND.

  • Error 1316: a network error has occurred trying to read the C:/windows/installer/Setup.msi__trying file for uninstall Manager communication at & t

    uninstallation of at & t communication manager

    https://www.wireless.att.com/support_static_files/KB/KB79807.html

    http://www.wireless.att.com/answer-Center/solutionDisplay.jsp?SolutionID=KB79807

    Read the above.

    See you soon.

    Mick Murphy - Microsoft partner

  • Error-200077 occurred at DAQmx control

    Hello

    I'm having a problem with a sample less than a rate of 1 k with the NI USB-4431.

    Possible reasons:

    Requested value is not supported for this property value. The value of the property may be invalid because it is in conflict with another property.

    Property: SampClk.Rate
    Asked the value: 100.000000
    Valid values begin with: 1.0e3
    Valid values ending with: 102.400000e3

    My vi is attached.

    I tried to change the wait, but it makes no difference.

    I would really appreciate the help on this one please.

    Thanks in advance,

    AT12.

    Hello

    http://www.NI.com/PDF/products/us/cat_usb4431.PDF

    According to the specificaitons in the aforementioned document, the sampling rate is 1kS/s to 102.4kS / s

  • Error 1316: a network error has occurred trying to read from C:\windows\installer\KasperskyPURE.msi

    Tried to uninstall KaperskyPURE2.0 in order to install Kaspersky 2013 and get the above message.   Running Windows 7. Thank you.

    [Moved from comments]

    There are once again this darn echo...

  • Error-200431 occurred at .vi DAQmx Create Channel (I-acceleration-accelerometer)

    Hello

    I tried to use DAQmx Create Channel to accelerometer and yet it responds with error (see below). When I use max OR to measure the accelerometer (I-acceleration-accelerometer), there is no error, and I see that acceloremeter works.

    OR PXI-1042 and I use OR-4462 card to measure vibration vith acceloremeter.

    Error-200431 occurred at DAQmx Virtual Channel Create

    Possible reasons:

    Physical channel selected does not support the type of measure required by the virtual channel you create.

    Create a channel to a type of measure that is supported by the physical channel, or select a physical channel that supports the type of measure.

    Property: I. MeasType
    Requested value:
    You can select: sound pressure, voltage: Microphone, accelerometer, Position: Eddy Current proximity probe, Force sensor: IEPE, speed sensor: IEPE

    Task name: _unnamedTask<104>

    Hi serdaryilmaz,

    I'm not sure why the accelerometer mode does not work, but it works very well in normal mode - it maybe has to do with the accelerometer, you?  Whatever it is, if it works with the voltage mode, I am happy that we found a way to make it work.  Is this an acceptable work around you?

  • multimedia card reader an error has occurred please drive reconnect to try again

    I have windows xp 32 bits SP3. I tried to copy the computer on a CD - RW disc images and a message kept popping up on the office.

    Multimedia card reader. An error has occurred please reconnect reader to try again. I got my coppied photos on the disk, but did not know what that message was talking about. It kept popping up.

    Hi Connie,

    1 is this problem limited only when you copy images from the computer to CD?

    2. What is the full/exact error message?

    3. have you connected any external to the computer card reader recently?

    4. What is the brand and model of the computer?

    It seems that the installation of the driver of the multimedia card reader is not over. If you have connected to any card reader recently, you can re - connect to the computer and allow the computer to detect the device.

    Hope this information helps. Provide more information so that we can help you.

Maybe you are looking for

  • How can I change European keyboard to English characters?

    I recently got an Apple iMac and the keyboard is European.  It's not hit a number of characters as they are shown on the keyboard which is irritating. I examined the means to change... through the language on the system of preferences Safari... but n

  • How can I re-size ferefox to fit my monitor?

    I had a kitten on my lap and it must have pushed some of the main causes now the screen is larger than my screen. I don't see the top or the bottom. I don't have my bookmark icon...

  • Broken HP printer driver

    iMac running OS 10.9.5 Finally I update software install HP printer software update 3.1.  Big mistake.  HP printer prints correctly.  No help from HP. How can I find/go back to the old version of the HP print driver?

  • A720 Wifi connection

    Hello How do I activate the A720 Lenovo WiFi connection with 5 GHz.? Kind regards

  • need to updrade my hard drive model DV9925nr

    HP Pavilion DV 9700 laptop model # DV 9925nr Windows Vista Edition Home Premium No more disck space, need to upgrade my current HARD drive HARD drive install is 250GB I need to know what the HARD drive can move to