Precision in the reading of temperature PT100 and Module of NI9219

Hello

I m the temperature reading with a PT100, connected to the NI9219 Module. I put LabVIEW on mode 4 son RTD (PT100 range). I m able to read the weather temperature but I m do not know the right precision s or not. The temperature is between 25.5 and 25.8 ° C. Is this possible? I am able to do something to have more precision?

Thank you in advance,

Claudia

Hi Claudia,.

The specifications for the 9217 provide the absolute measurement accuracy Pt 100 RTD (3 and 4 sons) on page 14, it is not necessary to calculate [1].

Since the 9219 is more flexible in the types of measures that it can bring, absolute accuracy for each use case is not provided. Instead, OR gives error of gain values and offset to be used for the calculation of the absolute accuracy [2].

Follow this logic to calculate the absolute accuracy:

(Absolute accuracy) = (entry reading) * (Gain error + drift in temperature) + (Offset + drift in temperature error)

Reading the line "RTD 4-wire or 3 wire Pt 100" in the table on page 24, the error of gain and offset for a module between 20 and 30 degrees Celsius is ±0, 1% of reading entry for gain and offset sectors ±2400ppm. Drift in temperature comes into play when the module is outside the normal operating temperature, but for Pt 100, gain drift is ±15ppm and the offset of the drift is the ±60ppm (see page 25).

So, for a module at room temperature 23 degrees Celsius and a Pt100 to 100 degrees Celsius using the 505 Ohm input range, the calculation is:

At 100 ° C, the RTD would measure 138.5 Ohms if its temperature coefficient 0,00385 Ohm/Ohm / ° C, then

Absolute accuracy = (138.5 ohms * 0,1%) + (2400 ppm * 505 Ohm)
= 1.212 Ohm + 0,1385 ohm
= 1.3505 ohms

fracture of 0,385 Ohm / ° C, and

Absolute accuracy = ±3, 5 degrees Celsius

[1] NI 9217 Operating Instructions and Specifications
http://www.NI.com/PDF/manuals/374187c.PDF

[2] NI 9219 specifications
http://www.NI.com/PDF/manuals/374473b.PDF

I hope that I can help you with this information.

Best regards

SUSE

Tags: NI Software

Similar Questions

  • Measuring temperature pt100 9219 module

    Hello

    I have a temperature PT100 probe three sons on the "input analog of the NOR 9219." I created a task with a maximum I the right temperature on the chart drop-down test. Room I displays the value of this task in Labview through Daqmx lire, and there big problem: I have a disproportionate value. I have probably a problem of scale or other, but I do not see how to solve it. Help thanks again for your, Frank

    Hello Zekaza,

    Thank you for your response. My problem is solved. See you soon. Frank

  • What is the difference between General LV and LV RT considering that I want to read the output of a sensor of temperature online?

    Hello world

    I am very new in LV and I need to read my temperature sensore outputs online so that necessary system changes each time the temperature changes. If I use genral LV or LV RT?

    Thank you

    Hi elahetal.  The LV vs LV RT decision really depends on what are your needs of the moment.

    RT is not necessarily to be as fast as possible, but rather as consistent as possible.

    If you have a measure which must be taken every 100mS + / 2 ms to practically use RT a generalist OS like Windows will be randomly off the coast and do other things (read a cd, the printer, the disc index, etc.), causing your position to be late.

    A RT environment will allow you to determine precisely at the time where the system should do what.  The compromise is that the RT environment is somewhat limited, because you do not have all the bells and whistles, practitioner OS.

    If your action must be taken every 15 years + / 10 s then you can very well get away with standard LV on a PC.

    In some cases, a combination works well.  For example, RT on FieldPoint or CRIO to manage the time of sensitive issues and LV on a PC to manage the analysis of data and user interface.

    Hope that helps, please specify your needs if you wish.

    Matt

  • Why my message a confirmation of reading on a device and not the other?

    I use my iMessage on my iPhone 5 and my Macbook Air, however, sometimes when I send a message from a device it shows a read receipt to the other person on my mac, but not on my iPhone. The message on my iPhone remains as "delivered" much later and then seems to be read (I'm done yet receive confirmations of reading on my phone), but my mac delivers the message, and it seems that the message has been read afterwards, but it shows the path of the read receipt before my iPhone don't. I don't know if it's just one little problem and they have not actually read the message, or if my mac book is somehow showing the first read receipts?

    Hello

    It has to do with which ID is used to send the iMessages and what devices are then synced to see this info.

    Device sending roughly see the pronouncement to feedback.

    If it's the Mac using the Apple ID it will 'see' the 'read' first response.

    However, if the Mac uses the iPhone number to send, then some info can run on the iPhone first it's the device the number belongs to.

    The Mac is only then light "Copies" of the synchronization version.

    Add to that the fact that some people will have a device set to join read receipts and not another.

    It is basically not a precise answer that there are many factors that can influence it.

    20:45 Thursday. 26 May 2016

     iMac 2.5 Ghz i5 2011 (El Capitan)
     G4/1GhzDual MDD (Leopard 10.5.8)
     MacBookPro (Snow Leopard 10.6.8) 2 GB
     Mac OS X (10.6.8).
     iPhone and iPad (2)

  • Satellite M70: access to the data of temperature and fan

    While we did not have these problems with other laptops, we found a way to access the data of temperature and fan on a Satellite M70.

    A friend has tried this on Linux but have failed and also with XP I do not find a way to read data (current temperature of the CPU, or State of the fan-cooler).

    Given that I noticed several irregularities when using (the fan is that the CPU load is very minimal), work sometimes is going to be a little uncomfortable.

    Thanks for the advice / gw

    I put t know if it will help you, but in this ad, someone managed to run a control application of the material.
    http://forums.computers.Toshiba-Europe.com/forums/thread.jspa?threadID=14284

    Maybe it will work on your laptop.
    But to my knowledge Toshiba doesn't support this request and I'm not sure it will work.
    Anyway, try it's free ;)

  • Change the precision of the waveform data or daqmx read

    Hi all

    I am currently using daqmx read and write data to a PDM daughter.  I would change the precision of the data if possible.

    Any advice?

    Thank you

    Matt

    It is important to get the right information in the data file. It is not a lot of overhead to limit your data with a specific precision if you as a table.

    I don't know which is faster, the method of accuracy of the channels or this:

    It took 1-2 ms per 1 million iterations.

  • Reading the words of temperature controller fits using Modbus

    I'm working on a project that involves the use of a certain number of temperature controllers, Omega CN 7823 s.  The Protocol of communication for them is RS485 Modbus ASCII or RTU.

    I had a bit of trouble getting a job of communicating.  I think I do everything correctly in terms of setting up the initial communication parameters (baud rate, parity, etc.), but have been unable to properly read the values.  I am able to write values to operating records, but cannot read them.  When I try to read (using the code 03), the result is simply a multiple of 256 (if I try to read registry 1001 H, which is 4097 in decimal form, I get a result of 256).

    I'm running in ASCII at a speed of 9600, 7-bit data length, parity and 1 stop bit.

    Any help would be appreciated - I am attaching my VI and the manual of the controller.

    In the end it turned out that I had to create a property node to the VISA Instrument and specify the mode series RS-485/2-Auto.  This allowed the computer read the response from the controllers of temperature instead of simply reading the message that was sent to them.  I wish I had discovered this day 1, 2 or 3 to work on this problem, instead of the day 5.

  • Temperature measurement and the CJC using thermocouples on a USB - 6229 BNC

    Hello

    I'm trying to get the measurements of temperature using type K thermocouples on the box nor usb-6229 BNC. SignalExpress software doesn't let me choose 'Built In' to the Source of the CJC. So, I must select 'Constant', which means that I then have to follow the evolution of the temperature during the day with a separate meter and adjust the value of CJC accordingly to maintain an accurate reading. Is there a way around that to avoid having to monitor the room temperature at the junction?

    Thanks in advance

    Mike

    Hi Mike,.

    It seems that you have managed to find a solution for you have this problem, which is great news.

    However, for future use, if you had bought the 6229 with massive ending (rather than the interface BNC) then you might have interfaced unit with a block of connection SCB-68 (see link)

    http://sine.NI.com/NIPs/CDs/view/p/lang/en/NID/1180

    The SCB-68 has a CYC source built-in, so you might have used in conjunction with 6229 (mass layoffs).

    A bit of in the way, but I thought you may be interested.

    Best wishes to you all

  • I am trying to record an mp3 file, but firefox does not allow me to save... it allows me to read the file but not download and asave to my computer. How can I enable to save the mp3 files on my computer?

    I am trying to record an mp3 file, but firefox does not allow me to save... it allows me to read the file but not download and asave to my computer. How can I activate the Firefox save MP3s on my computer?

    Go to Options > Applications tab > MPEG Layer 3 audio(audio/mpeg) image search > use the "Save file" option on the menu drop down.

  • Plugin check says that the plugin Acrobat Reader (10.0.1.434) is an outdated version. However, I downloaded the latest version of Acrobat and installed. Is there a problem on my PC environment or with the control plugin?

    1 did the plugin check June 10 - got the message that the plugin Acrobat Reader for Firefox and Netscape was an outdated version. You press the update on the page has been redirected to the Adobe site.
    2. download the latest version, AdbeRdr1001_en_US.exe, and then ran the executable locally on the PC. The updated normally. Note: I didn't uninstall the old Acrobat reader before running the executable file.
    3. I went to the plugin check page and I always get the obsolete message for this plugin. Restarting the system (i.e. overnight) and repeated the check, with the same results.
    4 did you open Acrobat Reader app, you tap Help and then search for updates - no new updates have been found. Have, run test Mozilla (Mozilla Privacy Policy PDF) without any problem.
    5. what version of the plugin that should be saved in the Add-ons Manager on my PC?
    6. Please advise on the appropriate action.

    For those who have had this problem. Adobe has released a fix yesterday and you need to update your Adobe Reader immediately. The latest version is 10.1.0. Once you updated your Firefox Adobe Acrobat plug-ins will be automatically updated to 10.1.0.534.

    If you receive a notification of update from Adobe, you can open Adobe and go to: help > check for updates

  • MacBook Pro running Mac OS 10.6. The font size for tabs and bookmarks toolbar is too small for comfortable reading for older eyes. Is there a way to change or expand?

    The font size is smaller and harder to read than on FF 3.x. Want to make some larger or to choose a different, more readable font altogether.

    Extension of theme font & size changer.

    https://addons.Mozilla.org/en-us/Firefox/addon/theme-font-size-changer/

  • I need to know how to remove the most recent version of Firefox. I JUST downloaded tonight and my computer does not have this edit bar little to work with, so I can download the reader good Adobe and my internet was screwed up ever since I downlo

    I need to know how to remove the most recent version of Firefox. I JUST downloaded tonight and my computer does not have this edit bar little to work with, so I can download the reader good Adobe and my internet was screwed up, since I downloaded the new version of Firefox. I want just the old version of this back because I can't download the Adobe stuff which is necessary to protect my computer against hackers apparently not. It would have been nice to know he had a problem with the new update of Firefox BEFORE I downloaded it. I have Vista, which is usually a problem with Adobe and Firefox. I don't seem to be able to run a lot of Adobe at all on my computer because of the Vista.

    This has happened

    Each time Firefox opened

    http://support.Mozilla.com/en-us/KB/installing+a+previous+version+of+Firefox

  • Cannot read iphoto library stored in an external drive, after the installation of el capitan and photos

    I can't read iphoto library stored in an external drive, after the installation of el capitan and photos, can anyone help?

    What size is the drive? How are you connected to it?

  • The 'writing INI Cluster_ogtk.vi' and 'reading INI Cluster_ogtk.vi'.

    I recently accquired a co-worker LabView application. I tried to run but miss me a few subsidiary screws, i.e. the 'write INI Cluster_ogtk.vi' and the 'Read INI Cluster_ogtk.vi. Can someone help me with how to accquire them?

    Thank you.

    Hi tdog.

    These screws are OpenG. OpenG is a community open source LabVIEW. They create tools that are very nice to improve the toolset of LV.

    Check it out at: http://wiki.openg.org/Main_Page

    It is a very good package install called VIPM which can be used to download all the OpenG files and integrate them into your LabVIEW installation. The version of the community is free.

    http://www.jkisoft.com/VIPM/

    The only drawback to the use of code from LabVIEW outside, is that you can run into situations that you have found yourself in. However since the tools are free, this is really not a big problem (except when you know about it).

    That said, I found the benefits outweigh certainly outweigh the negatives.

    Here are the links to access the descriptions of two live questions on:

    http://wiki.Openg.org/Write_INI_Cluster

    http://wiki.Openg.org/Read_INI_Cluster

    Steve

  • In Labview 8.6 and MAX, I can change a scale for a voltage read the string in a task once the application has been built and installed.

    In Labview 8.6 and MAX, I can change a scale for a voltage read the string in a task once the application has been built and installed on a second PC. Where's the info of the scale which is held?

    Hello

    Once you have built your VI and compiled into an executable file and deployed on another machine, it essentially becomes a file read-only, which means that you will not be able to change the balance in this deployed application.

    Kind regards

    Marcus

Maybe you are looking for

  • Connection PC Win7 for iMac USB printer

    Until yesterday, I had a printer is connected (USB connection) to a Time Capsule, and our laptop Windows 7 given the printer and would print it. But due to persistent problems with airport part not always wanted to connect with our satellite internet

  • Photoshop CS5 & El Capitan

    Hello I often use PS CS5, usually when using pictures in FCPX. Still, I Yosemite and have heard that el Capitan is problematic with CS5. What did you hear/experience? Are there updates to El Capitan, which may have solved these problems? The best Elm

  • Helps with 7852R input analog voltage measurement

    Hello I'm trying to measure three signals of tension off a QPD, the three signals are connected to the IA the SCB - 68 and then I used the example of vi to acquire analog inputs with FPGA R in the finder of the example. However, I make a range of ver

  • Naming of the individual parcels

    Hello I'm looking for a way to individual parcels of name using the graph IN. So far, I have been using the node property and only able to rename the name of ' main '. Is there a way I can feed an array of names for the locations? For example, index

  • Cannot connect to DRAC4 on PE2800

    I recently acquired a PE2800 and bought and installed a DRAC4 inside. I can configure the DRAC of CTRL-D and can change the admin user and the password of CTRL-E, but I'm unable to log the DRAC via the web interface. I get the prompt after dealing wi