PSU_REDUNDANCY - redundancy lost

Hi all

I encounter this problem on my UCS-210:

on the State of the power supply in my VMWare, it displays:

PSU_REDUNDANCY power supply 0 - lost redundancy ==> this give warning message

Power supply 2 PSU2_STATUS: Power Supply AClost - Deassert ==> this message give Normal

Power supply 1 PSU1_STATUS: Power Supply AClost - Deassert ==> this message give Normal

Can someone explain this message "PSU_REDUNDANCY - lost redundancy.

Everyone already knows about this problem?

What can I do?

Kind regards

Antra

Hello

You need to check on the LEDs of the PSU and collect certain personal information from the CLI:

chassis of scope

display power supply

View details of power supply

Please take a look at this information from Cisco.com

http://www.Cisco.com/en/us/TS/fn/634/fn63425.html

David

Tags: Cisco DataCenter

Similar Questions

  • Important: Redundancy lost for BE6K UCS C220 M3S PSU_REDUNDANCY

    Hello team,

    We have several deployments based on servers UCS C220 M3 (the famous BE6K) UA.

    I'm not derived from systems, I'm a guy of the voice.

    In fact, the UCS BE6K C220 M3 comes by default with a single power supply.

    However, in the MMIC, we find many times that an alert is triggered for the redundancy of power and the system LED turns into continuous light.

    Here's the warning: PSU_REDUNDANCY: PS redundancy sensor, redundancy Lost said

    We do not understand why this alert is triggered when we already know that the BE6K server contains only a power supply?

    What is a real problem or a false alarm?

    How we clear this alert?

    In fact the system LED is orange isn't bodes well from the perspective of the customer. As well as when let us it stay in the State of the orange light, we would be not only a more serious problem (and real) can happen?

    The MMIC version is: 1.5.4f

    Please notify.

    Unfortunately not (that I know) but if you go to loopholes in the Server tab, you should be able to view a summary of alerts and check what is happening.

    If it is useful, please rate... If it answers your question, please mark as well for future users.

    -Kenny

  • Create alarm "Network redundancy lost" by the script?

    Hello:

    I'm trying to write a script that will create the alarm in order to monitor the redundancy of the lost network (I know manually there) on the host.

    I know how to create alarm for additional exhibit the ' basic' event (LucD - thank you for your help) and I know that I have for alarm 'Lost network redundancy' to use 'vprob.net.redundancy.lost' instead of 'EnteringMaintenanceModeEvent' (as in my example); but I still struggle to combine...

    Can someone help me please?

    Thank you

    qwert

    I don't have a particular script fantasy with the settings and all the rest, but I can show you the steps to filter alarms by name and remove the desired one.

    alarm #retrieve Manager

    $alarmManager = get-view-Id "AlarmManager-AlarmManager.

    #Get the entity that contains the alarm that you want to remove. I'll do it for a virtual machine

    $entityView = get-Vm-name MyVm | Get-View

    #get all MoRefs alarm

    $alarmMoRefList = $alarmManager.GetAlarm($entityView.MoRef)

    #Retrieve tha alarm views from the MoRefs

    $alarmViewList = $alarmMoRefList | foreach (Get-view $_)

    #Now filter the name alrams

    $alarmToDelete = $alarmViewList | where {$_.Info.Name - eq "AlarmToDelete"}

    #Finally remove alarms

    $alarmToDelete.RemoveAlarm)

    It shouldn't be hard to put this in a script or function reussable. If you have problems with this, I'll be happy to help you again!

  • alert the uplink network redundancy lost

    VCenter has an uplink lost redundancy alert network, which takes about 5 days. The alert cannot be recognized or green value, because the option is grayed out. VCenter client does not show the cards down. A few questions

    -How can the alert being erased?

    -Where should I look for the question? I checked the network adapters on the host's configuration in vcenter client. Where would be ESXI connect alerts for this problem?

    It's vCenter.  Alarms are sometimes "buggy".

  • Uplink Network \Network connectivity redundancy lost lost

    Hello

    I have hp servers and they down due to electrical problem, and after that they up, I got these

    (redundancy uplink of lost network connectivity lost \Network)

    and I have on each server 1 standerd switch 8 vmnic 4 wrkking and 4 pending and I checked all, but I have not found any problem on any

    so please can anyone advice what is the problem

    Thnx for your support

    Hello

    Try alarm reset to green...

    Thank you

    SA

  • Alert - lost redundancy Uplink Network trap

    Is there a way to find this alert via PowerCLI?  I often get this alert and need to put in place an alert by e-mail when this happens, but I do not Get-VIEvent but it is in the console under alarms.

    To obtain the host name, you can do it like this:

    Get-VIEvent -Start (Get-Date).AddDays(-7) -MaxSamples 99999 | `
    Where-Object {$_.GetType().Name -eq "EventEx" -and $_.EventTypeID -eq "vprob.net.redundancy.lost"} | `
    Select-Object -Property EventTypeId,Severity,CreatedTime,@{N="VMHost";E={$_.Host.Name}}
    

    Best regards, Robert

  • Warnings of redundancy of the path in VMware

    Hello

    We noticed recurring warning events in VMware similar to this:

    Redundancy lost path to the storage device
    NAA.6090a0b8d08e35c1bd16d5ded001507f. road
    vmhba41:C1:T24:l0 is down. Affected data warehouses
    : eql_vmfs-vdi-thinapp.
    warning
    10.07.2013 12:18:48
    eql_vmfs-vdi-thinapp

    Followed by:

    Redundant path to the storage device
    NAA.6090a0b8d08e35c1bd16d5ded001507f
    (Data warehouses: eql_vmfs-vdi-thinapp) restored. Path
    vmhba41:C1:T24:l0 is active again.
    Info
    10.07.2013 12:19
    eql_vmfs-vdi-thinapp

    And also:

    Alarm "Unable to connect to storage" on esx04.hials.
    No. changed from gray to gray
    Info
    10.07.2013 12:22:51
    esx04.hials.no

    Firmware EQL: 6.0.2

    ESXi version: 5.1.0 - 799733

    Software iscsi adapter

    We installed the MEM disabled delayedack, LRO and also increased login_timeout to 60 s.

    Any tips?

    Welcome to the club,

    We have seen it work on every vSphere + solution EQL, we have deployed over the years. Most of the customers don't see it because the have not configured notification of special alarm on vCenter.

    The 'problem' produced once per week or month. Most of the time not all data warehouses are performed and also not all hosts. The reconnection is made in the same second, and we don't see never liked problem here. The bad news, it's that you get emails with false-positive alarm.

    Kind regards

    Joerg

  • network connection lost alarm

    Hello

    alarm sails host shows "Lost network connectivity" and "Network of uplink redundancy lost" errors in vCenter red Rectangle symbol and came on the host, but all VM and servises performs very well what was the reason for this alarm and what is the solution for this.

    In this case it could have been a temporary problem with the network, which is already solved. To get rid of the alarm message, you will need recognize/reset the alarm.

    André

  • By disco preventivo da 750 GB SAS [MB]

    Buongiorno

    MD 3000 Powervault fuori co - DellTag 167HH4J
    HA a disco at fault: I di seguito dettaglia

    Physical path of disk redundancy: lost
    Physical disc type: Serial Attached SCSI (SAS)

    Speed: 7,200 RPM
    Current rate: 3 Gbps
    Product ID: ST3750630SS
    Firmware version: MS04
    Serial number: 9QK2GVAH
    Seller: SEAGATE
    Manufacturing date: 5 September 2009

    It client ha di certainly need

    E' possibile avere un preventivo by disco it?

    Grazie
    Matteo b.

    Buongiorno,

    Disco questioned da 750 GB non pulito essere stato labor-intensive it con server there.

    Avete labor-intensive it disco con UN ordine successivo?

    Grazie

    Marco

  • connection iSCSI delivers or not?

    Hello,
    
    I'm encountering some issues with iscsi connections in my vSphere environment and my Equallogic group and wondering if I could get some input from you all. I'm curious to know if what I'm seeing is an Equallogic MEM or NLB event or if I actually have some type of issue. Here's a bit about my environment:
    
    3-ESXi Hosts - 5.0 U1 (623860)Each host has four 1Gbps cards dedicated to the iSCSI network (2 Intel and 2 Broadcom).Storage Heartbeat VMK configured and is the lowest vmk on vSwitch.Delayed ack is disabled.Dell MEM 1.1.2 installed
    
    2-HP 2910al-24g switches4 ports are dedicated to a LACP trunk group for the interswitch connectionjumbo frames enabledflow control enablediSCSI VLAN is not VLAN 1Switch logs look good with very few drops or errors.
    
    One Equallogic group with two PS4100's (One PS4100X and One PS4100XV).Both arrays on FW 5.2.2Dedicated management network.Latency looks good across the group.TCP Retransmits very low <0.1%
    
    Should I expect to see the re-balance event noted in the vmkernel.log file? From other logs I've seen online, it appears as if they all show an entry that states a re-balance request has been received from the array, but I'm not seeing that in my logs. I've provided the relevant entries from both the Equallogic group and vSphere host below. Thanks.
    
    Jake
    
    The informational events that have me somewhat concerned are logged on the group as:
    
    Severity Date and Time Member Message -------- ------------------- --------------- ------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------  INFO 5/16/13 12:08:41 PM PS4100X-0 iSCSI session to target '192.168.90.103:3260, iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f' from initiator '192.168.90.53:56744, iqn.1998-01.com.vmware:VHOST05-484f029e' was closed. Logout request was received from the initiator.  INFO 5/16/13 12:08:40 PM PS4100X-0 iSCSI login to target '192.168.90.102:3260, iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f' from initiator '192.168.90.53:60923, iqn.1998-01.com.vmware:VHOST05-484f029e' successful, using Jumbo Frame length.  INFO 5/16/13 12:08:40 PM PS4100X-0 iSCSI login to target '192.168.90.101:3260, iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f' from initiator '192.168.90.51:55351, iqn.1998-01.com.vmware:VHOST05-484f029e' successful, using Jumbo Frame length.  INFO 5/16/13 12:08:40 PM PS4100X-0 iSCSI login to target '192.168.90.104:3260, iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f' from initiator '192.168.90.50:56018, iqn.1998-01.com.vmware:VHOST05-484f029e' successful, using Jumbo Frame length.  INFO 5/16/13 12:08:40 PM PS4100X-0 iSCSI login to target '192.168.90.104:3260, iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f' from initiator '192.168.90.52:62320, iqn.1998-01.com.vmware:VHOST05-484f029e' successful, using Jumbo Frame length.  INFO 5/16/13 12:08:38 PM PS4100X-0 iSCSI session to target '192.168.90.102:3260, iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f' from initiator '192.168.90.50:53740, iqn.1998-01.com.vmware:VHOST05-484f029e' was closed. Logout request was received from the initiator.  INFO 5/16/13 12:08:38 PM PS4100X-0 iSCSI session to target '192.168.90.101:3260, iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f' from initiator '192.168.90.52:62640, iqn.1998-01.com.vmware:VHOST05-484f029e' was closed. Logout request was received from the initiator.  INFO 5/16/13 12:08:38 PM PS4100X-0 iSCSI session to target '192.168.90.103:3260, iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f' from initiator '192.168.90.51:53550, iqn.1998-01.com.vmware:VHOST05-484f029e' was closed. Logout request was received from the initiator.  INFO 5/16/13 12:08:27 PM PS4100X-0 iSCSI session to target '192.168.90.104:3260, iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f' from initiator '192.168.90.50:51627, iqn.1998-01.com.vmware:VHOST05-484f029e' was closed. Logout request was received from the initiator.  INFO 5/16/13 12:08:26 PM PS4100X-0 iSCSI login to target '192.168.90.102:3260, iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f' from initiator '192.168.90.50:53740, iqn.1998-01.com.vmware:VHOST05-484f029e' successful, using Jumbo Frame length.  INFO 5/16/13 12:08:26 PM PS4100X-0 iSCSI login to target '192.168.90.101:3260, iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f' from initiator '192.168.90.52:62640, iqn.1998-01.com.vmware:VHOST05-484f029e' successful, using Jumbo Frame length.  INFO 5/16/13 12:08:26 PM PS4100X-0 iSCSI login to target '192.168.90.103:3260, iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f' from initiator '192.168.90.51:53550, iqn.1998-01.com.vmware:VHOST05-484f029e' successful, using Jumbo Frame length.  INFO 5/16/13 12:08:26 PM PS4100X-0 iSCSI login to target '192.168.90.103:3260, iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f' from initiator '192.168.90.53:56744, iqn.1998-01.com.vmware:VHOST05-484f029e' successful, using Jumbo Frame length.  INFO 5/16/13 12:08:24 PM PS4100X-0 iSCSI session to target '192.168.90.101:3260, iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f' from initiator '192.168.90.53:53109, iqn.1998-01.com.vmware:VHOST05-484f029e' was closed. Logout request was received from the initiator.  INFO 5/16/13 12:08:24 PM PS4100X-0 iSCSI session to target '192.168.90.102:3260, iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f' from initiator '192.168.90.51:53339, iqn.1998-01.com.vmware:VHOST05-484f029e' was closed. Logout request was received from the initiator.  INFO 5/16/13 12:08:24 PM PS4100X-0 iSCSI session to target '192.168.90.104:3260, iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f' from initiator '192.168.90.52:53108, iqn.1998-01.com.vmware:VHOST05-484f029e' was closed. Logout request was received from the initiator. 
    
    The host logs these events in vmkernel.log:
    
    2013-05-16T16:08:24.658Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: vmhba37:CH:1 T:6 CN:0: Failed to receive data: Connection closed by peer2013-05-16T16:08:24.658Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: Sess [ISID: 00023d000006 TARGET: iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f TPGT: 1 TSIH: 0]2013-05-16T16:08:24.658Z cpu3:2997)NMP: nmp_ThrottleLogForDevice:2318: Cmd 0x28 (0x41244101e280, 4863) to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" on path "vmhba37:C1:T6:L0" Failed: H:0x2 D:0x0 P:0x0 Possible sense data: 0x0 0x0 0x0. Act:EVAL2013-05-16T16:08:24.658Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: Conn [CID: 0 L: 192.168.90.51:53339 R: 192.168.90.102:3260]2013-05-16T16:08:24.658Z cpu3:2997)WARNING: NMP: nmp_DeviceRequestFastDeviceProbe:237:NMP device "naa.64ed2a85165dc1561cf7c4851a02c0d6" state in doubt; requested fast path state update...2013-05-16T16:08:24.658Z cpu1:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: vmhba37:CH:1 T:6 CN:0: Connection rx notifying failure: Failed to Receive. State=Online2013-05-16T16:08:24.658Z cpu3:2997)ScsiDeviceIO: 2309: Cmd(0x41244101e280) 0x28, CmdSN 0x800000d3 from world 4863 to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" failed H:0x2 D:0x0 P:0x0 Possible sense data: 0x0 0x0 0x0.2013-05-16T16:08:24.658Z cpu1:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: Sess [ISID: 00023d000006 TARGET: iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f TPGT: 1 TSIH: 0]2013-05-16T16:08:24.658Z cpu1:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: Conn [CID: 0 L: 192.168.90.51:53339 R: 192.168.90.102:3260]2013-05-16T16:08:24.658Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: vmhba37:CH:1 T:6 CN:0: iSCSI connection is being marked "OFFLINE" (Event:6)2013-05-16T16:08:24.658Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: Sess [ISID: 00023d000006 TARGET: iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f TPGT: 1 TSIH: 0]2013-05-16T16:08:24.658Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: Conn [CID: 0 L: 192.168.90.51:53339 R: 192.168.90.102:3260]2013-05-16T16:08:24.658Z cpu5:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: vmhba37:CH:2 T:6 CN:0: Failed to receive data: Connection closed by peer2013-05-16T16:08:24.658Z cpu5:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: Sess [ISID: 00023d000007 TARGET: iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f TPGT: 1 TSIH: 0]2013-05-16T16:08:24.658Z cpu5:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: Conn [CID: 0 L: 192.168.90.52:53108 R: 192.168.90.104:3260]2013-05-16T16:08:24.658Z cpu5:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: vmhba37:CH:2 T:6 CN:0: Connection rx notifying failure: Failed to Receive. State=Online2013-05-16T16:08:24.659Z cpu5:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: Sess [ISID: 00023d000007 TARGET: iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f TPGT: 1 TSIH: 0]2013-05-16T16:08:24.659Z cpu5:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: Conn [CID: 0 L: 192.168.90.52:53108 R: 192.168.90.104:3260]2013-05-16T16:08:24.659Z cpu5:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: vmhba37:CH:2 T:6 CN:0: iSCSI connection is being marked "OFFLINE" (Event:6)2013-05-16T16:08:24.659Z cpu5:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: Sess [ISID: 00023d000007 TARGET: iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f TPGT: 1 TSIH: 0]2013-05-16T16:08:24.659Z cpu5:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: Conn [CID: 0 L: 192.168.90.52:53108 R: 192.168.90.104:3260]2013-05-16T16:08:24.659Z cpu3:2997)NMP: nmp_ThrottleLogForDevice:2318: Cmd 0x28 (0x412441cb8500, 4863) to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" on path "vmhba37:C2:T6:L0" Failed: H:0x2 D:0x0 P:0x0 Possible sense data: 0x5 0x24 0x0. Act:EVAL2013-05-16T16:08:24.659Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: vmhba37:CH:3 T:6 CN:0: Failed to receive data: Connection closed by peer2013-05-16T16:08:24.659Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: Sess [ISID: 00023d000008 TARGET: iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f TPGT: 1 TSIH: 0]2013-05-16T16:08:24.659Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: Conn [CID: 0 L: 192.168.90.53:53109 R: 192.168.90.101:3260]2013-05-16T16:08:24.659Z cpu0:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: vmhba37:CH:3 T:6 CN:0: Connection rx notifying failure: Failed to Receive. State=Online2013-05-16T16:08:24.659Z cpu0:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: Sess [ISID: 00023d000008 TARGET: iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f TPGT: 1 TSIH: 0]2013-05-16T16:08:24.659Z cpu0:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: Conn [CID: 0 L: 192.168.90.53:53109 R: 192.168.90.101:3260]2013-05-16T16:08:24.659Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: vmhba37:CH:3 T:6 CN:0: iSCSI connection is being marked "OFFLINE" (Event:6)2013-05-16T16:08:24.659Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: Sess [ISID: 00023d000008 TARGET: iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f TPGT: 1 TSIH: 0]2013-05-16T16:08:24.659Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: Conn [CID: 0 L: 192.168.90.53:53109 R: 192.168.90.101:3260]2013-05-16T16:08:24.771Z cpu15:5735)NMP: nmp_ThrottleLogForDevice:2318: Cmd 0x28 (0x412441018980, 4863) to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" on path "vmhba37:C1:T6:L0" Failed: H:0x2 D:0x0 P:0x0 Possible sense data: 0x0 0x0 0x0. Act:EVAL2013-05-16T16:08:24.860Z cpu4:4828)NMP: nmp_ThrottleLogForDevice:2318: Cmd 0x2a (0x4124010a25c0, 2064) to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" on path "vmhba37:C3:T6:L0" Failed: H:0x2 D:0x0 P:0x0 Possible sense data: 0x0 0x0 0x0. Act:EVAL2013-05-16T16:08:24.908Z cpu10:2777)ScsiDeviceIO: 2309: Cmd(0x412440982980) 0x2a, CmdSN 0x80000059 from world 4863 to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" failed H:0x2 D:0x0 P:0x0 Possible sense data: 0x0 0x0 0x0.2013-05-16T16:08:24.912Z cpu15:2063)NMP: nmp_ThrottleLogForDevice:2318: Cmd 0x28 (0x412441018980, 4863) to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" on path "vmhba37:C3:T6:L0" Failed: H:0x2 D:0x0 P:0x0 Possible sense data: 0x0 0x0 0x0. Act:EVAL2013-05-16T16:08:24.921Z cpu10:10448)WARNING: NMP: nmp_SelectPathAndIssueCommand:2693:PSP selected path "vmhba37:C1:T6:L0" in a bad state (dead)on device "naa.64ed2a85165dc1561cf7c4851a02c0d6".2013-05-16T16:08:24.921Z cpu10:10448)NMP: nmp_ThrottleLogForDevice:2318: Cmd 0x2a (0x412440b242c0, 4863) to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" on path "vmhba37:C1:T6:L0" Failed: H:0x1 D:0x0 P:0x0 Possible sense data: 0x0 0x0 0x0. Act:FAILOVER2013-05-16T16:08:24.921Z cpu10:10448)WARNING: NMP: nmp_DeviceRetryCommand:133:Device "naa.64ed2a85165dc1561cf7c4851a02c0d6": awaiting fast path state update for failover with I/O blocked. No prior reservation exists on the device.2013-05-16T16:08:24.921Z cpu10:10448)WARNING: NMP: nmp_DeviceStartLoop:721:NMP Device "naa.64ed2a85165dc1561cf7c4851a02c0d6" is blocked. Not starting I/O from device.2013-05-16T16:08:24.964Z cpu7:2088)WARNING: dell_psp_eql_routed: psp_eqlUpdatePathSelection:1014:Path is reported as inactive (0x50475304)2013-05-16T16:08:24.964Z cpu7:2088)WARNING: dell_psp_eql_routed: psp_eqlUpdatePathSelection:1014:Path is reported as inactive (0x50475304)2013-05-16T16:08:24.964Z cpu7:2088)WARNING: dell_psp_eql_routed: psp_eqlUpdatePathSelection:1014:Path is reported as inactive (0x50475304)2013-05-16T16:08:24.965Z cpu0:2088)WARNING: dell_psp_eql_routed: psp_eqlUpdatePathSelection:1014:Path is reported as inactive (0x50475304)2013-05-16T16:08:24.965Z cpu0:2088)WARNING: dell_psp_eql_routed: psp_eqlUpdatePathSelection:1014:Path is reported as inactive (0x50475304)2013-05-16T16:08:24.965Z cpu0:2088)WARNING: dell_psp_eql_routed: psp_eqlUpdatePathSelection:1014:Path is reported as inactive (0x50475304)2013-05-16T16:08:24.967Z cpu6:2209)ScsiPath: 4963: DeletePath : adapter=vmhba37, channel=1, target=6, lun=02013-05-16T16:08:24.967Z cpu6:2209)WARNING: dell_psp_eql_routed: psp_eqlUpdatePathSelection:1014:Path is reported as inactive (0x50475304)2013-05-16T16:08:24.967Z cpu6:2209)WARNING: dell_psp_eql_routed: psp_eqlUpdatePathSelection:1014:Path is reported as inactive (0x50475304)2013-05-16T16:08:24.967Z cpu6:2209)WARNING: ScsiPath: 5022: Remove path: vmhba37:C1:T6:L02013-05-16T16:08:24.967Z cpu6:2206)ScsiPath: 4963: DeletePath : adapter=vmhba37, channel=2, target=6, lun=02013-05-16T16:08:24.967Z cpu6:2206)WARNING: dell_psp_eql_routed: psp_eqlUpdatePathSelection:1014:Path is reported as inactive (0x50475304)2013-05-16T16:08:24.967Z cpu6:2206)WARNING: ScsiPath: 5022: Remove path: vmhba37:C2:T6:L02013-05-16T16:08:24.967Z cpu6:2206)ScsiPath: 4963: DeletePath : adapter=vmhba37, channel=3, target=6, lun=02013-05-16T16:08:24.968Z cpu2:2206)WARNING: ScsiPath: 5022: Remove path: vmhba37:C3:T6:L02013-05-16T16:08:25.232Z cpu12:2698)WARNING: NMP: nmpDeviceAttemptFailover:599:Retry world failover device "naa.64ed2a85165dc1561cf7c4851a02c0d6" - issuing command 0x412440b242c02013-05-16T16:08:25.233Z cpu15:2063)NMP: nmpCompleteRetryForPath:321: Retry world recovered device "naa.64ed2a85165dc1561cf7c4851a02c0d6"2013-05-16T16:08:25.271Z cpu1:2724)iscsi_vmk: iscsivmk_ConnNetRegister: socket 0x410023555110 network resource pool netsched.pools.persist.iscsi associated2013-05-16T16:08:25.271Z cpu1:2724)iscsi_vmk: iscsivmk_ConnNetRegister: socket 0x410023555110 network tracker id 1 tracker.iSCSI.192.168.90.100 associated2013-05-16T16:08:25.272Z cpu1:2724)iscsi_vmk: iscsivmk_ConnNetRegister: socket 0x410023490210 network resource pool netsched.pools.persist.iscsi associated2013-05-16T16:08:25.272Z cpu1:2724)iscsi_vmk: iscsivmk_ConnNetRegister: socket 0x410023490210 network tracker id 1 tracker.iSCSI.192.168.90.100 associated2013-05-16T16:08:25.272Z cpu1:2724)iscsi_vmk: iscsivmk_ConnNetRegister: socket 0x41002cdc23b0 network resource pool netsched.pools.persist.iscsi associated2013-05-16T16:08:25.272Z cpu1:2724)iscsi_vmk: iscsivmk_ConnNetRegister: socket 0x41002cdc23b0 network tracker id 1 tracker.iSCSI.192.168.90.100 associated2013-05-16T16:08:25.272Z cpu1:2724)iscsi_vmk: iscsivmk_ConnNetRegister: socket 0x41002cdc2a50 network resource pool netsched.pools.persist.iscsi associated2013-05-16T16:08:25.272Z cpu1:2724)iscsi_vmk: iscsivmk_ConnNetRegister: socket 0x41002cdc2a50 network tracker id 1 tracker.iSCSI.192.168.90.100 associated2013-05-16T16:08:25.280Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: vmhba37:CH:1 T:6 CN:0: Failed to receive data: Connection closed by peer2013-05-16T16:08:25.280Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: Sess [ISID: TARGET: (null) TPGT: 0 TSIH: 0]2013-05-16T16:08:25.280Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: Conn [CID: 0 L: 192.168.90.53:49974 R: 192.168.90.100:3260]2013-05-16T16:08:25.280Z cpu1:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: vmhba37:CH:1 T:6 CN:0: Connection rx notifying failure: Failed to Receive. State=Bound2013-05-16T16:08:25.280Z cpu1:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: Sess [ISID: TARGET: (null) TPGT: 0 TSIH: 0]2013-05-16T16:08:25.280Z cpu1:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: Conn [CID: 0 L: 192.168.90.53:49974 R: 192.168.90.100:3260]2013-05-16T16:08:25.289Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: vmhba37:CH:2 T:6 CN:0: Failed to receive data: Connection closed by peer2013-05-16T16:08:25.289Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: Sess [ISID: TARGET: (null) TPGT: 0 TSIH: 0]2013-05-16T16:08:25.289Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: Conn [CID: 0 L: 192.168.90.51:59154 R: 192.168.90.100:3260]2013-05-16T16:08:25.289Z cpu1:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: vmhba37:CH:2 T:6 CN:0: Connection rx notifying failure: Failed to Receive. State=Bound2013-05-16T16:08:25.289Z cpu1:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: Sess [ISID: TARGET: (null) TPGT: 0 TSIH: 0]2013-05-16T16:08:25.289Z cpu1:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: Conn [CID: 0 L: 192.168.90.51:59154 R: 192.168.90.100:3260]2013-05-16T16:08:25.298Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: vmhba37:CH:3 T:6 CN:0: Failed to receive data: Connection closed by peer2013-05-16T16:08:25.298Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: Sess [ISID: TARGET: (null) TPGT: 0 TSIH: 0]2013-05-16T16:08:25.298Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: Conn [CID: 0 L: 192.168.90.52:53935 R: 192.168.90.100:3260]2013-05-16T16:08:25.298Z cpu1:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: vmhba37:CH:3 T:6 CN:0: Connection rx notifying failure: Failed to Receive. State=Bound2013-05-16T16:08:25.298Z cpu1:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: Sess [ISID: TARGET: (null) TPGT: 0 TSIH: 0]2013-05-16T16:08:25.298Z cpu1:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: Conn [CID: 0 L: 192.168.90.52:53935 R: 192.168.90.100:3260]2013-05-16T16:08:25.306Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: vmhba37:CH:4 T:6 CN:0: Failed to receive data: Connection closed by peer2013-05-16T16:08:25.306Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: Sess [ISID: TARGET: (null) TPGT: 0 TSIH: 0]2013-05-16T16:08:25.306Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: Conn [CID: 0 L: 192.168.90.50:49401 R: 192.168.90.100:3260]2013-05-16T16:08:25.306Z cpu1:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: vmhba37:CH:4 T:6 CN:0: Connection rx notifying failure: Failed to Receive. State=Bound2013-05-16T16:08:25.306Z cpu1:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: Sess [ISID: TARGET: (null) TPGT: 0 TSIH: 0]2013-05-16T16:08:25.306Z cpu1:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: Conn [CID: 0 L: 192.168.90.50:49401 R: 192.168.90.100:3260]2013-05-16T16:08:25.507Z cpu7:2055)NMP: nmp_ThrottleLogForDevice:2318: Cmd 0x1a (0x412401cfc340, 0) to dev "mpx.vmhba1:C0:T0:L0" on path "vmhba1:C0:T0:L0" Failed: H:0x0 D:0x2 P:0x0 Valid sense data: 0x5 0x20 0x0. Act:NONE2013-05-16T16:08:25.507Z cpu7:2055)ScsiDeviceIO: 2322: Cmd(0x412401cfc340) 0x1a, CmdSN 0x1175b from world 0 to dev "mpx.vmhba1:C0:T0:L0" failed H:0x0 D:0x2 P:0x0 Valid sense data: 0x5 0x20 0x0.2013-05-16T16:08:25.560Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: vmhba37:CH:1 T:6 CN:0: iSCSI connection is being marked "OFFLINE" (Event:4)2013-05-16T16:08:25.560Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: Sess [ISID: TARGET: (null) TPGT: 0 TSIH: 0]2013-05-16T16:08:25.560Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: Conn [CID: 0 L: 192.168.90.53:49974 R: 192.168.90.100:3260]2013-05-16T16:08:25.561Z cpu1:2724)iscsi_vmk: iscsivmk_ConnNetRegister: socket 0x41002cdd7210 network resource pool netsched.pools.persist.iscsi associated2013-05-16T16:08:25.561Z cpu1:2724)iscsi_vmk: iscsivmk_ConnNetRegister: socket 0x41002cdd7210 network tracker id 1 tracker.iSCSI.192.168.90.103 associated2013-05-16T16:08:25.561Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: vmhba37:CH:2 T:6 CN:0: iSCSI connection is being marked "OFFLINE" (Event:4)2013-05-16T16:08:25.561Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: Sess [ISID: TARGET: (null) TPGT: 0 TSIH: 0]2013-05-16T16:08:25.561Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: Conn [CID: 0 L: 192.168.90.51:59154 R: 192.168.90.100:3260]2013-05-16T16:08:25.562Z cpu1:2724)iscsi_vmk: iscsivmk_ConnNetRegister: socket 0x41002347f910 network resource pool netsched.pools.persist.iscsi associated2013-05-16T16:08:25.562Z cpu1:2724)iscsi_vmk: iscsivmk_ConnNetRegister: socket 0x41002347f910 network tracker id 1 tracker.iSCSI.192.168.90.103 associated2013-05-16T16:08:25.562Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: vmhba37:CH:3 T:6 CN:0: iSCSI connection is being marked "OFFLINE" (Event:4)2013-05-16T16:08:25.562Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: Sess [ISID: TARGET: (null) TPGT: 0 TSIH: 0]2013-05-16T16:08:25.562Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: Conn [CID: 0 L: 192.168.90.52:53935 R: 192.168.90.100:3260]2013-05-16T16:08:25.563Z cpu1:2724)iscsi_vmk: iscsivmk_ConnNetRegister: socket 0x41002cdc23b0 network resource pool netsched.pools.persist.iscsi associated2013-05-16T16:08:25.563Z cpu1:2724)iscsi_vmk: iscsivmk_ConnNetRegister: socket 0x41002cdc23b0 network tracker id 1 tracker.iSCSI.192.168.90.101 associated2013-05-16T16:08:25.563Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: vmhba37:CH:4 T:6 CN:0: iSCSI connection is being marked "OFFLINE" (Event:4)2013-05-16T16:08:25.563Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: Sess [ISID: TARGET: (null) TPGT: 0 TSIH: 0]2013-05-16T16:08:25.563Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: Conn [CID: 0 L: 192.168.90.50:49401 R: 192.168.90.100:3260]2013-05-16T16:08:25.564Z cpu1:2724)iscsi_vmk: iscsivmk_ConnNetRegister: socket 0x41002cdc2a50 network resource pool netsched.pools.persist.iscsi associated2013-05-16T16:08:25.564Z cpu1:2724)iscsi_vmk: iscsivmk_ConnNetRegister: socket 0x41002cdc2a50 network tracker id 1 tracker.iSCSI.192.168.90.102 associated2013-05-16T16:08:26.869Z cpu11:2724)WARNING: iscsi_vmk: iscsivmk_StartConnection: vmhba37:CH:1 T:6 CN:0: iSCSI connection is being marked "ONLINE"2013-05-16T16:08:26.869Z cpu11:2724)WARNING: iscsi_vmk: iscsivmk_StartConnection: Sess [ISID: 00023d000008 TARGET: iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f TPGT: 1 TSIH: 0]2013-05-16T16:08:26.869Z cpu11:2724)WARNING: iscsi_vmk: iscsivmk_StartConnection: Conn [CID: 0 L: 192.168.90.53:56744 R: 192.168.90.103:3260]2013-05-16T16:08:26.870Z cpu11:2724)WARNING: iscsi_vmk: iscsivmk_StartConnection: vmhba37:CH:2 T:6 CN:0: iSCSI connection is being marked "ONLINE"2013-05-16T16:08:26.870Z cpu11:2724)WARNING: iscsi_vmk: iscsivmk_StartConnection: Sess [ISID: 00023d000006 TARGET: iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f TPGT: 1 TSIH: 0]2013-05-16T16:08:26.870Z cpu11:2724)WARNING: iscsi_vmk: iscsivmk_StartConnection: Conn [CID: 0 L: 192.168.90.51:53550 R: 192.168.90.103:3260]2013-05-16T16:08:26.871Z cpu11:2724)WARNING: iscsi_vmk: iscsivmk_StartConnection: vmhba37:CH:3 T:6 CN:0: iSCSI connection is being marked "ONLINE"2013-05-16T16:08:26.871Z cpu11:2724)WARNING: iscsi_vmk: iscsivmk_StartConnection: Sess [ISID: 00023d000007 TARGET: iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f TPGT: 1 TSIH: 0]2013-05-16T16:08:26.871Z cpu11:2724)WARNING: iscsi_vmk: iscsivmk_StartConnection: Conn [CID: 0 L: 192.168.90.52:62640 R: 192.168.90.101:3260]2013-05-16T16:08:26.872Z cpu11:2724)WARNING: iscsi_vmk: iscsivmk_StartConnection: vmhba37:CH:4 T:6 CN:0: iSCSI connection is being marked "ONLINE"2013-05-16T16:08:26.872Z cpu11:2724)WARNING: iscsi_vmk: iscsivmk_StartConnection: Sess [ISID: 00023d010005 TARGET: iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f TPGT: 1 TSIH: 0]2013-05-16T16:08:26.872Z cpu11:2724)WARNING: iscsi_vmk: iscsivmk_StartConnection: Conn [CID: 0 L: 192.168.90.50:53740 R: 192.168.90.102:3260]2013-05-16T16:08:27.085Z cpu6:3533)ScsiScan: 1098: Path 'vmhba37:C1:T6:L0': Vendor: 'EQLOGIC ' Model: '100E-00 ' Rev: '5.2 '2013-05-16T16:08:27.085Z cpu6:3533)ScsiScan: 1101: Path 'vmhba37:C1:T6:L0': Type: 0x0, ANSI rev: 5, TPGS: 1 (implicit only)2013-05-16T16:08:27.085Z cpu4:3533)ScsiScan: 1582: Add path: vmhba37:C1:T6:L02013-05-16T16:08:27.085Z cpu4:3533)ScsiScan: 1098: Path 'vmhba37:C2:T6:L0': Vendor: 'EQLOGIC ' Model: '100E-00 ' Rev: '5.2 '2013-05-16T16:08:27.085Z cpu4:3533)ScsiScan: 1101: Path 'vmhba37:C2:T6:L0': Type: 0x0, ANSI rev: 5, TPGS: 1 (implicit only)2013-05-16T16:08:27.086Z cpu4:3533)ScsiScan: 1582: Add path: vmhba37:C2:T6:L02013-05-16T16:08:27.087Z cpu4:3533)ScsiScan: 1098: Path 'vmhba37:C3:T6:L0': Vendor: 'EQLOGIC ' Model: '100E-00 ' Rev: '5.2 '2013-05-16T16:08:27.087Z cpu4:3533)ScsiScan: 1101: Path 'vmhba37:C3:T6:L0': Type: 0x0, ANSI rev: 5, TPGS: 1 (implicit only)2013-05-16T16:08:27.091Z cpu0:3533)ScsiScan: 1582: Add path: vmhba37:C3:T6:L02013-05-16T16:08:27.091Z cpu0:3533)ScsiScan: 1098: Path 'vmhba37:C4:T6:L0': Vendor: 'EQLOGIC ' Model: '100E-00 ' Rev: '5.2 '2013-05-16T16:08:27.091Z cpu0:3533)ScsiScan: 1101: Path 'vmhba37:C4:T6:L0': Type: 0x0, ANSI rev: 5, TPGS: 1 (implicit only)2013-05-16T16:08:27.092Z cpu0:3533)ScsiScan: 1582: Add path: vmhba37:C4:T6:L02013-05-16T16:08:27.092Z cpu0:3533)ScsiPath: 4541: Plugin 'NMP' claimed path 'vmhba37:C4:T6:L0'2013-05-16T16:08:27.092Z cpu0:3533)ScsiPath: 4541: Plugin 'NMP' claimed path 'vmhba37:C3:T6:L0'2013-05-16T16:08:27.092Z cpu0:3533)ScsiPath: 4541: Plugin 'NMP' claimed path 'vmhba37:C2:T6:L0'2013-05-16T16:08:27.092Z cpu0:3533)ScsiPath: 4541: Plugin 'NMP' claimed path 'vmhba37:C1:T6:L0'2013-05-16T16:08:27.189Z cpu13:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: vmhba37:CH:0 T:6 CN:0: Failed to receive data: Connection closed by peer2013-05-16T16:08:27.189Z cpu13:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: Sess [ISID: 00023d000005 TARGET: iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f TPGT: 1 TSIH: 0]2013-05-16T16:08:27.189Z cpu13:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: Conn [CID: 0 L: 192.168.90.50:51627 R: 192.168.90.104:3260]2013-05-16T16:08:27.189Z cpu13:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: vmhba37:CH:0 T:6 CN:0: Connection rx notifying failure: Failed to Receive. State=Online2013-05-16T16:08:27.189Z cpu13:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: Sess [ISID: 00023d000005 TARGET: iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f TPGT: 1 TSIH: 0]2013-05-16T16:08:27.189Z cpu13:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: Conn [CID: 0 L: 192.168.90.50:51627 R: 192.168.90.104:3260]2013-05-16T16:08:27.189Z cpu10:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: vmhba37:CH:0 T:6 CN:0: iSCSI connection is being marked "OFFLINE" (Event:6)2013-05-16T16:08:27.189Z cpu10:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: Sess [ISID: 00023d000005 TARGET: iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f TPGT: 1 TSIH: 0]2013-05-16T16:08:27.189Z cpu10:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: Conn [CID: 0 L: 192.168.90.50:51627 R: 192.168.90.104:3260]2013-05-16T16:08:27.189Z cpu14:2677)WARNING: NMP: nmp_DeviceRequestFastDeviceProbe:237:NMP device "naa.64ed2a85165dc1561cf7c4851a02c0d6" state in doubt; requested fast path state update...2013-05-16T16:08:27.189Z cpu14:2677)ScsiDeviceIO: 2309: Cmd(0x412440985380) 0x28, CmdSN 0x8000003a from world 4863 to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" failed H:0x2 D:0x0 P:0x0 Possible sense data: 0x0 0x0 0x0.2013-05-16T16:08:27.238Z cpu10:2058)WARNING: NMP: nmp_DeviceRequestFastDeviceProbe:237:NMP device "naa.64ed2a85165dc1561cf7c4851a02c0d6" state in doubt; requested fast path state update...2013-05-16T16:08:27.278Z cpu15:2063)NMP: nmp_ThrottleLogForDevice:2318: Cmd 0x28 (0x412441114a40, 4863) to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" on path "vmhba37:C0:T6:L0" Failed: H:0x2 D:0x0 P:0x0 Possible sense data: 0x0 0x0 0x0. Act:EVAL2013-05-16T16:08:27.314Z cpu14:2062)ScsiDeviceIO: 2309: Cmd(0x41244136e280) 0x28, CmdSN 0x800000d9 from world 4863 to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" failed H:0x2 D:0x0 P:0x0 Possible sense data: 0x0 0x0 0x0.2013-05-16T16:08:27.314Z cpu14:2062)ScsiDeviceIO: 2309: Cmd(0x412441832f00) 0x28, CmdSN 0x800000ca from world 4863 to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" failed H:0x2 D:0x0 P:0x0 Possible sense data: 0x0 0x0 0x0.2013-05-16T16:08:27.368Z cpu10:2058)NMP: nmp_ThrottleLogForDevice:2318: Cmd 0x28 (0x412440f813c0, 4863) to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" on path "vmhba37:C0:T6:L0" Failed: H:0x2 D:0x0 P:0x0 Possible sense data: 0x0 0x0 0x0. Act:EVAL2013-05-16T16:08:27.456Z cpu9:2057)NMP: nmp_ThrottleLogForDevice:2318: Cmd 0x28 (0x412440f50600, 4863) to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" on path "vmhba37:C0:T6:L0" Failed: H:0x2 D:0x0 P:0x0 Possible sense data: 0x0 0x0 0x0. Act:EVAL2013-05-16T16:08:27.456Z cpu9:2057)ScsiDeviceIO: 2309: Cmd(0x412440f50600) 0x28, CmdSN 0x80000044 from world 4863 to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" failed H:0x2 D:0x0 P:0x0 Possible sense data: 0x0 0x0 0x0.2013-05-16T16:08:27.478Z cpu11:2059)NMP: nmp_ThrottleLogForDevice:2318: Cmd 0x28 (0x412440f813c0, 4863) to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" on path "vmhba37:C0:T6:L0" Failed: H:0x1 D:0x0 P:0x0 Possible sense data: 0x0 0x0 0x0. Act:FAILOVER2013-05-16T16:08:27.478Z cpu11:2059)WARNING: NMP: nmp_DeviceRetryCommand:133:Device "naa.64ed2a85165dc1561cf7c4851a02c0d6": awaiting fast path state update for failover with I/O blocked. No prior reservation exists on the device.2013-05-16T16:08:27.478Z cpu11:2059)NMP: nmp_ThrottleLogForDevice:2318: Cmd 0x28 (0x41244054a180, 4863) to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" on path "vmhba37:C0:T6:L0" Failed: H:0x1 D:0x0 P:0x0 Possible sense data: 0x0 0x0 0x0. Act:FAILOVER2013-05-16T16:08:27.478Z cpu11:2059)NMP: nmp_ThrottleLogForDevice:2318: Cmd 0x28 (0x41244136d180, 4863) to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" on path "vmhba37:C0:T6:L0" Failed: H:0x1 D:0x0 P:0x0 Possible sense data: 0x0 0x0 0x0. Act:FAILOVER2013-05-16T16:08:27.488Z cpu2:2196)WARNING: dell_psp_eql_routed: psp_eqlUpdatePathSelection:1014:Path is reported as inactive (0x50475304)2013-05-16T16:08:27.488Z cpu6:2698)WARNING: NMP: nmpDeviceAttemptFailover:599:Retry world failover device "naa.64ed2a85165dc1561cf7c4851a02c0d6" - issuing command 0x412440f813c02013-05-16T16:08:27.497Z cpu9:2057)NMP: nmpCompleteRetryForPath:321: Retry world recovered device "naa.64ed2a85165dc1561cf7c4851a02c0d6"2013-05-16T16:08:28.196Z cpu7:2206)ScsiPath: 4963: DeletePath : adapter=vmhba37, channel=0, target=6, lun=02013-05-16T16:08:28.197Z cpu14:2062)WARNING: NMP: nmp_DeviceStartLoop:721:NMP Device "naa.64ed2a85165dc1561cf7c4851a02c0d6" is blocked. Not starting I/O from device.2013-05-16T16:08:28.198Z cpu14:2062)WARNING: NMP: nmp_DeviceStartLoop:721:NMP Device "naa.64ed2a85165dc1561cf7c4851a02c0d6" is blocked. Not starting I/O from device.2013-05-16T16:08:28.201Z cpu14:2062)WARNING: NMP: nmp_DeviceStartLoop:721:NMP Device "naa.64ed2a85165dc1561cf7c4851a02c0d6" is blocked. Not starting I/O from device.2013-05-16T16:08:28.201Z cpu10:2058)WARNING: NMP: nmp_DeviceStartLoop:721:NMP Device "naa.64ed2a85165dc1561cf7c4851a02c0d6" is blocked. Not starting I/O from device.2013-05-16T16:08:28.229Z cpu14:2062)WARNING: NMP: nmp_DeviceStartLoop:721:NMP Device "naa.64ed2a85165dc1561cf7c4851a02c0d6" is blocked. Not starting I/O from device.2013-05-16T16:08:28.229Z cpu4:2206)WARNING: ScsiPath: 5022: Remove path: vmhba37:C0:T6:L02013-05-16T16:08:38.588Z cpu5:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: vmhba37:CH:2 T:6 CN:0: Failed to receive data: Connection closed by peer2013-05-16T16:08:38.589Z cpu5:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: Sess [ISID: 00023d000006 TARGET: iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f TPGT: 1 TSIH: 0]2013-05-16T16:08:38.589Z cpu5:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: Conn [CID: 0 L: 192.168.90.51:53550 R: 192.168.90.103:3260]2013-05-16T16:08:38.589Z cpu5:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: vmhba37:CH:2 T:6 CN:0: Connection rx notifying failure: Failed to Receive. State=Online2013-05-16T16:08:38.589Z cpu5:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: Sess [ISID: 00023d000006 TARGET: iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f TPGT: 1 TSIH: 0]2013-05-16T16:08:38.589Z cpu5:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: Conn [CID: 0 L: 192.168.90.51:53550 R: 192.168.90.103:3260]2013-05-16T16:08:38.589Z cpu5:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: vmhba37:CH:2 T:6 CN:0: iSCSI connection is being marked "OFFLINE" (Event:6)2013-05-16T16:08:38.589Z cpu5:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: Sess [ISID: 00023d000006 TARGET: iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f TPGT: 1 TSIH: 0]2013-05-16T16:08:38.589Z cpu5:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: Conn [CID: 0 L: 192.168.90.51:53550 R: 192.168.90.103:3260]2013-05-16T16:08:38.589Z cpu2:2701)WARNING: NMP: nmp_DeviceRequestFastDeviceProbe:237:NMP device "naa.64ed2a85165dc1561cf7c4851a02c0d6" state in doubt; requested fast path state update...2013-05-16T16:08:38.589Z cpu2:2701)ScsiDeviceIO: 2309: Cmd(0x412441780f40) 0x28, CmdSN 0x80000047 from world 4863 to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" failed H:0x2 D:0x0 P:0x0 Possible sense data: 0x0 0x0 0x0.2013-05-16T16:08:38.590Z cpu5:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: vmhba37:CH:3 T:6 CN:0: Failed to receive data: Connection closed by peer2013-05-16T16:08:38.590Z cpu5:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: Sess [ISID: 00023d000007 TARGET: iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f TPGT: 1 TSIH: 0]2013-05-16T16:08:38.590Z cpu5:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: Conn [CID: 0 L: 192.168.90.52:62640 R: 192.168.90.101:3260]2013-05-16T16:08:38.590Z cpu5:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: vmhba37:CH:3 T:6 CN:0: Connection rx notifying failure: Failed to Receive. State=Online2013-05-16T16:08:38.590Z cpu5:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: Sess [ISID: 00023d000007 TARGET: iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f TPGT: 1 TSIH: 0]2013-05-16T16:08:38.590Z cpu5:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: Conn [CID: 0 L: 192.168.90.52:62640 R: 192.168.90.101:3260]2013-05-16T16:08:38.590Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: vmhba37:CH:3 T:6 CN:0: iSCSI connection is being marked "OFFLINE" (Event:6)2013-05-16T16:08:38.590Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: Sess [ISID: 00023d000007 TARGET: iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f TPGT: 1 TSIH: 0]2013-05-16T16:08:38.590Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: Conn [CID: 0 L: 192.168.90.52:62640 R: 192.168.90.101:3260]2013-05-16T16:08:38.590Z cpu4:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: vmhba37:CH:4 T:6 CN:0: Failed to receive data: Connection closed by peer2013-05-16T16:08:38.590Z cpu4:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: Sess [ISID: 00023d010005 TARGET: iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f TPGT: 1 TSIH: 0]2013-05-16T16:08:38.590Z cpu4:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: Conn [CID: 0 L: 192.168.90.50:53740 R: 192.168.90.102:3260]2013-05-16T16:08:38.590Z cpu4:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: vmhba37:CH:4 T:6 CN:0: Connection rx notifying failure: Failed to Receive. State=Online2013-05-16T16:08:38.590Z cpu4:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: Sess [ISID: 00023d010005 TARGET: iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f TPGT: 1 TSIH: 0]2013-05-16T16:08:38.590Z cpu4:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: Conn [CID: 0 L: 192.168.90.50:53740 R: 192.168.90.102:3260]2013-05-16T16:08:38.590Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: vmhba37:CH:4 T:6 CN:0: iSCSI connection is being marked "OFFLINE" (Event:6)2013-05-16T16:08:38.590Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: Sess [ISID: 00023d010005 TARGET: iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f TPGT: 1 TSIH: 0]2013-05-16T16:08:38.590Z cpu1:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: Conn [CID: 0 L: 192.168.90.50:53740 R: 192.168.90.102:3260]2013-05-16T16:08:38.651Z cpu11:2059)ScsiDeviceIO: 2309: Cmd(0x412441cbc700) 0x28, CmdSN 0x800000dd from world 4863 to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" failed H:0x2 D:0x0 P:0x0 Possible sense data: 0x0 0x0 0x0.2013-05-16T16:08:38.651Z cpu11:2059)NMP: nmp_ThrottleLogForDevice:2318: Cmd 0x28 (0x41244101b280, 4863) to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" on path "vmhba37:C4:T6:L0" Failed: H:0x2 D:0x0 P:0x0 Possible sense data: 0x0 0x0 0x0. Act:EVAL2013-05-16T16:08:38.651Z cpu11:2059)ScsiDeviceIO: 2309: Cmd(0x41244101b280) 0x28, CmdSN 0x800000b0 from world 4863 to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" failed H:0x2 D:0x0 P:0x0 Possible sense data: 0x0 0x0 0x0.2013-05-16T16:08:38.681Z cpu11:2059)NMP: nmp_ThrottleLogForDevice:2318: Cmd 0x28 (0x41244101b280, 4863) to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" on path "vmhba37:C4:T6:L0" Failed: H:0x2 D:0x0 P:0x0 Possible sense data: 0x0 0x0 0x0. Act:EVAL2013-05-16T16:08:38.731Z cpu11:2059)NMP: nmp_ThrottleLogForDevice:2318: Cmd 0x28 (0x41244101b280, 4863) to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" on path "vmhba37:C4:T6:L0" Failed: H:0x2 D:0x0 P:0x0 Possible sense data: 0x0 0x0 0x0. Act:EVAL2013-05-16T16:08:38.796Z cpu11:4863)NMP: nmp_ThrottleLogForDevice:2318: Cmd 0x28 (0x41244101b280, 4863) to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" on path "vmhba37:C4:T6:L0" Failed: H:0x2 D:0x0 P:0x0 Possible sense data: 0x0 0x0 0x0. Act:EVAL2013-05-16T16:08:38.842Z cpu5:2088)WARNING: dell_psp_eql_routed: psp_eqlUpdatePathSelection:1014:Path is reported as inactive (0x50475304)2013-05-16T16:08:38.842Z cpu5:2088)WARNING: dell_psp_eql_routed: psp_eqlUpdatePathSelection:1014:Path is reported as inactive (0x50475304)2013-05-16T16:08:38.842Z cpu5:2088)WARNING: dell_psp_eql_routed: psp_eqlUpdatePathSelection:1014:Path is reported as inactive (0x50475304)2013-05-16T16:08:38.846Z cpu8:2207)ScsiPath: 4963: DeletePath : adapter=vmhba37, channel=2, target=6, lun=02013-05-16T16:08:38.846Z cpu8:2207)WARNING: dell_psp_eql_routed: psp_eqlUpdatePathSelection:1014:Path is reported as inactive (0x50475304)2013-05-16T16:08:38.846Z cpu8:2207)WARNING: dell_psp_eql_routed: psp_eqlUpdatePathSelection:1014:Path is reported as inactive (0x50475304)2013-05-16T16:08:38.846Z cpu8:2207)WARNING: ScsiPath: 5022: Remove path: vmhba37:C2:T6:L02013-05-16T16:08:38.846Z cpu8:2209)ScsiPath: 4963: DeletePath : adapter=vmhba37, channel=3, target=6, lun=02013-05-16T16:08:38.846Z cpu8:2209)WARNING: dell_psp_eql_routed: psp_eqlUpdatePathSelection:1014:Path is reported as inactive (0x50475304)2013-05-16T16:08:38.846Z cpu8:2209)WARNING: ScsiPath: 5022: Remove path: vmhba37:C3:T6:L02013-05-16T16:08:38.846Z cpu8:2209)ScsiPath: 4963: DeletePath : adapter=vmhba37, channel=4, target=6, lun=02013-05-16T16:08:38.846Z cpu8:2209)WARNING: ScsiPath: 5022: Remove path: vmhba37:C4:T6:L02013-05-16T16:08:39.199Z cpu1:2724)iscsi_vmk: iscsivmk_ConnNetRegister: socket 0x410023490210 network resource pool netsched.pools.persist.iscsi associated2013-05-16T16:08:39.200Z cpu1:2724)iscsi_vmk: iscsivmk_ConnNetRegister: socket 0x410023490210 network tracker id 1 tracker.iSCSI.192.168.90.100 associated2013-05-16T16:08:39.200Z cpu1:2724)iscsi_vmk: iscsivmk_ConnNetRegister: socket 0x410023461d30 network resource pool netsched.pools.persist.iscsi associated2013-05-16T16:08:39.200Z cpu1:2724)iscsi_vmk: iscsivmk_ConnNetRegister: socket 0x410023461d30 network tracker id 1 tracker.iSCSI.192.168.90.100 associated2013-05-16T16:08:39.200Z cpu4:2724)iscsi_vmk: iscsivmk_ConnNetRegister: socket 0x41002cdc23b0 network resource pool netsched.pools.persist.iscsi associated2013-05-16T16:08:39.200Z cpu4:2724)iscsi_vmk: iscsivmk_ConnNetRegister: socket 0x41002cdc23b0 network tracker id 1 tracker.iSCSI.192.168.90.100 associated2013-05-16T16:08:39.201Z cpu4:2724)iscsi_vmk: iscsivmk_ConnNetRegister: socket 0x41002cdc2a50 network resource pool netsched.pools.persist.iscsi associated2013-05-16T16:08:39.201Z cpu4:2724)iscsi_vmk: iscsivmk_ConnNetRegister: socket 0x41002cdc2a50 network tracker id 1 tracker.iSCSI.192.168.90.100 associated2013-05-16T16:08:39.208Z cpu4:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: vmhba37:CH:0 T:6 CN:0: Failed to receive data: Connection closed by peer2013-05-16T16:08:39.208Z cpu4:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: Sess [ISID: TARGET: (null) TPGT: 0 TSIH: 0]2013-05-16T16:08:39.208Z cpu4:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: Conn [CID: 0 L: 192.168.90.50:63278 R: 192.168.90.100:3260]2013-05-16T16:08:39.208Z cpu4:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: vmhba37:CH:0 T:6 CN:0: Connection rx notifying failure: Failed to Receive. State=Bound2013-05-16T16:08:39.208Z cpu4:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: Sess [ISID: TARGET: (null) TPGT: 0 TSIH: 0]2013-05-16T16:08:39.208Z cpu4:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: Conn [CID: 0 L: 192.168.90.50:63278 R: 192.168.90.100:3260]2013-05-16T16:08:39.217Z cpu4:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: vmhba37:CH:2 T:6 CN:0: Failed to receive data: Connection closed by peer2013-05-16T16:08:39.217Z cpu4:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: Sess [ISID: TARGET: (null) TPGT: 0 TSIH: 0]2013-05-16T16:08:39.217Z cpu4:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: Conn [CID: 0 L: 192.168.90.52:51827 R: 192.168.90.100:3260]2013-05-16T16:08:39.217Z cpu4:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: vmhba37:CH:2 T:6 CN:0: Connection rx notifying failure: Failed to Receive. State=Bound2013-05-16T16:08:39.217Z cpu4:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: Sess [ISID: TARGET: (null) TPGT: 0 TSIH: 0]2013-05-16T16:08:39.217Z cpu4:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: Conn [CID: 0 L: 192.168.90.52:51827 R: 192.168.90.100:3260]2013-05-16T16:08:39.225Z cpu4:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: vmhba37:CH:3 T:6 CN:0: Failed to receive data: Connection closed by peer2013-05-16T16:08:39.225Z cpu4:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: Sess [ISID: TARGET: (null) TPGT: 0 TSIH: 0]2013-05-16T16:08:39.225Z cpu4:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: Conn [CID: 0 L: 192.168.90.51:56110 R: 192.168.90.100:3260]2013-05-16T16:08:39.225Z cpu4:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: vmhba37:CH:3 T:6 CN:0: Connection rx notifying failure: Failed to Receive. State=Bound2013-05-16T16:08:39.225Z cpu4:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: Sess [ISID: TARGET: (null) TPGT: 0 TSIH: 0]2013-05-16T16:08:39.225Z cpu4:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: Conn [CID: 0 L: 192.168.90.51:56110 R: 192.168.90.100:3260]2013-05-16T16:08:39.233Z cpu4:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: vmhba37:CH:4 T:6 CN:0: Failed to receive data: Connection closed by peer2013-05-16T16:08:39.233Z cpu4:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: Sess [ISID: TARGET: (null) TPGT: 0 TSIH: 0]2013-05-16T16:08:39.233Z cpu4:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: Conn [CID: 0 L: 192.168.90.53:57285 R: 192.168.90.100:3260]2013-05-16T16:08:39.233Z cpu4:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: vmhba37:CH:4 T:6 CN:0: Connection rx notifying failure: Failed to Receive. State=Bound2013-05-16T16:08:39.233Z cpu4:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: Sess [ISID: TARGET: (null) TPGT: 0 TSIH: 0]2013-05-16T16:08:39.233Z cpu4:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: Conn [CID: 0 L: 192.168.90.53:57285 R: 192.168.90.100:3260]2013-05-16T16:08:39.494Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: vmhba37:CH:0 T:6 CN:0: iSCSI connection is being marked "OFFLINE" (Event:4)2013-05-16T16:08:39.494Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: Sess [ISID: TARGET: (null) TPGT: 0 TSIH: 0]2013-05-16T16:08:39.494Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: Conn [CID: 0 L: 192.168.90.50:63278 R: 192.168.90.100:3260]2013-05-16T16:08:39.495Z cpu0:2724)iscsi_vmk: iscsivmk_ConnNetRegister: socket 0x41002347f910 network resource pool netsched.pools.persist.iscsi associated2013-05-16T16:08:39.495Z cpu0:2724)iscsi_vmk: iscsivmk_ConnNetRegister: socket 0x41002347f910 network tracker id 1 tracker.iSCSI.192.168.90.104 associated2013-05-16T16:08:39.495Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: vmhba37:CH:2 T:6 CN:0: iSCSI connection is being marked "OFFLINE" (Event:4)2013-05-16T16:08:39.495Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: Sess [ISID: TARGET: (null) TPGT: 0 TSIH: 0]2013-05-16T16:08:39.495Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: Conn [CID: 0 L: 192.168.90.52:51827 R: 192.168.90.100:3260]2013-05-16T16:08:39.496Z cpu0:2724)iscsi_vmk: iscsivmk_ConnNetRegister: socket 0x410023461d30 network resource pool netsched.pools.persist.iscsi associated2013-05-16T16:08:39.496Z cpu0:2724)iscsi_vmk: iscsivmk_ConnNetRegister: socket 0x410023461d30 network tracker id 1 tracker.iSCSI.192.168.90.104 associated2013-05-16T16:08:39.496Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: vmhba37:CH:3 T:6 CN:0: iSCSI connection is being marked "OFFLINE" (Event:4)2013-05-16T16:08:39.496Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: Sess [ISID: TARGET: (null) TPGT: 0 TSIH: 0]2013-05-16T16:08:39.496Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: Conn [CID: 0 L: 192.168.90.51:56110 R: 192.168.90.100:3260]2013-05-16T16:08:39.497Z cpu0:2724)iscsi_vmk: iscsivmk_ConnNetRegister: socket 0x41002cdc23b0 network resource pool netsched.pools.persist.iscsi associated2013-05-16T16:08:39.497Z cpu0:2724)iscsi_vmk: iscsivmk_ConnNetRegister: socket 0x41002cdc23b0 network tracker id 1 tracker.iSCSI.192.168.90.101 associated2013-05-16T16:08:39.497Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: vmhba37:CH:4 T:6 CN:0: iSCSI connection is being marked "OFFLINE" (Event:4)2013-05-16T16:08:39.497Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: Sess [ISID: TARGET: (null) TPGT: 0 TSIH: 0]2013-05-16T16:08:39.497Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: Conn [CID: 0 L: 192.168.90.53:57285 R: 192.168.90.100:3260]2013-05-16T16:08:39.498Z cpu0:2724)iscsi_vmk: iscsivmk_ConnNetRegister: socket 0x41002cdc2a50 network resource pool netsched.pools.persist.iscsi associated2013-05-16T16:08:39.498Z cpu0:2724)iscsi_vmk: iscsivmk_ConnNetRegister: socket 0x41002cdc2a50 network tracker id 1 tracker.iSCSI.192.168.90.102 associated2013-05-16T16:08:40.873Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_StartConnection: vmhba37:CH:2 T:6 CN:0: iSCSI connection is being marked "ONLINE"2013-05-16T16:08:40.873Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_StartConnection: Sess [ISID: 00023d000007 TARGET: iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f TPGT: 1 TSIH: 0]2013-05-16T16:08:40.873Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_StartConnection: Conn [CID: 0 L: 192.168.90.52:62320 R: 192.168.90.104:3260]2013-05-16T16:08:40.874Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_StartConnection: vmhba37:CH:0 T:6 CN:0: iSCSI connection is being marked "ONLINE"2013-05-16T16:08:40.874Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_StartConnection: Sess [ISID: 00023d000005 TARGET: iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f TPGT: 1 TSIH: 0]2013-05-16T16:08:40.874Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_StartConnection: Conn [CID: 0 L: 192.168.90.50:56018 R: 192.168.90.104:3260]2013-05-16T16:08:40.875Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_StartConnection: vmhba37:CH:3 T:6 CN:0: iSCSI connection is being marked "ONLINE"2013-05-16T16:08:40.875Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_StartConnection: Sess [ISID: 00023d000006 TARGET: iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f TPGT: 1 TSIH: 0]2013-05-16T16:08:40.875Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_StartConnection: Conn [CID: 0 L: 192.168.90.51:55351 R: 192.168.90.101:3260]2013-05-16T16:08:40.876Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_StartConnection: vmhba37:CH:4 T:6 CN:0: iSCSI connection is being marked "ONLINE"2013-05-16T16:08:40.876Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_StartConnection: Sess [ISID: 00023d010008 TARGET: iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f TPGT: 1 TSIH: 0]2013-05-16T16:08:40.876Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_StartConnection: Conn [CID: 0 L: 192.168.90.53:60923 R: 192.168.90.102:3260]2013-05-16T16:08:40.963Z cpu6:3533)ScsiScan: 1098: Path 'vmhba37:C0:T6:L0': Vendor: 'EQLOGIC ' Model: '100E-00 ' Rev: '5.2 '2013-05-16T16:08:40.963Z cpu6:3533)ScsiScan: 1101: Path 'vmhba37:C0:T6:L0': Type: 0x0, ANSI rev: 5, TPGS: 1 (implicit only)2013-05-16T16:08:40.964Z cpu6:3533)ScsiScan: 1582: Add path: vmhba37:C0:T6:L02013-05-16T16:08:40.964Z cpu6:3533)ScsiScan: 1098: Path 'vmhba37:C2:T6:L0': Vendor: 'EQLOGIC ' Model: '100E-00 ' Rev: '5.2 '2013-05-16T16:08:40.964Z cpu6:3533)ScsiScan: 1101: Path 'vmhba37:C2:T6:L0': Type: 0x0, ANSI rev: 5, TPGS: 1 (implicit only)2013-05-16T16:08:40.965Z cpu6:3533)ScsiScan: 1582: Add path: vmhba37:C2:T6:L02013-05-16T16:08:40.965Z cpu6:3533)ScsiScan: 1098: Path 'vmhba37:C3:T6:L0': Vendor: 'EQLOGIC ' Model: '100E-00 ' Rev: '5.2 '2013-05-16T16:08:40.965Z cpu6:3533)ScsiScan: 1101: Path 'vmhba37:C3:T6:L0': Type: 0x0, ANSI rev: 5, TPGS: 1 (implicit only)2013-05-16T16:08:40.965Z cpu6:3533)ScsiScan: 1582: Add path: vmhba37:C3:T6:L02013-05-16T16:08:40.966Z cpu6:3533)ScsiScan: 1098: Path 'vmhba37:C4:T6:L0': Vendor: 'EQLOGIC ' Model: '100E-00 ' Rev: '5.2 '2013-05-16T16:08:40.966Z cpu6:3533)ScsiScan: 1101: Path 'vmhba37:C4:T6:L0': Type: 0x0, ANSI rev: 5, TPGS: 1 (implicit only)2013-05-16T16:08:40.967Z cpu6:3533)ScsiScan: 1582: Add path: vmhba37:C4:T6:L02013-05-16T16:08:40.967Z cpu1:3533)ScsiPath: 4541: Plugin 'NMP' claimed path 'vmhba37:C4:T6:L0'2013-05-16T16:08:40.967Z cpu1:3533)ScsiPath: 4541: Plugin 'NMP' claimed path 'vmhba37:C3:T6:L0'2013-05-16T16:08:40.967Z cpu1:3533)ScsiPath: 4541: Plugin 'NMP' claimed path 'vmhba37:C2:T6:L0'2013-05-16T16:08:40.967Z cpu1:3533)ScsiPath: 4541: Plugin 'NMP' claimed path 'vmhba37:C0:T6:L0'2013-05-16T16:08:41.063Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: vmhba37:CH:1 T:6 CN:0: Failed to receive data: Connection closed by peer2013-05-16T16:08:41.063Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: Sess [ISID: 00023d000008 TARGET: iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f TPGT: 1 TSIH: 0]2013-05-16T16:08:41.063Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_ConnReceiveAtomic: Conn [CID: 0 L: 192.168.90.53:56744 R: 192.168.90.103:3260]2013-05-16T16:08:41.063Z cpu0:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: vmhba37:CH:1 T:6 CN:0: Connection rx notifying failure: Failed to Receive. State=Online2013-05-16T16:08:41.063Z cpu0:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: Sess [ISID: 00023d000008 TARGET: iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f TPGT: 1 TSIH: 0]2013-05-16T16:08:41.063Z cpu0:2724)iscsi_vmk: iscsivmk_ConnRxNotifyFailure: Conn [CID: 0 L: 192.168.90.53:56744 R: 192.168.90.103:3260]2013-05-16T16:08:41.063Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: vmhba37:CH:1 T:6 CN:0: iSCSI connection is being marked "OFFLINE" (Event:6)2013-05-16T16:08:41.063Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: Sess [ISID: 00023d000008 TARGET: iqn.2001-05.com.equallogic:4-52aed6-56c15d168-d6c0021a85c4f71c-eql-esxi-vol-f TPGT: 1 TSIH: 0]2013-05-16T16:08:41.063Z cpu0:2724)WARNING: iscsi_vmk: iscsivmk_StopConnection: Conn [CID: 0 L: 192.168.90.53:56744 R: 192.168.90.103:3260]2013-05-16T16:08:41.063Z cpu12:2701)WARNING: NMP: nmp_DeviceRequestFastDeviceProbe:237:NMP device "naa.64ed2a85165dc1561cf7c4851a02c0d6" state in doubt; requested fast path state update...2013-05-16T16:08:41.063Z cpu12:2701)ScsiDeviceIO: 2309: Cmd(0x412441465980) 0x28, CmdSN 0x800000fd from world 4863 to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" failed H:0x2 D:0x0 P:0x0 Possible sense data: 0x0 0x0 0x0.2013-05-16T16:08:41.063Z cpu12:2701)ScsiDeviceIO: 2309: Cmd(0x41244037cbc0) 0x28, CmdSN 0x80000080 from world 4863 to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" failed H:0x2 D:0x0 P:0x0 Possible sense data: 0x0 0x0 0x0.2013-05-16T16:08:41.092Z cpu12:2060)ScsiDeviceIO: 2309: Cmd(0x412441bb3300) 0x28, CmdSN 0x8000002e from world 4863 to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" failed H:0x2 D:0x0 P:0x0 Possible sense data: 0x0 0x0 0x0.2013-05-16T16:08:41.092Z cpu12:2060)NMP: nmp_ThrottleLogForDevice:2318: Cmd 0x28 (0x412441baeec0, 4863) to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" on path "vmhba37:C1:T6:L0" Failed: H:0x2 D:0x0 P:0x0 Possible sense data: 0x5 0x24 0x0. Act:EVAL2013-05-16T16:08:41.092Z cpu12:2060)ScsiDeviceIO: 2309: Cmd(0x412441baeec0) 0x28, CmdSN 0x80000059 from world 4863 to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" failed H:0x2 D:0x0 P:0x0 Possible sense data: 0x5 0x24 0x0.2013-05-16T16:08:41.146Z cpu13:5262)ScsiDeviceIO: 2309: Cmd(0x412441834100) 0x28, CmdSN 0x80000040 from world 4863 to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" failed H:0x2 D:0x0 P:0x0 Possible sense data: 0x0 0x0 0x0.2013-05-16T16:08:41.170Z cpu12:2060)ScsiDeviceIO: 2309: Cmd(0x4124403a6c80) 0x28, CmdSN 0x8000006a from world 4863 to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" failed H:0x2 D:0x0 P:0x0 Possible sense data: 0x0 0x0 0x0.2013-05-16T16:08:41.200Z cpu8:2056)ScsiDeviceIO: 2309: Cmd(0x41244037b5c0) 0x28, CmdSN 0x800000c9 from world 4863 to dev "naa.64ed2a85165dc1561cf7c4851a02c0d6" failed H:0x2 D:0x0 P:0x0 Possible sense data: 0x2 0x3a 0x1.2013-05-16T16:08:41.218Z cpu11:2088)WARNING: dell_psp_eql_routed: psp_eqlUpdatePathSelection:1014:Path is reported as inactive (0x50475304)2013-05-16T16:08:41.233Z cpu2:2201)WARNING: dell_psp_eql_routed: psp_eqlUpdatePathSelection:1014:Path is reported as inactive (0x50475304)2013-05-16T16:08:42.072Z cpu7:2209)ScsiPath: 4963: DeletePath : adapter=vmhba37, channel=1, target=6, lun=02013-05-16T16:08:42.074Z cpu15:2063)WARNING: NMP: nmp_DeviceStartLoop:721:NMP Device "naa.64ed2a85165dc1561cf7c4851a02c0d6" is blocked. Not starting I/O from device.2013-05-16T16:08:42.074Z cpu13:2061)WARNING: NMP: nmp_DeviceStartLoop:721:NMP Device "naa.64ed2a85165dc1561cf7c4851a02c0d6" is blocked. Not starting I/O from device.2013-05-16T16:08:42.074Z cpu7:2209)WARNING: ScsiPath: 5022: Remove path: vmhba37:C1:T6:L0
    
    Thanks for any information you can provide.
    

    When a connection is moved either by the table for IO balancing through interfaces available on the battery, page movement when you have more than three members in a pool, or with installed MEM it will periodically move connections, you will see redundancy lost messages.  As you have noted, at the time wherever you check paths, that connection has already connected as it should.   For this shorter periods, less than a second in general, this session is gone and again one is created at the same time.  The volume is always accessible via the other sessions.   Therefore, a message of info, not an indication of a problem.  When the table of balances of the slices for a new Member in the pools only three, expect to see many, simulaneous messages from all hosts to connect to the data store.  This whirlpool is quite normal.

  • Offer by guasto componente PowerEdge R710 [MS]

    Buongiorno,

    Ho Server UN PowerEdge R710 (Service Tag = ) stamattina mi è questo allert love Dove,.

    Event: System Board PS redundancy: PS redundancy to system board sensor, redundancy lost said
    Date/time: Friday, April 15, 2016 01:31:08
    Severity: critical
    Model: PowerEdge R710
    Service etiquette: DQV705J
    BIOS version: 6.4.0

    MI sono is alla remote console e ho trovato a "Build redundancy power" error e lo del PS2 e status in error, come che if ditch rotto.

    A tal purpose I wanted to get one offer per questo componente rotto (senza intervento del tecnico, visto che lo sostituiremo noi).

    Buongiorno,

    Con passing it mouse sopra identifier c Supporto Dell'e the voce "private message", it could mandarmi come message privato di seguito required information?

    -Service tag del Server

    By the spedizione (intervento o):

    1. company name:

    2 address:

    3 City:

    4 Provincia:

    5 cap:

    6 name/last name/number phone/e-mail del referent in loco:

    With the fatturazione

    1 nome società (o codice client o number order recent):

    Address 2:

    3 City:

    4 Provincia:

    Heading 5:

    Name/last name/number 6 telephone/e-mail del referent by the fatturazione:

    7 partita IVA:

    Speaking saluti

    Manual

  • Problem of fans

    Hello, I need help, I have dell R710 server, and I have the following error, redundancy Lost Fan. check the Fans

    all fans spin normally and replaced it and I always two errors.

    the first: Fans exceeding 1 RPM range. check

    the second: redundancy lost fan. Check fans

  • The M1000e CMC redundancy is lost, all new case

    I have a brand new box running firmware 5.11. The primary CMC works, but has a number of questions

    -connections at least two DRACS M630 show as expire

    -connection to the secondary CMC shows that "redundancy is lost.

    It seems that the internal communication to the enclosure has failed.

    I tried to restart the CMC, is there anything else I can do? for example the reinstallation of the CMC would be a good idea? The blades are 160KM away from me, so I have to tell someone else what to do. The speaker is not yet in production.

    DRAC - problem came from firewall question - CMC was related to a switch problem

  • vcops to monitor the storage lost path redundancy

    Vcenter, I'd have an alarm for called host

    'More redundancy of storage path'

    I'm moving all of these functions to vcops

    I tried to create a KPI KEY HT for this, and I can't find this setting.

    In addition, I wanted to create a heat map that I can see if all connections

    are broken and can not find this attribute type.

    Anyone know how to integrate this into vcops?

    You won't have a HT or KPI for it - it's a fault. This flaw is already a heavy weight against the health score for the host system resources. You cannot make a heatmap specific defects, but you can make a heatmap of the host systems and view the badge | Score of fault, which will include your flaws. Then maybe have an Alert widget, so that when you click on the host system in the heatmap, interaction will spend this resource in the alert widget, with the defined alert widget to display only the defects... and there are go.

  • Lost network redundancy!

    Normally, when die NIC 1, we have netword redundancy. But this time, time 2 die of network card in a standard switch in a 5.1 ESXi host-> that is why, many network down-> affect to multiple virtual machines. There is only avaible network management yet.

    Is there anyone to deal with this problem? Help us...

    Thank you!

    If it is urgent and machines production is declining, please contact VMware Support.

    If its not urgent please let us know more details about what happened, what kind of configuration it is, etc. error messages.

    Linjo