Phaser in LabVIEW for voltage and current indicator

When I read a research paper on the power system, I've seen has a reasearcher program LabVIEW (its block diagram is not shared just GUI). My question is: is-LabVIEW has a built-in function that allows to display the amount of complex in | Mag |

Greetings muahang1234

There is a suite for LabVIEW called Suite of electrical power OR LabVIEW that might interest you. Visit ni.com and evaluate the software, it may be the tool you're looking for!

Let us know how it goes. Nice day.

Tags: NI Software

Similar Questions

  • Variables for voltage and current on each component (for use in graphically the diagram)

    Hello

    I have a very simple circuit containing only a source of AC voltage and resistance of two series.

    I want to draw the voltage of the source and each resistance. I can't find any variable involves pre right now, I know I und came to the value of the resistance.

    for example

    UR1 = I * r1

    USource = I *(r1+r2)

    It's pretty boring... especially because that put in square brackets does not work.

    probably the cause variables containing itselfes media.

    hope you have an idea

    THX

    Hello

    The way that you have set in place now of things is correct. Multisim, as well as most of other circuit simulators, monitors the node voltages, no voltage drops. When you draw your diagram, Multisim assigns numeric node names to each node. That's why you see v(1) and v(2) and not something like V (R2). To find the voltage drop in R2, you will need to calculate V (2) v (1). To know the name of each of your nodes (also called threads), simply do the following:

    1. Click Options > properties sheet
    2. For option Net names, select Show all
    3. Click OK

    To make it easier for you, you can name a few nets to something that is easier to read. You can do this:

    1. Double-click on the net you want to rename (the net is the wire you drew connecting elements)
    2. Enter your name, preferred net in the space provided
    3. Click OK

    Hope that answered some of your questions.

  • Define independent for rpm and current control

    Hello

    I need assistance with labview. I am able the current, voltage and rpm of a pump connected to a control box. The control box is also connected to my DAQ. My requirement is that I would like to monitor the blood and fluctuations in current on an in labview waveform chart, once I run the file vi and monitor the number of laps when I start the pump. When I try to run the file vi before the pump starts, I get an error code "200284. I understand that the RPM in my vi counter does not receive signals and ends the program. How to set a control sparate for the display of the voltage and current regardless of whether if the pump is started or not? or how to set a control to monitor RPM display only when the pump is started and does not affect the voltage and current display part of the VI.

    This may seem a bit complicated! Please give me your suggestions on how to do this!

    Thank you

    Rajesh

    Looking at your code, the DAQ Assistant on the background is taking in the RPM data you are looking for. You can do a right click on the arrow to the left of the option "timeout (s)" at the bottom of the DAQ Assistant ExpressVI and select Create > Constant. This will create a constant within seconds that represents the DAQ Assistant time-out on entry. You can base the number on how long it will take the number of LAPS to enter to start.

    .

    It should look like the above, but you can change the time that the ExpressVI will wait for your needs.

  • calculate the symmetrical components of voltage and current

    Hi all. I work on the calculation of symmetrical components of voltage and current in Labview. I have included the relationship between the symmetrical components and sequence as photo 1 voltage. I'm going to use this calculation for several times, so I wonder if anyone has some ideas far better bc I wired just so much together to realize the expression. It seems aweful. Any suggestion? as built-in function to achieve this function? Thank you

    Let's take a look on your form (you don't say what is complex, etc, so modify as needed)

    For example, here is how you create the matrix A to an alpha given.

    Similarly, you can create A ^(-1) matrix (your definition of A and A ^(-1) seem incompatible, otherwise you could just pick matrix inverse of A). After that, you can multiply with you V123 vector using AxB.

  • How to display the voltage and current of synchronously

    Recently, doing a project on the acquizeing voltage and current synchronouly, then display. the design is welding a resistor(1%) 0.5 ohm in NI 6251 entered analog of her HAVE differential, then acquired the differential voltage at the input to convert current. At the same time, I hope to recover the path of analog input voltage. My problem is that the current profile data. Please help me .the program screenshot is show below. ---1. Perhaps you ask why not use no. - a way to get voltage at all port of AI, then in the use of the software less to get a voltage inputs HAVE. in this way, my problem is solved. I try, but the current accuracy is failure. because my current range expect is 1uA ~ 100mA. precision current samll won't be promised if you use simple ways for granted NOR 6251 voltage. NEITHER 6251 device spec (HAVE an absolute precision) (v) nominal range sensitivity absolute Accuracy (uV) 10 1920 112 5 1010 56 2 410 22.8 74 0.2 6.4 0.1 52 6.0 (I want to use this range to measure current samll) - cordially Shawnh.Chen

    shawn1 wrote:
    1. how show the waveform by accumulating 1 d data table, rather than showing all 100 acquisition

    Use a waveform graph.  Graphics keep history, you do not have to accumulate the data.  He does it for you on the screen.

    shawn1 wrote:
    2. What is the minimum unit of identification of the TSC103IPT amplifier? I doubt that the 0.5uA can be identified? (0.5uV = 0.5 ohm * 1uA) Because I can't find anything on the auccary in TSC101IPT datasheet.

    The amplifier is analog.  Thus, he can win anything.  But you should really think about a higher resistance if you really want to measure this small of a current.

  • Chroma DC power supply RS232 communication (read problem of over-voltage and current)

    Dear all.

    I chroma programmable DC power. Based on the programming of the Instrument manual I develop using RS232 communication. Based on the program I can set the voltage, current, over-current protection, protection against overvoltages and make IT / OFF out put supply perfectly.

    But I have to read the measured values of the output power as current and voltage. Measured applications are the voltage and current of the output of the power supply. My problem is two of them read at the same time. Currently, the reading is only voaltge or current (if the first request is v? it is voltage read out but no reading for the current) and if the first request is CURR? the reading for the current, but not for VOLT? The status message is OK, even if it is to read values.

    Thanks in advance

    What I see in your program, it's that you do not use the stop for reading character. For your writing, you do the hard with all these concantanate string functions. You can set the stop character for all entries with a node unique propert - "ASRL end Out.

  • scanning voltage and current measurement for Keithley 2400

    Dear all

    Hello

    can someone help me?

    Despite days nearlly10 I am option to find any program LabVIEW 2010 for sweeping the voltage and measure current who works with RS-232, I have a end not have nothing exept examples read single and multiple data. I tried to SmartData labview and changed a few prorgram gpib to RS - 232, but I couldn't.

    In another attempt to find a good VI "votltage scanning and current measurement" that work with RS-232 in labview 5.1.1. I have converted in 2008, but it takes old driver (ke24xx.dll) and do not work in my labview 2010 and I could ' t find older driver.

    My thesis project was halted in those 10 days, and I couldn't do anything for our keithley.

    Please helpe...

    in the following, I have attached these files:

    1.-first, what voltage scan that works with GPIB

    2 - Vi that I change the gpib for visa (rs232) port that I don't know why it doesn't work.

    3. it is Vi related to the "sweeping and current measurement votltage" that works with the RS-232, but it takes old dirver so I can't use it.

    4-slot-VI necessary for the implementation of program 3 (but there is no driver for these subVIs) was attached to the reply message of this post

    If any body has this program ("scan votltage and current measurement" running rs - 232) please send to me

    Thanks in advance.

    None of you attached the screws are the driver OR you spoke. There is no conversion required for this driver.

  • 6009OEM output voltage and current

    Hi all

    Just try to make sense:

    http://www.NI.com/PDF/products/us/20043762301101dlr.PDF

    Page 3 says: high output voltage (push - pull, I = - 8.5 my) = minimum voltage 2.0 v maximum voltage = 3.5V but where can I find out what current can it provide and continue to produce an output voltage more than 4.2V?  (4, 2V is the worst case for the high threshold of logic of a chip, I want to control).

    Thank you!

    J

    Hello J,

    As you mentioned is the maximum voltage of 3.5V when you have a high output voltage (push - pull, I = - 8.5 my). If you need more than 3.5V then you might need to change to an open-drain output. As you can see from the link you provided that you would receive a maximum voltage of 5V.

    If you do not use an open-drain output you have to combine with a pull up resistor.

    I hope this helps.

  • my project is to measure the voltage and current by using the view of laboratory.

    Dear Sirs,

    I have a project to measure parameters electric ac current, voltage, power factor etc through aquisitioin of data with labview. Can I do this? If yes then kindly help me with some opinions and ideas. I'll be very grateful to you.

    Muhammad Azam Hanan.

    Student of the University of engineering and Technolgy, Lahore, Pakistan.


  • Venue Pro 8: use the charger with a little more voltage and current?

    I just bought a Dell came Pro 8 tablet used running Windows 8.1. The seller didn't have the original charger, so he gave me a 12W of Apple loader that had taken out nominal 5.2V and 2. 4A

    Is it okay to use this charger for my Tablet? Any potential problems in the long term?

    Thank you!

    I'm sure that the voltage is OK to 99.9%.  The extent of the current note goes, which is often misunderstood.  The rated current for a charger power or power is the maximum that the charger/power is able to provide. It could be evaluated to a zillion amps, but the equipment to which it will draw only what it requires.

  • data acquisition in line voltage and current signals

    What is the name and model of the instrument OR measure the 220V 3-phase, 5 signals? Also, what will be the approximate cost of this equipment (s)?

    Hello Yasink,

    Looks like you could do reference the entry Module current 5A with insulation of 250Vrms, NI 9227.

    Can you provide more information on the app you want? From there I was able to provide a better recommendation.

  • How to measure high voltage (60-70 v) and current (75-80 a) using a DAQ PCI or USB DAQ

    Hello

    I work with a system that works on about 5kW. The output of the system voltage can go maximum up to 60-70 v and thus the corresponding current around 75-80 a. I have 10 these systems that I want to read one by one continuously for long periods.

    I am designing the automated system best suited for this and looking for the best material that would be appropriate for this purpose. Looking for options, I found that an SCC - A10 attenuator may be used to get the tension down by a factor of 10. But I'm confused, if the high current will pose a problem and also how to measure this high current.

    I need to measure the voltage and current at the same time. Please suggest what would be the most appropriate fitting for the same (preferably PCI or USB)

    The hope of a quick response. Thanks and greetings

    Reena Sharma

    Facilitated learning

    Reena says:

    Hi all

    There is good news that the idea of using a compact data acquisition has been accepted by the authorities of the society. I'll be very grateful, if you could suggest me with some hardware modules suitable for my application and how I can use them best.

    Thank you very much

    Reena

    I was able to make a few suggestions, but do not have the time to understand your needs and the forums are not the best solution.

    Your Local OR representitive actully gets paid to do this kind of thing.  a google search suggests THAT LME is in Pasadena. Zack Collins would be the contact rep

  • Which is better: Labview for everyone or learning with Labview?

    I am a novice user of Labview, but I went through essentially through the 6 hours on Web site tutorial for NOR and that I'm currently going through the massive list of examples included in Labview. I heard the two Labview for everyone and learning with Labview recommended texts. I'd rather pay one, unless I really should bring both eventually. Thoughts and opinions by comparing the two?

    The two books are very good.  If your just starting, go to Amazon, buy a copy used learning with LabView 8 or 9.  I got mine for $18 shipped.  You can download all the vi.  Can also buy LabView for everyone $61.  LabView for everyone covers almost everything on LabView and brings you to some more advanced things, but learning with LabView has been better for basic stuff.

    Jerry

  • In Labview 8.6 and MAX, I can change a scale for a voltage read the string in a task once the application has been built and installed.

    In Labview 8.6 and MAX, I can change a scale for a voltage read the string in a task once the application has been built and installed on a second PC. Where's the info of the scale which is held?

    Hello

    Once you have built your VI and compiled into an executable file and deployed on another machine, it essentially becomes a file read-only, which means that you will not be able to change the balance in this deployed application.

    Kind regards

    Marcus

  • LabVIEW for control unlimited, a camera and a light meter (Minolta T - 10A)

    Hello world

    I'm totally new in the use of data acquisition software, but I found out, I use LabView for continuous measures (intervals of 15 min for 1 month or maybe more), the thing is that I need to get pictures simoultanously (Canon camera EOS) and illumination (in lux) device: Minolta T-10 a vision series T-10MA. My question is what software LabVIEW do I need to buy (or my institution actually) in order to get this. I look at the options of LabVIEW software and cannot understand what is needed. Subsequently, I guess that I need controllers for each of the devices (minolta and canon). Can you please tell me if this is possible and how to do it. I would really appreciate it.

    Steph.

    The following items are required: LabVIEW full, all drivers of devices (including DAQmx and pilots of the Vision) and the Acquisition of Vision software package.

    The Minolta luxometer has a connector for a PC and some communication software (which I did not inspect) which, I suppose, would allow you to take readings.  There is a comment about current if the USB cable is connected - I don't check if there is a power connector on the luxometer (since you will need to leave it plugged in for a month, the same problem with the camera).  As far as the camera is concerned, I don't know if it is controlled from a PC - my experience has been with (the size of 640 x 480 pixels) video cameras, which are probably controlled by LabVIEW.

    As for simultaneous readings, it is something that LabVIEW did pretty well.  I advise you to consult a professional if it's anything other than a school project, maybe even hire someone to work a few week of.

    Bob Schor

Maybe you are looking for

  • Satellite L500D-164 - black screen

    When I start to start my Satellite L500D 164, fan works but screen remains black. Cannot start Bios.no Desktop on external screen as well.please advise.thank, you

  • Noise thermocouple with PCI-6230

    What level of noise should be expected for a K type thermocouple used with an acquisition of data PCI-6230 and a map derivation CB-37F-HVD? I read the data with LabVIEW and Daq Assist module on the setting of the thermocouple and the noise see of +/-

  • Slate 6 manual error update of KitKat

    I downloaded the 4.4.2 update on the HP website, followed the instructions to copy it onto a SD card, etc and I tried to install it. I got the following error message: -Install /sdcard...Finding update package...Open the update package...Update("WARN

  • Dependence of the Lenovo 1.2.0.21 settings package does not install correctly

    Lenovo system update offered an update package dependencies of parameters. After installation and reboot, I got a pop up telling me that 'C:\Program' is not found. What's happened is that Setup you forgot the quotes in a registry entry: PWMTRV had a

  • No power VAIO laptop

    My VPCEB23FX shows no light power and will not power. The adapter works with green LED