I use an entrance Module differential differential NI9411 under cRIO-9074 with scan Mode, but I noticed that some problems are present.

My application needs two encoder and we choose two incremental encoders with 1024pulses/rev. I have configured the NI9411 quadrature Mode, so I can read the position and speed of the encoder. Each shaft turn at different speeds.

One of them can turn 4.6 rad/s as a maximum speed, while the other hit it up to 402 rad/s. Then, the configuration of the module input filter is set to 1microsed, the time base speed 32768 microseconds and the disabled index mode. These values make for a correct reading? The cRIO scanning speed is set to 1ms.

On the other hand, watching the tutorials or (http://zone.ni.com/devzone/eda/tut/p/id/7109), that the degree of rotation depends on the encoding type, what type of encoding is used in Scan Mode? X 4?

Using System Manager OR distributed, one of the encoders to read impulses sometimes sporadic (up to 2 digits) Although the encoder is stopped. However, the other bed is always 0. It seems that the encoder is broken, isn´t it?

Thanks in advance for your comments

Hi Juancar,

I think that the values are suitable. The issue of reading 0 is explained in this KB:

http://digital.NI.com/public.nsf/allkb/C9088DFDF803CD8B862575F3007C40FD?OpenDocument

In addition, according to this document:

http://zone.NI.com/DevZone/CDA/tut/p/ID/7338

decoding type must be set to X 4.

I hope this helps! Suerte con ello.

Jesus

Tags: NI Software

Similar Questions

  • RT: fault 9512 module when you use the hybrid mode

    Hello, I have a problem with my configuration of hyrbid cRIO. I am currently using Labview 2010, cRIO-9074, x 1 NI 9234, and NI 9512 3 x.

    Summary:

    What you trying to accomplish?

    -J' built two screws, one who acquires the data of a NI 9234. This vi is one that uses the FPGA due to 51.2 kHz sampling frequency needs. The other is to playback motion and three NI 9512 s (scan mode) encoder. Both work fine separately (on the same FPGA bitfile), but when I copy and paste the VI for the NI 9234 in VI for the 3 9512 x s and click Run, the fault of motors.

    What are the steps needed to reproduce the problems?
    Click on execute in the joint (prepared program_2VItesting.vi).

    What measures, if any, you have taken to solve all the problems and the results of your attempts
    -J' have confirmed that if I turn the two screws separately, they work fine. The first time I combine work 9512 s for a second (i.e. the engines a bit) on the two screws. Then he cracks. I then used the distribution manager to clear the fault and run it again (note: there is no error code, I just erase the Red led on the module by changing the configuration mode and active mode). Every time the first time the engines do not move at all.

    -J' have confirmed that I have properly configure this kB from hybrid mode:
    http://digital.NI.com/public.nsf/allkb/0DB7FEF37C26AF85862575C400531690

    I have attached the vi of two combined screw (prepare program_2VITesting.vi) together. Half upper is program FPGA copied and pasted (as noted by the reference open VI) and the bottom is the scan mode (as noted by the timed loop). I've also attached the separate screw (program prepared and JustDAQ) that can also work well now by pressing justing run.

    Am I missing something simple here right?

    Thank you

    Troy

    So it turns out that you just put the cRIO in Setup mode when you set up your open your ref FPGA and reset. Then change to the active mode (any program) before you do anything else in your program (i.e. the very very beginner). A picture is attached.

    -Troy

  • I use Photoshop CC and I have problems to use the scanning feature PLC culture and the strraigten.  Other printing features work within the progrram, but no connection when I use don't automate.

    Am I missing a configuration of PLC to allow me to crop and scan several photos?

    With the help of 8.1 with canon MX340 wireless and final version of Photoshop CC.

    Help.

    [email protected]

    VIC

    I plugged a usb cable and I was able to use the WIA import feature and

    the menu of the controller,

    He gave me the opportunity to select the printer and scan using the automaton

    function.

    When I removed the cable, it would not recognize the printer scanner in the

    Wireless mode.

    I tried to restart the system, no luck.

    In fact, when the cable is removed, the function to automate is

    "grayed out" which would explain why it cannot find the scanner.

    Any ideas?

    VIC Ouellette

    K1CGI... QRZ?

    In a message dated 12/09/2015 11:41:18 eastern standard time,

    [email protected] wrote:

    You talked

    by [email protected]

    (https://forums.adobe.com/people/[email protected]?et=notification.mention//forums.adobe.com/people/ [email protected]? and = notification.mention) in Re: I use Photoshop CC and I

    problems to use the scanning feature strraigten and the cultures of the automaton. Another impression

    features work within the progrram, but no connection when I use don't automate.

    in Adobe Community - view [email protected]of reference for you

    (https://forums.adobe.com/message/8274458?et=notification.mention#8274458)

  • Disabled IPad can be reset using the recovery mode

    Someone with a good it knowledge doctored iPad without permission and now it can be reset using the recovery mode. While that plugged into iTunes, software downloads, iPad, then displays the Apple symbol but then returns the message "iPad is disabled connect to iTunes".

    Hi stephen158,

    I understand that, in the process of restoration of an iPad in recovery mode, your iPad rebooted and returns to the screen "connect to iTunes". This can occur if the software download takes longer than 15 minutes, how the iPad will exit Recovery mode and the software will continue to download. In this case, you should be able to put the iPad in recovery mode and choose to restore the device when prompted.

    1. Connect your device to your computer and open iTunes. If you don't have a computer, borrow one from a friend or go to an Apple Store or service provider authorized Apple for help.
    2. When your device is connected, force restart it: press and hold the sleep/wake and home for at least 10 seconds, and only release when you see the Apple logo. Keep until you see the screen in recovery mode now.
    3. When you see the option restore or update, choose update. iTunes will try to reinstall iOS without erasing your data. Please wait while iTunes downloaded the software for your device.
      If the download takes more than 15 minutes the device out of recovery mode, you must repeat these steps and choose restore instead of update when you return to this step.
    4. After the update or restore is complete, configure your device. If you have backed up your device with iTunes or iCloud and you need to restore your device in step 3, you may be able to restore from your backup during installation.

    If you are unable to update or restore your iPhone, iPad or iPod touch
    https://support.Apple.com/en-us/HT201263

    See you soon!

  • OfficeJet J4660 all-in-One on Windows Server 2003 R2 - cannot use the scan and fax functionality

    Hello everyone,

    I recently purchased the Officejet J4660 AIO.  I had to install on our Windows Server 2003 R2 (with all latest updates), being present on the CD of driver for Win XP, I had to download the latest driver (OJJ4600_Corporate_ENU_10 - 55.8 MB) from the HP site.  During installation, ONLY the printer driver has been installed.  I can't use the SCAN function or the FAX software.  In fact, the icons for these two programs not created in the HP program group.  No error message appeared well while installing.

    All the world was a program similar and been able to get a work around for this?  I would like to use AIO printer that I bought, not only on the side of impression of it.

    Any help will be much appreciated.

    Thank you.

    Salim

    I think that the Acquisition of Image Windows (WIA) service is disabled in your system. Unlike Windows XP or Vista, in most Windows Server systems, this service is disabled by default. You can activate it in this way:

    1. right click on my computer and select manage.

    2. Select "Applications and Services-> Services";

    3. find Windows Image Acquisition (WIA), right click and select Properties.

    4. Select "auto" in the "Startup Type" list box in the "Général" tab

    5. in the situation 'Services', click 'start '.

  • Photosmart B209a can you overried printer function? use the scan only?

    I have the Photosmart Plus B209a model installed print head is not intended for this printer, or is damaged. Refer to the Doc of the printer. Now, I have done this and cleaned ect. So, assuming that is damaged. I called to get this part and OMG! I might as well buy a new one! $85.00 and I did. My question is can I substitute the information of the printer and use the scan function again?   Thanks for any help!  Michael

    Unfortunately, you can not.  If the printer is in an error state, it locks you out of all the other functions of the printer.  I'm sorry.

  • After mac os update and software reinstall now unable to use the scan function

    Hello

    I never thought I had to post on one of them, but it really made me. I have a Macbook and stupidly thought that I would update to the mavericks os 10.9 the other day.

    I continued to be able to print once the update, but it was impossible to use the scan function. So, I removed the printer and the drivers and downloaded the new drivers which would have been compatible with os x 10.9. When I went to reinstall the printer, he couldn't locate it on the list of "available printers" - I connect using wi - fi connection at home.

    The only way I could connect the printer was installed manually by entering the ip address. It was found and I print now, so I don't think there is nothing wrong with the connectivity, but a warning when you do this that says scan function does not work, and of course the scan option is simply not there.

    Thought I have would bypass this using analysis of e-mail on the printer. It seemed to work fine, but when I received the email there was no attachment.

    My husband is now scanning these documents to his computer (a pc) and emailing for me - is not ideal.

    Any ideas on how I can fix this?

    Thank you

    Annie

    Hi Annie,.

    Here is a picture of a printer, USB cable,

    Now that I know what printer we work with, I have another idea. On the front screen of the printer please press the wireless icon. There are 4 icons in the upper part, the wireless is the second from the left. In the Menu arrow until settings wireless advanced. I would like to disable IPV6, arrow down to IPV6, and then select OFF.

    I saw the IPV6 interferes with the Hello Protocol several times, often time turning off this feature will solve the problem and allow the Mac to see the printer on the network. Once IPV6 is disabled try to add the printer again.

    Please let me know if this solves the problem, I am eager to see this solved and you get printing and scanning of your own computer.

  • Using the blending modes

    I provide 2 images and stack them in layers.  Can I use the blending modes (lighten, screen, overlay, etc.) to make a picture. If I want to paint the rear part of the image that I lost in through mask preparation, normal brush no longer works. I even tried to change normanl brush in some mixture that I used at the time with no joy. Help

    You say that you want to display the top layer, as it originally was before the blending mode has been applied?  To do that you would need a dupe layer, then mask in the areas you want to "restore".

  • Module NI 9214 and cRIO, where is the example for the scan Mode

    Hello

    I'm new to programming of cRIO. I'll use a cRIO 9022 with different modules, such as 9214, Labview 2010.

    However, when I go to the examples, I can't load the get started scan for 9214 module Mode, it says that I have to reinstall. I don't know what examples are not installed, as I reinstalled my software already once and I could not find any change. Anyong can tell me where I can find this example, so I'll try to find more easily the example and install it.

    Thank you very much

    See you soon,.

    Antonio

    Hi Antonio,.

    I recorded the example mentioned to be compatible with 10.0 using the function 'Save for the previous version' of LabVIEW and attached the new document below. Please let me know if it works.

    The course will be very useful if you want to use it much in the future. Real time quotes are most relevant to develop on CompactRIO and the FPGA course will be very useful if you plan to use the FPGA in your applications. Do you have a course of training before sitting?

    Thank you

  • You try to run the scan mode and mode interface fpga at the same time is causing errors

    I'm reading a 9236 9237 and a 9215 with the scanning engine and read from two 9211 modules with the fpga. It's because I need to acquire to 200 Hz with the 9236 9237 9215 but maximum rate of the scan engine is limited by the slower module in the system, which in this case is the max of 15 hz the 9211.

    So to use both interfaces (scan engine and fpga), I followed the percisely given in this article for instructions.

    1. the project has created and added the peripheral crio using the interface of the scan engine.

    2. Add the target fpga and drag and drop the 9211 inside modules

    3. has created the fpga in interface file with and compiled with no error.

    4. interfaced with the file fpga at almost exactly the way the sample project of "getting started with 9211' by using the engine of analysis in the interface with the other modules.

    5. after the errors to discover that I created a VI that tests for just the portion 9211 code (called "thermocouple FPGA method Test.vi")

    The data returned by the interface fpga was nothing else than zeros on all channels, even if thermocouples were hooked on some of them. (all zeros as entries in the convert temperature vi gives-410, 6160 degrees F, if you happen to have the material to try this.)

    I get the following error from the open fpga vi reference:

    code error-61141
    "Thermocouple method Test.vi FPGA.
    Activities FPGA:

    Open FPGA interface reference.
    Reserved outside LabVIEW FPGA: turns The RIO Scan Interface. You must set the mode Interface FPGA chassis in order to unlock the FPGA. »

    It's extremely frustrating, because as I explained, I've been very attentive not only follow the instructions for concurrent fpga and analysis but also to model my VI by the example of VI, even if only for the moment, just to try to work things out.

    Any help would be appreciated as I need to fix this for the further development and I am somehow in a lack of time. I opened a support ticket (reference #7256226), but the app engineer had no time to answer.

    My system:

    cRIO-9014 controller RT with crio-9104 bottom of basket.

    LabVIEW 2009

    Latest drivers and peripheral software pc and rio (RIO scan 3.2 engine support june2009)

    rex1030 wrote:

    I'm reading a 9236 9237 and a 9215 with the scanning engine and read from two 9211 modules with the fpga. It's because I need to acquire to 200 Hz with the 9236 9237 9215 but maximum rate of the scan engine is limited by the slower module in the system, which in this case is the max of 15 hz the 9211.

    This should not be the case.  9211 data will not update with each sweep, but you should be able to run the scan faster than 15 Hz without problem.  Do you have specific issues with this?

    So to use both interfaces (scan engine and fpga), I followed the percisely given in this article for instructions.

    1. the project has created and added the peripheral crio using the interface of the scan engine.

    2. Add the target fpga and drag and drop the 9211 inside modules

    3. has created the fpga in interface file with and compiled with no error.

    4. interfaced with the file fpga at almost exactly the way the sample project of "getting started with 9211' by using the engine of analysis in the interface with the other modules.

    5. after the errors to discover that I created a VI that tests for just the portion 9211 code (called "thermocouple FPGA method Test.vi")

    You can try making sure that the chassis is set to mode Interface FPGA and the setting is deployed.  I wrote that article that you referenced says will select the deploy option later and not explicitly speak to deploy the chassis later.  Run a VI with a reference open FPGA vi not automatically deploy chassis settings if you need to do it explicitly.  Try the following steps.

    1. right click on the frame element and select Properties.  Make sure that the Interface FPGA option button is selected. \

    2. right click on the frame element and select deploy.

    3. repeat your VI.

    The data returned by the interface fpga was nothing else than zeros on all channels, even if thermocouples were hooked on some of them. (all zeros as entries in the convert temperature vi gives-410, 6160 degrees F, if you happen to have the material to try this.)

    I get the following error from the open fpga vi reference:

    code error-61141


    "Thermocouple method Test.vi FPGA.
    Activities FPGA:

    Open FPGA interface reference.
    Reserved for LabVIEW FPGA outside: The RIO Scan Interface is running. You must set the mode Interface FPGA chassis in order to unlock the FPGA. »

    The likely cause of this error is that the setting of the FPGA Interface on the chassis has not been deployed.  If the chassis is still Mode Scan fixed personality bitfile will be loaded on startup and the FPGA will be locked.

    It's extremely frustrating, because as I explained, I've been very attentive not only follow the instructions for concurrent fpga and analysis but also to model my VI by the example of VI, even if only for the moment, just to try to work things out.

    I'm sorry that you have had difficulties.  Assuming that I'm wrong about the source of your problem, it seems we have to update less than Ko to include the deployment step.

    Any help would be appreciated as I need to fix this for the further development and I am somehow in a lack of time. I opened a support ticket (reference #7256226), but the app engineer had no time to answer.

    My system:

    cRIO-9014 controller RT with crio-9104 bottom of basket.

    LabVIEW 2009

    Latest drivers and peripheral software pc and rio (RIO scan 3.2 engine support june2009)

  • How to get the time controller for cRIO-9074 real download

    Hello

    I am a beginner of LabView. Now, I'm doing a project at school with cRIO 9074.

    My problem is that I deleted the default embedded controller system. But in the measurement and automation software I have not found the system controller with function of monitor online. How can I download the load file?

    Wait for your help and thank you for your help.

    Even if you format the cRIO system it should be found by the MAX and opening the software config that you can only reinstall the file system assuming that they are installed on the system (PC).

    Therefore, use the MAX for the cRIO. Maybe it's a help to set the dipswitches to NoApp and IPReset first.

    It may be useful

    Christian

  • Computer stops in normal mode. Do not use the safe mode, because I have no sound, or security out there, please help?

    Computer stops in normal mode quickly. Do not use in safe mode, because I have no sound or security, please help?

    Hello

    Could be heat related - try using a small fan to blow into the air intakes to see if that helps.
    It is just like it loses power or stop it in the normal way? Keep in mind
    This associated heat does not always mean too much heat as it is often a part or a component
    who is too sensitive to normal levels even heat.

    Remove ALL power and reinstall all the memory cards and cables (both ends where possible).
    in fact, remove and replace - don't do not just tight. Remove the dust bunnies and clean the
    air vents. Check that fans are working (before and after opening the case). When your laptop on all the
    You can do is to reinstall the memory and clean the vents (still may try to add a small fan as a
    test).

    This sounds like material so if the above does not help you then probably need help
    a real computer store (not the leeks and the glances at a Best Buy or other stores) or the
    Support of system Maker.

    ===========================================================

    Check with these utilities to see if information may be collected: run BlueScreenView
    to see if there were any BlueScreens and verify in MyEventViewer at shutdown
    (or a few seconds before) See the event log contains useful information.

    It is an excellent tool for displaying the blue screen error information

    -Free - BlueScreenView scans all your minidump files created during "blue screen of death," collisions
    and displays information about all accidents of a table.
    http://www.NirSoft.NET/utils/blue_screen_view.html

    -------------

    MyEventViewer can be verified at the time of the blue screen (BSOD) or event within a second
    or time of the BSOD or event to provide more information about the possible cause - see TIP.

    MyEventViewer - free - a simple alternative in the standard Windows Event Viewer.
    TIP - Options - Advanced filter allows you to see a period of time instead of the whole of the record-
    Set it a bit before and after the time of the event or BSOD.
    http://www.NirSoft.NET/utils/my_event_viewer.html

    ------------

    AppCrashView - free - a small utility for Windows Vista and Windows 7 which shows details
    application of all accidents occurred in your system. The information breaks down is extracted from the
    .WER files created by the Windows Error Reporting (WER) of the operating system component of each
    time that an accident has occurred. AppCrashView also allows you to easily record the list of accidents to
    text/html/csv/xml file.
    http://www.NirSoft.NET/utils/app_crash_view.html

    ------------------------------

    Also do this so you can see the probable bluescreens. (You may or may not be able to see
    them if they occur even after doing this according to the cause.)

    Windows Vista restarts automatically if your computer encounters an error that requires him to plant.
    (also Windows 7)
    http://www.winvistatips.com/disable-automatic-restart-T84.html

    =========================================

    What antivirus/antispyware/security products do you have on the machine? Be one you have NEVER
    on this machine, including those you have uninstalled (they leave leftovers behind which can cause
    strange problems).

    I hope this helps.

    Rob Brown - Microsoft MVP<- profile="" -="" windows="" expert="" -="" consumer="" :="" bicycle="" -="" mark="" twain="" said="" it="">

  • I can't see the pictures in my yahoo email, I did not have this problem with other browsers. I used the safe mode and still no success. Help, please.

    Question
    I can't see the pictures in my yahoo email, I did not have this problem with other browsers. I used the mode 5 firefox safe and always without success. Help, please

    To help other users find solutions, please come back to this Thread and connect you to the
    Forum with your user name and password:

    Click on 'resolved' beside the answer above that BETTER resolved your issue

    DO NOT CLICK on 'Solved It' next to this answer

  • 5610 all-in-one - black thick top of line down on the pages scanned using the scan feeder tray ONLY

    Using HP Officejet 5610 all-in-one I've had for years and maybe 6 months ago, I noticed that anything that is analyzed by the load plate (if you need to scan a bunch of pages without having to analyze each page individually between analyses what is tedious that need constant attention) has this thick black line goes up and down on the middle left of THE pages scanned. Honestly, it looks really bad like if there is something hidden in this terrible line through the process of moving the paper through the feeder, BUT the original is just fine without damage.

    If I scan just a page by placing the document on the scanner glass, and then NO matter whatsoever.

    100% reproducible every time.

    So I know that it has nothing to do with the glass (which is clean), but only when the scanned document must pass through.

    Checked the forums for similar problem and found no exact match.

    I imagine that an expert out there knows the answer to that high hand. IF you could speak up, I would appreciate it.

    I THOUGHT ABOUT IT!

    I read another post:

    http://h30434.www3.HP.com/T5/scanning-faxing-and-copying/HP-OfficeJet-Pro-8500A-plus-vertical-black-lines-only-when/m-p/1391261/highlight/true#M30268

    who is mentioned on opening the ADF cover. Well I opened the whole Assembly, having absolutely NO idea how it all works, and I found a 1 "x 8.5" thick mirror (for lack of a better term) who had what looked like white paint on it to the place where the pages were probably getting the black line. I scratched, retested and the question was gonzo - that's all!

    Then my wife just told me that she thinks that she knew what the problem was all along. She had put on a page and it had not dried, and she tried to put it in the charger to make a copy. She just thought that we were going to replace the printer even when and if ever, let me know. During this time it was me mad for months. What are you laughing at me? This all-in-one works very well for years - replace without good reason, must learn a new product, get new cartridges, out the same old, same old, NO way. If it is not broke, do not replace it!

    Detective Conan.

  • OfficeJet Pro 8600 Plus N911G: Cannot use the Scan to PC, option on my printer

    I recently updated from Windows 8.1 for Windows 10 and had to reinstall my printer drivers and software.  Since doing so, the office of my printer scanning function did not work.

    When I use the option on the printer, I get the message that no computer I'm done to open the HP printing software, select the scanner actions and select manage the scan of the computer.  The only thing is that twhen, I go to the HP folder in my Start menu, there is no installed printer HP software.

    I went to the page support and download the complete software solution for my printer and ran the installation, but I still do not have anything that will allow me to select the actions of scanner, and then select manage the scan of the computer.

    I even tried to use HP Print and scan v4.7 doctor.  He said full software solution is not installed on my computer and it gives me a button to click to download the software, and it is said that it downloads all the 123 file meg, then it gives me an error download failed message and offers try again immediately, but it fails every time.

    My printer is connected to my PC via my WIFI router.

    Hey there,
    Try the next step, I believe that this will help you overcome the problem.
    1. remove the printer driver of "devices and printer" which is located in Control Panel.
    2 Download this file (http://ftp.hp.com/pub/softlib/software12/COL40120/bi-108858-4/OJ8600_1315-1.exe), which is the solution full HP JO 8600 series.
    3. extract the contents of the file.
    4. open the "Utils" folder and choose the folder 'x 64', inside you should be able to locate a file called "RemovePreInstalledDrivers" > once you open this file black screen opens, wait for it to close, then move to the next step.
    5. go to the main folder where you have already extracted the software and right click on the file x 64.msi (name is most likely your printer model), then choose the Option "repair". > Subsequently, you will be asked of preformed a reboot. (Incase you will get a Messege saying "this action is only valid for products that are currently installed" simply double-click the file instead)
    6. after the restart, the head disk Local C/ProgramFiles/HP/PrinterModelFolder/bin/USBSetupLuncher and double click it.
    7 start the installation, choose the wireless option.

    Who should add the scanner to your imaging devices.
    Best Of luck ~

Maybe you are looking for

  • automatic filling in of causing false entries email address

    Sorry if this is a bit confusing:Thunderbird 31.5.0I have unexplained incomplete registration of e-mail addresses and cannot find their source. Here's what happens:I have an e-mail address that is stored:[email protected] when I typed in this

  • How can I delete a mail that does not exist?

    Trying to remove my trash an email that says does not exist. He seems to be now my recycle bin to empty properly. I get this message... The file '153539.emlx' could not be opened because there is no file.

  • Satellite L50-B-23F - how to move to the AMD graphics card

    On this laptop its says I have intel graphics card integrated over an Amd Radeon r7 m260 but for some reason its only using low-end intel graphics when I'm games. When I right click on the desktop and my window appears there is a tab to configure swi

  • Replacing the hard drive in Presario C304NR

    Work on a Compaq Presario C304NR, dead hard drive.    I can't find a service manual for this model and this the first time that I could not remove the hard drive from its housing.  It does not move.   Removed from the laptop, removed the screws (unle

  • error hplaserjetservice on PC

    I get an error in my PC. I installed a printer HP Laserjet 200 color MFP M276 and during the day, the message appears "An unhandled exception occurred in HPLaserjetservice 'number' (this number changes)" " Any idea? Printing does not work normally in