NOR-9472 and SMC solenoid valve

Hello

I'm writing the code for the valve of the SCM activity. I need to control the amount of time that the tap is open. The tap is connected to the / 0 on the NOR-9472

Don't know how to start the problem.

Second, I want to save data to an accelerometer in the VI even.

Yet once again, don't know where to start. If someone could please tell me some examples, it would be fantastic.

Here I have two screws, one to control the faucet, the other to the data recored, separate and have them both in an another vi?

See you soon

K

I wrote code examples that if everything will work well for you, or at least give you an idea of what I was talking about.  There are three cases

-Wait, the VI is waiting for to press you the fire button

-Acquire, the VI changes the value of the solenoid valve and starts the acquisition of the accelerometer for a period of time

-Analyze, the VI performs an analysis of the data and then returns to the waiting state.

http://decibel.NI.com/content/docs/doc-8596

Tags: NI Software

Similar Questions

  • Toolkit NOR EIP and SMC EX600

    Hi all

    I am very new to connect via Ethernet/IP and I got the mission to integrate a SMC EX600 Ethernet/IP fieldbus module into a labview system. Currently, the EX600 is attached to 10 solenoid SMC and SMC 8 SOP 2 digital input modules.

    I did some research on here, and it seems that I got myself a bit confused on the ability of a Communication and the Communication Scanner adapter. What I read, the EIP Toolbox is an adapter, so it cannot start I/O communications between other adapters. It turns out the SMC EX600 is also one adapter per pg 29 of the data sheet (http://www.smcworld.com/upfiles/manual/e/EXxx-OMN0032.pdf), bad luck. So I have reason to assume that implicit messaging is out of the question?

    This might be fine with me, as I don't need a constant flow of e/s and I would rather contact the EX600 on a point-to-point basis. In reading some posts, I found that explicit messaging is supported (http://forums.ni.com/t5/Industrial-Communications/SMC-Valve-Ethernet-IP-Communication/td-p/2979621). This means that I can always get the status of a digital input port or set the position of a solenoid, correct?

    Define States of solenoid valve using messaging explicit or by reading the data sheet, I'm at an impasse on how I actually read entered digital. Could someone clear this up for me? Thank you.

    Quick update,

    After a careful reading, I was able to communicate with the MSC EX600. Using the example of Assembly (Explicit) .vi access Instance data I could read the State of the digital input modules, as well as to define the State of the digital output module and operate solenoids on valve battery module.

    On page 60 of the manual (http://www.smcpneumatics.ie/media/EX600-SEN1_2-Ethernet.pdf), it describes which instance of the assembly to use when specifying inputs or outputs. Using these values, I get a decimal number response corresponding to the State of each module. Convert this number in binary retrieves the value of bit for each individual digital line. Digital outputs are processed similarly except that you write the digital number.

    Valves after your output in table modules and are managed by groups of 4, because there might be 2 solenoids by valve on some configurations.  0 disables the block of 4 and 255 turns on the block of 4. The correct binary value convert decimal to obtain the desired combination.

    I hope this post can help someone who has the same problem on the road.

    PS: Don't forget to put your EX600 have a static IP address before you do all this. The utility BootP rockwell has not worked for me, but this one did http://www.anybus.com/support/support.asp?PID=509&ProductType=Support%20Tools

  • Solenoid valves control

    Hey everybody

    I designed the system pressure (dp cell) with a variety of 8 ports each of what solenoid. What I'm trying to do is to control the valve through labview so the open 1 stay open for 30 seconds in time, then close and another is open and so on. I have attached the plug of the valves. I use with NOR: 9203 and neither Cdaq-9178: 9472.

    The valves are normally closed and the liquid flowing through them is silicone oil.

    I tried to look at the different examples, but I got confused.

    I would be grateful of any advice or suggestion that you give. (I started using labview just a few weeks ago).

    Best regards

    Rajab


  • Motor current and the current valve using CAN interface.

    Hello

    I want to order current engine and valve for some time. The currents of control valves and engine are different for different times, they also have different repetation for test times.

    My problem is how can exploit all the valve and engine at the same time.

    I use NOR-X-net, I have attached a capture, control valves and motors signals are the same message PSD1 - x 605.

    The valve are engine operation is also attached to the file xlx.

    Thank you.

    Rahul.

    Hello

    Please suggest me that how can I run motor and valves separately, both of the soul, I have attaced a program in which I am running engine and set of valves, but I want to run them with time to different repetation and check the valve and engine based on time, current diffrently.

    Thanks in advance.

  • a solenoid valve control

    Hello everyone.

    I need to design a system where it is supposed to control two solenoid valves (for gas of 5 l/min flow), a thermocouple and a moisture sensor. I have a few questions with respect to the foregoing:

    1. what valves would be ideal to achieve flow rates of gas of 5 l/min.

    2. is if possible to use NI - USB-6009 to control via PC or some other hardware DAQ system the above would be better

    3. what additional devices are required in the above configuration

    I'm looking for some preliminary information that could help me get started with the aforementioned project. Any help would be greatly appreciated.

    Deepak

    (1) do not know...
    2) the 6009 will be have limits, no hardware timing for cardiac control loops, can not read TCs, if it's a school or a University project, take a look at the myRio. I'm not shure if it can read the TC directly, but you can easily connect an i2C / SPI TC IC conditioner.
    (3) you will need some vor to power external power valves and a pilot valve (at least a transistor and a diode)

  • basis of solenoid valve

    Hi, I know there is a lot of info on valves and solenoid valves on the forums, but I'm looking to establish myself a starting point. I need a solenoid (or any faucet that can be controlled, really) that will allow me to open and close the tap fairly quickly (less than 1 second) so I can control the level of the liquid in a container. It will be constantly liquid on one side (the top side of the valve in vertical position), and the valve opens for a short period of time until a few mL are exempt, and then close. I have read a lot about who have need of an acquisition of data, or a relay card, but is it here that I can just plug into the wall to power and then have a usb key or another wire run to my PXI to open and close easily? I have a card 4130,2564,8232,4065,8101 PXI slots.

    For example, could just use something like the coleparmer below valve and just supply 24V to the PXI-4130 to open it and then remove tension to close?

    http://www.coleparmer.com/product/Cole_Parmer_Low_Flow_Direct_Lift_Proportioning_Solenoid_Valve_0_02...

    http://www.Grainger.com/Grainger/Red-Hat-solenoid-valve-6WTP4?PID=Search

    Good, but don't forget a solenoid works using a magnetic field to move a piece of metal--a lower voltage, more current is needed to produce the same field, you just need to make sure that everything you go to interface it can handle the voltage and current (or power, which is simply volts * current pure DC).

  • EFI and SMC firmware MBP 8.1 do not match list Apple

    Hi all

    I have a MacBook Pro 13 ", beginning 2011, 8.1.

    I changed the hard drive with a Samsung SSD 850 EVO and installed the OSX El Capitan 10.11.4 Version (15E65) with a clean install (format, then install).

    After that, I noticed that my fans are working more than usual. So I checked the SMC and EFI.

    When I check the presentation of the material, here's what I find:

    Model identifier: MacBookPro8, 1

    Boot ROM version: MBP81.0047.B2C

    Version of the SCM (System): 1.68f99

    But it seems my SMC and EFI firmware do not match Apple list/recommendation:

    MacBook Pro (13 inch, early 2011) MacBookPro8, 1 MBP81.0047.B2A (2015-001) 1.69f4 (SMC 1.7)

    I found this information here:

    On the updates of the EFI and SMC firmware for Mac computers with processor Intel - Apple Support

    I am trying to update, but I received the following message: "this software is not supported on your system."

    Someone at - it already had the same issue on the fans or mismatch SMC/EFI?

    Kind regards

    Carpet

    Hi the-Mat:

    I have the same exact computer and the exact same hard drive. Here are a few impressions of screen.

    My information is the same as yours.

    The version that you and I have is a more recent version. We have MBP81.0047.B2C instead of B2A.

    < Alter > for your fans, try the following:

    Try the PRAM reset: reset the PRAM

    And try the SMC reset: Reset the SMC

    How to reset your Mac SMC & PRAM - and why: reset the SMC & LANDAU

    Kim

  • Keithley 2000 not identified NOR Measurement and Automation Explorer using GPIB

    Hello

    I recently used NI TestStand and NI MAX with IVI drivers to get my working(using USB) peripheral. He has worked successfully for TG5011 and TDS1002B Oscilloscope function generator.

    Following the same procedure: I started with 2000 model DMM of Keithley with GPIB.

    I am facing difficulties in finding my camera on OR-MAX devices and interfaces. I use a GPIB KUSB - 488B USB adapter to connect.

    I can interact with the device of VISA Interactive Control and KUSB diagnosis tool and you can see the device in the device Windows and KI-Configuration Utility Manager. Surprisingly, I don't see GPIB Board in the NOT-MAX.

    Help, please.

    System details: NI-VISA 5.2 installed on Windows 7, KUSB-488 driver installed in command compatibility mode OR. (only ieee_32m.dll is present), installed UN NOR-488.

    Thank you

    Martin

    To help all those who have read this thread:

    I had the Keithley 2000 NOR-MAX and NOR-Test Stand using IVI Driver (for Keithley 2000 of NOR) using the KUSB - 488 B (GPIB to USB adapt from Keithley).

    Layer of keithley installed IO Keithley and I can see the unit property. I then followed the procedure for IVI MAX and TestStand pilot program and IT WORKED!

    Please find attached the screenshots for Visual clarity.

    Thank you and best regards,

  • How to program a remote adjustent with a Laser sensor and a pressure valve

    Hallo,

    I'm looking for a solution set a monostable pneumatic cylinder via a laser sensor and a pressure valve.

    The Laser sensor and the valve has a domain controller as a signal input/output. The position of the cylinder is controlled by the laser sensor and pressure valve schould adjust pressure as needed to get the cylinder into position.

    Sample:

    The cylinder schould be 5mm extended from the initial position. If a team is on the stem of the actuator pressure valve schould be able to increase the pressure in the cylinder so that the location of Rod 5mm remains approximately constant.

    Thank you for a few suggenstions!

    Kind regards

    Manual

    I guess you could use a system by which the laser sensor output when it receives the laser beam.

    Something like this:

    Laser has detected ==> move in the first direction

    Laser (later) has detected ==> move in the other direction

    Laser (later) has detected ==> move in the first direction

    ..........

    So that it switches between two States.

    Or if it is possible, you could just output intensities different laser to represent different values.

    You could get the signal valve dc, translate to a numeric value, set a threshold (or an upper and lower threshold could be better) where the system is stable and doing some codes to ensure that the valve maintains the pressure inside the threshold.

    The rest I think is too deep, and I guess it's to you from there

    See you soon

    David

  • A NOR-RFSG and NOR-DAA on Labview test error

    Hey guys,.

    I'm trying to run a VI, but by testing vi which compose it, I got an error on close vi NOR-DAMA and the narrow vi NOR RFSG (as shown on the picture). Do you have a solution for me please please?

    Thank you

    Thanks guys,.

    I use 2 MIMO blocks, 1 vote against and 4 NOR 5663E (3 slaves and 1 master) and other with 4 NOR 5673E (3 slaves and Master 1 also). I found the solution, this morning, the problem was due to an obsolete vi, I just take a version of Labview 2012 some vi (such as initialization of niRFSA and a few others) and the problem was solved!

    Thank you for helping

  • After internal reset PRAM and SMC microphone still does not work properly

    I've recently updated to el capitan. For the first time that I had to use the microphone internal, so I went to the system preference, the maximum capacity, the value clapped my hands, but the microphone reacts just as shown on the scale bar. So I reset the SMC first then the LANDAU and now it reacts a little more because I clap my hands, I want to tell the scale bar that detects the incoming sound shows like 5 spots (and there are 15 points). I tried to register and the sound of the recording is very low. Is this normal? What I need to fix my mac (3.06 GHz Intel Core 2 Duo, 4 GB of DDR3 memory a 1067 MHz, GB 999,35-909, 89 GB free)? Thanks for any response.

    Susan of morro bay , October 28, 2014 16:21
    in reply to Sirae87   Useful

    I cleaned the little tiny micro holes - and it worked:

    I also had a problem with my internal microphone. In system preferences > Sound > entry, I had the internal mic selected, and the entry level bar would show some activity when I typed in the top of the computer, but not when I spoke. So first of all, I had to figure out WHERE the microphone was actually and I googled and found this on top of my iMac - a very small circle of TINY holes, right in the Middle at the top of the screen. Turns out I have had covered with a decorative Angel, using a sealant that is usually used to stick things to the surfaces. I removed the little angel and PuTTY... but did not always receive my voice recording in the bar of entry-level in sound preferences. I used canned air to blow at the level of the tiny holes, but that did not help. Finally I found a brooch (thinking it was actually too thick, drill holes of small microphone) but I WAS able to push the small holes - so I poked each other - and voila - my internal microphone now work! Yay!

  • NOR-XNET and CAN - FD

    Hello

    The OR Web site mentioned the XNET interfaces are compatible CAN - FD. Could you tell me which are the XNET interfaces with FD CAN 11898 - standard 2:2015?

    Kind regards

    Hello SmileBoB,

    Supported devices:

    In general, the family of NOR-XNET CAN interfaces of is designed to be high performance modules that are easily adaptable to new standards and protocols. Since the physical layer CAN FD is very similar to that of high-throughput CAN, all interfaces CAN of NOR-XNET that support high-speed CAN communication also support FD CAN with bit rates up to 8 Mbit/s.

    The list of NOR-XNET interfaces that support communication CAN FD is below:

    PXI


    • OR PXI-8513/2

    • OR PXI-8513

    • OR PXI-8512/2

    • OR PXI-8512

    PCI


    • OR PCI-8513/2

    • OR PCI-8513

    • OR PCI-8512/2

    • OR PCI-8512

    CompactDAQ or CompactRIO


    • NEITHER 9862

    • OR high-speed/FD CAN cable transceiver for us with the NI CompactDAQ and NI 9860 compatible controllers

    For X-NET 15.0 OR > http://digital.ni.com/public.nsf/allkb/588B7A1E9F2419B086257F1D00667F8D?OpenDocument

    For NOR-XNET 15.5 and 16.0 > allows customers to choose between ISO CAN FD and non - ISO CAN FD in the software.

    Understanding CAN with data Flexible rate (CAN FD) > http://www.ni.com/white-paper/52288/en/

    I hope this helps!

    Best regards

  • difference between NOR-USRP and UHD

    Hello

    The goal of my project is to develop both the driver code for a custom daughterboard and a control panel of vi Labview to change the properties of Remora.

    I have developed the UHD Linux to include support for the follwing the format of the existing Ettus committees daughter card. This all works very well in conjunction with GNU radio/RCMP.

    Now that I am developing a Labview application to control the Board of Directors, I had to walk away from Linux, because there is no support for the USRP in Lunix LabVIEW.

    I'm just here doing with Windows and am about to install the kit of NOR-USRP for Labview support.

    I'm worried that it's a dead end, however. What is the NOR-USRP? What is a wrapper that allows to serve as an interface with the API UHD Labview? Or is it another pilot for the UHD?

    I was counting on the construction of the UHD in windows to include the patch I made for our daughter and then to develop a top-level control system in Labview. In my reading so far however, it seems that the NOR-USRP is not the UHD, a stand-alone pilot with his own material. If NEITHER-USRP and UHD are mutually exclusive, how do I build the USRP-OR source? (assuming that it is the code of industrial property)

    More generally I could frame my question: how to develop support for the drivers for my daughter card that I can use it with Labview?

    After all, I heard one of the main goals the USRP is sold, is to allow the development of Council of girl. It goes without saying that it should be possible to use development environment NOR?

    Any advice on what I need to install/build to set up a:

    LabVIEW-driver >-> USRP-> card girl custom

    development environment would be greatly appreciated.

    Alex

    Alex-

    Your request seems very interesting and innovative.   The NOR-USRP driver is designed to work on a specific version of UHD and a specific image of FPGA.  In order to provide a user experience that is refined it has been tested with the NI USRP-29erxx materials and was not supposed to be recompiled by the end user or used with custom Remora.

    That said, you can call labraries and communicate with your own internal radio via a UDP socket GNU applications.  Based on the little information I have on the application I would recommend remaining under Linux and the use of LabVIEW for Linux.  You will have the ability to call libraries and use UDP as I've described.  If you choose to switch to windows, you can add a few basic IP capaiblies for functions / toolboxes that run only in Windows operating system.

    Erik

  • Best configuration for the control of solenoid valve

    Hi all

    I'm really new with everything regarding controllers or the relay so that any help would be much appreciated.

    I want to control 5 valves (Web site) with the following characteristics:

    Rated voltage: 12 or 24 VDC, available voltage fluctuation: 10% of energy consumption (when 24V nominal voltage): 1.5W (0.06 A)

    I want to use LabView to control. In a similar position, I knew I would need a digital camera I/O driver relay and a generator of 24V.

    I was thinking of using these:

    NEITHER 6501
    Relay driver (uln2003)

    and a 24V generator.

    Is it enough to order the valves with LabView or do I need something else?

    Thank you very much for your help!

    Ilan

    Yes, this combination should suffice.  The ULN2003 is designed for exactly this type of application, and works well.

    Usually in English, we refer to the power supplies when we talk about devices to convert AC line voltages to lower DC voltage.

    In addition to LabVIEW, you will need a driver for the USB-6501 DAQ. Under Windows, it will be DAQmx. On Mac or Linux, the dirver is DAQmx Base. The driver is a separate LV facility, although it can occur on the same disks.

    Lynn

  • How to speed up loop DAQ triggered using NOR cDAQ-9174 with NOR-9215 and NOR-9402

    Hello

    I use LV2010 and NOR-DAQmx 9.2.2. I have a NOR cDAQ-9174 with a NEITHER-9215 4 channel 100 k simultaneous ADC and NOR-9402 4 channel DIO module trigger and reset.

    We run WinXP sp3 on a Dell M4400 core 2 duo @2. 26 Ghz.

    I used the code example NI DAQmx for acquisition of tension with trigger HW. My goal is to try all 4 channels on the 9215 simultaneously when a trigger is received on channel 0 of the 9402, after data is read, I use channel 1 on the 9402 to reset the trigger of the target material.  I have a version of this work, however the maximum event rate is ~ 16/second. I have the Setup 9215 for finite samples / 10 samples per channel which is ~ 400uSec of conversion time and I realize he is above in the appeal of vi, but ~ 50mSeconds worth?

    The target detector can put out up to 1 k / event triggers / seconds.  Only, I received a rate of 8 per second and I added the NOR-DAQmx control vi driver and chose "commit" this did double the rate.

    My question is what is the maximum rate of loop for these devices (trigger/conversion/reading device / reset) and start over? I noticed that just let free the 9215, carried out using the 'Acq & chart internal strain Clk' raised only the rate of events up to 20 Hz.

    Thank you

    normbo663

    Hi normbo663,

    You can get this works far better assuming you have an available counter (there are 4 on the backplane of the 9174).

    DAQ Compact supports the tasks of meter output "redeclenchables" that can be used to generate a finite pulse train.  You can set a task of finished meter redeclenchables output to be used as sample for your task of analog clock.  The task of the meter output will be re-Army (less than 12, 5-25 ns) as soon as it's finished out the last pulse.  The task of analog input would be configured to run continuously, but it would only sample based on the output of the meter triggered.  For an example, see here.

    You can reference the internal counters on the cDAQ without signals through a routing module using: cDAQ1/_ctr0 (right click on the chain counter control, then select i/o name of filtering and check channels internal to add these options to the drop down).

    Thus, with the tips above, you should be able to immediately re - arming your analog acquisition on the 9215 using one background basket counters.  It seems that the second half of the application is to use a second channel on the 9402 to reset the trigger of your DUT.  You can deterministically generate this signal so by configuring a 2nd redeclenchables meter out task (single pulse, but this time).  All you need to do is the initial delay on the appropriate value for your analog acquisition.  Trigger this counter on the same PFI line that trigger you your analog task from.

    Using counters to generate the signals you need in a deterministic way, the loop becomes is no longer a problem (as long as your input buffer does not overflow).  You may need to re-read several triggers at the same time for the loop to keep (for example to read 1000 samples each, which would correspond to 100 triggers 10 samples).

    Best regards